Are Lithium Batteries the way to go?

ligwyd
ligwyd Registered Users Posts: 209 ✭✭
Hi All,

Some say Lithium solves a lot of the problems with flooded lead acid batteries. To all who have experience in the area what are your thoughts?


«13

Comments

  • softdown
    softdown Solar Expert Posts: 3,812 ✭✭✭✭
    I use a lot of lithium tool batteries. It is a much better technology in many ways. But the prices for lithium solar batteries are still iffy in my estimation. My vote would be for lead acid for the next ~5 years. Then see what lithium is offering. 

    Unless, perhaps, you can get a great deal on a used lithium automobile battery. May be worth checking into.
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Lithium (of which there are multiple types with distinct characteristics), solves some problems, but creates others. Some include inability to charge in cold temps, greater risk of fire, difficulty in using voltage as a SOC indicator, and cost.

    These can be overcome with some chemistries in some applications, but for my off-grid application, like softdown, I think I'll wait a bit for costs to come down.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,731 ✭✭✭✭✭✭
    Cold is an issue and so is heat. More so than LA. They like the temperatures humans do and do not like a shed out in the tundra/desert.
    I think the cost is not going to come down.
    I also think if you do the math, they could outlive you guys.
    The Soc accuracy is one of the main attributes of Lithium chemistries and their integrated BMS.
    Incredibly accurate Soc !
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • BB.
    BB. Super Moderators, Administrators Posts: 33,431 admin
    Lithium batteries are still a bit "bleeding edge". If they do not get you something, probably waiting 5 years is not a bad idea. Li Ion batteries generally have an integrated battery management system--That should feed back to the inverter, solar charger, etc. -- That is still not a common configuration at this time.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Being quite efficient, SOC accuracy can be excellent with a good BMS. Just saying voltage doesn't work well, and a good BMS isn't optional.

    Will have to agree to disagree on the cost coming down. I don't know what the capacity vs EV take-up curve looks like. At this point, your guess is probably at least as good as mine.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • Raj174
    Raj174 Solar Expert Posts: 795 ✭✭✭✭
    I've been using a 12 kWh prismatic LiFePO4 bank for over 2 years now and it is 99% efficient and very reliable. It is installed in an air conditioned space, temps vary from 60 to 78 degrees over the year. I cycle it down to 28% but most days during the summer, the bank doesn't reach 100% due to poor solar weather and because I keep a load on it all day with the A/C running. Honestly it pretty much works like an appliance. It also works well with Outback's Grid Zero mode, sort of set it and forget it. But I micro manage it to get maximum production. Like @Dave said, SOC is very accurate if using a good battery monitor, for me that's Midnite's Wizbang Jr. wired to a Classic 150. This bank is probably cycling at about 60% which should go for about 4000 cycles if usage doesn't change. LFP is expensive, my bank was 3300 dollars. A similar bank today would be about 4000 dollars, consisting of 16 or 17 3.2 volt 200AH prismatic cells in series.

    Rick
    4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
  • ligwyd
    ligwyd Registered Users Posts: 209 ✭✭
    edited July 2018 #8
    I have a friend that purchased a 7 kWh lithium battery for around $7000 CAD and ended up not needing it. Might be a good chance to purchase at a discount and experiment with it. Being dead in the water when its below freezing does not sound fun and I am not too comfortable with lithium to close to where the family resides. I am considering installing a Mitsibishi or Fujitsu heat pump to climate control the framed, and insulated sea-cans but even then in very cold climates (below -25 C)the heat pumps are not feasible. Might have to cut my teeth on the batteries I have now and go from there.

    If you guys had purchased 12 - 12V batteries not knowing any better would you back out and buy something more suitable for off-grid or would you carry on towards the iceberg. Not excited about 3 strings.....



  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Personally, if I already had the three strings of 12v batteries, I'd do the best I can with what I have. If you wire them properly, and monitor for/remediate potential problems by checking SG regularly etc, you can do fine. Ideally, a single string is best/easiest, but you can make multiple strings work too. It just takes a bit more work and vigilance.

