Batteries in the attic?
Thick8
Thick8 Registered Users Posts: 49 ✭✭
I want to move my battery backup system into the attic. I am in the process of finishing that space as a living area but can section off part of it for the batteries. What would I need to do to make that work? venting, spill mitigation, etc. Is there a building code established for doing this?
«1
  • Estragon
    Estragon Registered Users Posts: 4,498 ✭✭✭✭✭
    Assuming the sectioned off attic area is likely to get hot, a couple additional things to note; battery life expectancy is severely reduced with heat, and proper temperature corrected charging voltage will be important.
    Sturdy plastic tub(s) would likely work for spill mitigation. I imagine venting required for heat mitigation would be more than enough for venting gasses.
    Building code varies by jurisdiction (and sometimes by specific individual inspector), but other than requirements for conduit etc. I'm not sure there's anything saying you can't (assuming system voltage of 12-48v). I've run across inspectors who seem to approach things such that if it isn't specifically allowed, it's prohibited. Luckily (or not, depending on your POV) I don't have to worry about inspectors though. Others who do may know more than I.
    Dave Angelini Solar Expert Posts: 7,023 ✭✭✭✭✭✭
    Sure go ahead and do it. I just hope you never have a need to use your home insurance policy. Maybe you do not have one and so at least do what Estragon suggested. If it is conditioned living space the battery needs to be listed for this also.
  • Thick8
    Estragon, I currently have my battery bank in a non-climate controlled (way) detached garage. It gets over 100F in there. The attic is well insulated so It doesn’t get as hot. I was thinking of building a small room to house the batteries and inverter. Then run a duct from the crawl space beneath the house (which is encapsulated and dehumidified) straight up to the attic to better maintain a constant acceptable temperature. I would also vent the room above the roofline. I would probably use a plastic A/C air handler pan to hold the 3 8D batteries. Then I could put a drain line on it in case of leakage.
    Just wondering if anyone has done something like this.
  • mcgivor
    Why not use the crawl space for the battery location?
  • Estragon
    I was thinking a tub with enough excess volume to contain (at least) the volume of a rupture and acid leakage of all batteries in the unlikely event of same. I wouldn't have a pre-installed drain (as a potential leak), but rather deal with the contained situation if it occurred..
    As @mcgivor asks, why not put batteries in the crawlspace? It would likely be easier to run wire to the attic than ducting, and ducting from crawlspace introduces potential for earth gasses being forced into living space.
  • littleharbor2
    littleharbor2 Solar Expert Posts: 2,134 ✭✭✭✭✭
    Plus lugging a bunch of heavy batteries into and out of the attic sounds like an unpleasant job.
  • Thick8
    I did think of that but the crawl space is only about 2’ tall with an 18” access hole. And where I would need to place them is about 40’ from the access. Also I wouldn’t check on them as often as I would in the attic. Plus building an enclosure to remove any outgassing would be difficult at best.
  • Estragon
    Why would they need to live 40' from the access?
  • mcgivor
    Having worked in many attics in the past as an electrican, I've never encountered a cool one in the heat of summer, even with insulation, but then again I didn't work in yours.
    Up the ladder, over the ceiling and through the sheetrock !
    Attics are not designed to carry much more of a load than a box of holiday ornaments.  putting hundreds of pounds of batteries in it, is going to cause problems - according to my crystal ball.
  • WaterWheel
    WaterWheel Registered Users Posts: 387 ✭✭✭
    Like Mike said that's a lot of weight for an attic.      And I assume that you also plan to move the inverter to the attic to keep the battery cables short, rerun your panel wires, and probably move the charge controller too.      Throw in rerouting the AC wires that your inverter is putting out and that's quite a job.
    If you're going to do all that it may just be easier to use a water bath and keep the batteries in the garage.
    48v Rolls 6CS 27P
  • Thick8
    I like the idea of a water bath. Would I need to run a little 12 volt pump waterfall to gain evaporative cooling of the water. I have an extra PC water cooling pump and some corrugated plastic panels. The pump only draws 1 amp and I could put it on a sunload sensor.
  • WaterWheel
    edited September 2018 #14
    With only 3 batteries you could get a large plastic tote from Walmart.      That's what I use for a solar system at my shop with 3 batteries but I don't keep them in water.
    48v Rolls 6CS 27P
  • Thick8
    edited September 2018 #15
    I don't think the weight is a problem. The house was built in 1950 with the attic designed to be a living space. It is all tongue in groove decked over full dimension 10"x2" spaced at 16" OC. The location that I plan to place the batteries is over the original location of the oil furnace. So it is basically a 3'x3' floor the ceiling room placed directly over a 4'x4' brick pier. Plenty of support I think. I don't have a ladder, I have a full 36" wide staircase that I put in. I guess calling it an attic is not exactly correct.
    The inside breaker panel is located in a space that used to be a doorway from the kitchen to ( what was originally) the housekeeper's room. Which is right next to where the oil furnace was. I just cut access holes to the panel and floor to run a 6/3 cable for my new Leaf charger. So it would be a simple task to move the circuits that I want on the backup to new circuit box next to the existing one.
    My question is really about the codes governing the batteries being in the house as apposed to located in a garage or remote location.
  • Estragon
    AFAIK, at least in my jurisdiction, there's nothing in the code beyond the electrical stuff that would apply wherever the batteries live. That may change if/when R.E., powerwalls, etc get common enough that bad things happen and code responds, but for now it appears to be crickets.