    7kw 2nd hand lithium for $7k CAD wouldn't be all that tempting to me.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    If it was me and I knew which Li chemistry I would ask make model, serial number, type /make of  BMS ,etc... the good thing about most  Li chemistries is that they can sit for a long time with no degradation as opposed to FLA etc...
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • ligwyd
    ligwyd Registered Users Posts: 209 ✭✭
    edited July 2018 #11
    I could probably get the 7 kw lithium for 5K CAD which is roughly what I got into each of my banks of 12-12V batteries. Here is the link to the 48 V Lithium product I am referring to:
    I did do a couple weeks of research on FLA and my 12 V batteries in particular and have charged them regularly and equalize them in separate strings as they sit waiting to be put into service.  I think the reason my supplier bought the 12 V batteries was simply price point I am assuming because 12 V batteries are probably more mass produced?

  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    Those batteries are approved for use with  Schnider Xanbus charge controllers and inverter chargers, which I believe is what you have, or are considering. @Dave Angelini was, I believe, testing their compatability for Schneider, perhaps the best person with hands on experience to offer an opinion, that I'm aware of, he mentioned cost was ~$ 1000 per Kw. As far as lithium batteries are concerned, I often wonder if it's the fear of fire associated with some chemistries which paints them all with the same brush, all I'm definitely not an expert, but from what I've read and understand is that  LiPo4 are safe if properly used with an applicable  BMS.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,731 ✭✭✭✭✭✭
    As Mcgivor said or the update is that is all I use for my new clients who have reasonable temperatures and Schneider electronics. Outback soon will interface directly with the AES.

    It is a common configuration at this time Bill because I would not use anything that does not interface the BMS, battery, and Soc/temp directly from the battery manufacturer into the system over Schneider insight or soon Outback optics. The reason I do not think they will comedown is simply the cost of the materials in an LFP battery. They are going up lately. The BMS is pretty simple and electronics do tend to come down. I definitely would not buy a lead acid if i knew that this was for the long haul and that I could keep them at temperatures that are pretty well spelled out in the warranty. Partial cycling is what people forget to add when they cost an LFP battery BTW.

    Having accurate Soc, Not worrying about being full on a regular basis,  =   Priceless offgrid if you live there full time!

    I really respect what Rick has done but I could never use that system for a client and maybe that is what BB is referring to.

     I just looked,  at close to 2 years I am still at 99% state of life from my BMS. A bit of math and at the rate we cycle, about 34 years left. I do live within an hour of Costco if the math  is wrong ;) My clients really like this battery, I mean really like it! Cheers!
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • Raj174
    Raj174 Solar Expert Posts: 795 ✭✭✭✭
    As Mcgivor said or the update is that is all I use for my new clients who have reasonable temperatures and Schneider electronics. Outback soon will interface directly with the AES.

    It is a common configuration at this time Bill because I would not use anything that does not interface the BMS, battery, and Soc/temp directly from the battery manufacturer into the system over Schneider insight or soon Outback optics. The reason I do not think they will comedown is simply the cost of the materials in an LFP battery. They are going up lately. The BMS is pretty simple and electronics do tend to come down. I definitely would not buy a lead acid if i knew that this was for the long haul and that I could keep them at temperatures that are pretty well spelled out in the warranty. Partial cycling is what people forget to add when they cost an LFP battery BTW.

    Having accurate Soc, Not worrying about being full on a regular basis,  =   Priceless offgrid if you live there full time!

    I really respect what Rick has done but I could never use that system for a client and maybe that is what BB is referring to.

     I just looked,  at close to 2 years I am still at 99% state of life from my BMS. A bit of math and at the rate we cycle, about 34 years left. I do live within an hour of Costco if the math  is wrong ;) My clients really like this battery, I mean really like it! Cheers!
    I agree, @Dave, it's not a system for clients. But for someone who manages their own system and understands LFP balancing and  charging characteristics, it works well and the price is hard to beat.