    If pulling a permit for the work, you might want to run it by the assigned inspector. In a past life I did heritage building restorations and conversions, in which uncommon things came up pretty frequently. For the run of the mill stuff, the inspectors were fairly predictable in what was likely to pass, but they varied a lot when it came to dealing with the uncommon conditions.
    You may also want to check insurance conditions. My policies are silent on the issue so far, but may be worth checking.
    Batteries can not be in conditioned space unless they are listed for it in most of the United States. If you have a fire, and the insurance company hires someone like me, they have the option of not covering the claim.  Of the 3 I have done, one was not covered.
    It is a dumb idea to do this in my most humble opinion.
  • softdown
    softdown Solar Expert Posts: 3,963 ✭✭✭✭
    Absolutely horrible idea for so many reasons I can't even begin to start on.
  • Thick8
    Fortunately my wife is an adjuster for our insurance company. She didn’t find anything that excludes a backup system. She also said that in order to deny a claim, the battery bank (if it were done without a permit) would have to be the source of the claim, and as long as it passes inspection it is covered. Solar panels require a separate endorsement though. So that answers the insurance question.
    How many here have batteries in their finished basement or on the wall that separates the garage from the living space? Are these installations against code? Trying to figure out why the second level of a home is a no-no and these other installations are acceptable. Guess I’ll have to go digging through building codes. Yuck...
  • Estragon
    The basement would normally be considered conditioned space. Lots of basements have batteries for alarm systems, UPSs, etc., but AHJ may require ETL certification for such systems.
    A garage would normally be unconditioned space, with code requirements for fire separation etc., so not directly comparable to an attic space (unless you're planning similar fire separation products and assemblies between the battery space and living space).
  • softdown
    Roof trusses are generally made of 2 x 4s that span a large gap. They are not designed to hold the compact weight of lead batteries. Roof truss failure would be unimaginably catastrophic. Ask a roof truss manufacturer about your plans and see what they say.
    Attics are also very hot. The batteries would suffer a very short life as a result.
    The safety of lugging heavy batteries up and down a steep attic ladder? What do folks think?
    This is about the worst idea imaginable.
  • Thick8
    edited September 2018 #22
    I described the space in post #15. Reading before slamming is always a good idea.
  • Estragon
    2x10s at 16"OC and a 4' span would support orders of magnitude more weight than 3 x 130# batteries.
    Even assuming they were put on plywood spanning the bottom chord of 3-4 2x4 trusses, a dead weight load of ~ 400# wouldn't be my first concern. Trusses that couldn't take the weight of a couple of guys working in the attic would be firewood IMHO..
  • bill von novak
    For a while we had a bank of 24 T105's powering an airport.  We had a wooden box built to hold the batteries, vented to the outside.  The fans failed within about 2 years due to acid mist.  When we decommissioned the system the plywood under the batteries was black. When a worker got the first 4 batteries out he got into the battery box to get the next few out.  His foot went through the 3/4" plywood below.
    Imagine that happening to your house.
    Your post is titled  Batteries in the Attic.    Then you complain when you are told the attic is a poor choice for MANY reasons.
    The next comeback is it's a finished 2nd floor, with stairs, and such, supported by a brick pier.   But that's still not a good place to put batteries.
      So don't get all huffy about an answer to a question  you asked.
    Good luck and have fun.
  • Thick8
    No complaining at all. I better described the area to eliminate the confusion understandably caused by the title. And again asked if ther were codes established governing this type of installation.
     Asking someone to quantify their opinion is not a comeback; it is part of intelligent productive discourse.
    Thank you and I usually do.
  • Thick8
    edited September 2018 #27
    Yes that would be bad.
    When I built a hidden gun cabinet I lined the entire enclosure with spray-on bed liner material. That might not be a bad idea for a battery enclosure. Fire retardant bedliner sprayed on fireboard.
    You also just made me realize that any ductwork to remove fumes would need to be made of an acid proof material. Metal ductwork would be a no-no.
  • Estragon
    My plan for ventilation is a fan on the intake side with PVC pipe. With bottom intake / top exhaust, I think it should vent naturally most of the time, but I'll put a computer muffin fan on the intake to pressurize the box a bit to assist.
  • Thick8
    That makes the most sense as long as the enclosure is sealed so that all the ventilation air flows out the pipe. Using convective current for airflow would probably work as well. I remember seeing one of those rooftop spinning ventilation “fans” made of plastic with ceramic bearing for move positive ventilation if needed.
    Some schedule 80 4” PVC bringing stable low temperature air up from the encapsulated crawlspace. Up to an acid and fire proof enclosure. Then out through a roof vent.
     I could mount the inverter/charger and charge controller outside the box with only the 2 cables passing through the wall of the enclosure.
    Thanks for the ventilation idea.
  • Estragon
    As well as temperature (warm air rising) hydrogen produced by batteries is lighter than mostly nitrogen ambient air, so should normally vent naturally out the top.
  • jonr
     > Using convective current for airflow would probably work as well.
    In the Winter, but may reverse when the AC is on (80F air doesn't passively rise through a vent surrounded by 100F air).   Probably more of a concern is things that lower interior pressure (eg, kitchen/bathroom fans, dryer).
    On the other hand, I once did the calculations and for anything larger than a small room, hydrogen levels typically can't get high enough to be a problem.   But don't rely on this.