    Rick
    4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
  • ligwyd
    ligwyd Registered Users Posts: 209 ✭✭
    edited July 2018 #15
    Great discussion. Dave, so the 48 V Discover AES Lithium is "THE" battery, at the present, for Schneider equip hey? And yes that is what I have now, everything Schneider. XW+ 6848, 2 - MPPT 60 150's, SCP, Battery monitor, Com box, AGS.
    Also, would 4680 watts of PV (STC) be appropriate with that 7 kw Discover Lithium battery or severely undersized? With the potential to push 130 A in to the battery, although not necessary and not sure why you would want to too due to excess heat, what is an appropriate sized back up generator. Obviously not a 130 A output generator (that'd be huge and $$$) or do you increase PV for your AES clients? I like this little guy so far:



  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,731 ✭✭✭✭✭✭
    Become a client! I only give general info on this forum. There are two hungry cats and 5 turkeys depending on me :)

    Stay cool Rick!  My fingers are crossed for the mean season!
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • ligwyd
    ligwyd Registered Users Posts: 209 ✭✭
    Has anybody looked into the 14 kWh Tesla Battery or is it still just overpriced hype with a sleek finish?

  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    I think Elon sent them all to Australia and Puerto Rico for his mega projects there
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • ligwyd
    ligwyd Registered Users Posts: 209 ✭✭
    I haven't been able to find out if the Power Wall 2 can operate as an off grid battery or not?
  • Graham Parkinson
    Graham Parkinson Registered Users Posts: 160 ✭✭✭
    The 48 VDC Blue Ion 2.0 battery (LiFePO4) works off grid (8 kWh, 12 kWh, 16 kWh), they quote 8000 cycles - no idea on cost yet.

    Offgrid in cloudy PNW

    MacGyver'ed museum collection of panels, castoff batteries and generators - ready for state of art system install .... parade of surviving and dead generators: H650, Ryobi 900, Briggs and Scrap Iron 2000, H2200, H3000, Kubota 3500, Kubota 4500, Onan 7500

  • ligwyd
    ligwyd Registered Users Posts: 209 ✭✭
    On the spec sheet it says it cannot charge at below freezing.


    FLA's seem to be an old, simple design which can handle the cold. If you can climate control the area the Lithium will go then it mat be a great solution in the near future. Power wall 2 self regulates temp (though at a consumption of stored energy I am sure).

    I signed up for updates on the  Blue Ion. Thanks for the info.
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    All battery chemistrys have their pros and cons, choose the ones interested in, make a column for each, list all criteria, in a spreadsheet format,  high temperature performance, low temperature performance, self discharge, efficiency, life span, depth of discharge ability, weight, ease of maintenance  etcetera, etcetera, then tick the boxes. That's what I did and lifepo4 came out on top for my application so that's the road I'm going down, lots to learn no doubt, but being the proverbial fly on the wall reading others posts, it would seem individual prysmatic cells is the cost effective option. The price is competitive with LA considering cycle count, my cost for 450Ah LA was $1187,  200Ah LiFePO4 $1232 at 24V nominal, plus BMS, import tax and shipping, still working on that. The first system will be a learning system, not the primary which will actually be smaller, thinking around 100Ah, 24V nominal, going to be interesting.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    > @ligwyd said:
    Power wall 2 self regulates temp (though at a consumption of stored energy I am sure).
    >
    >
    My understanding is none of the lithium chemistries should be charged below freezing. Not sure how PW or others do it, but I would design it so available incoming R.E. power is used first to warm the bank, and charging enabled only when bank reaches a min temp. Using stored energy would run the risk of of a cycle of heating and cool-down with intermittent sun and overdischarge, and strikes me as a bad idea.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Winter  time insulation panels, and DC heat pads , so little internal resistance that there is little self heating with solar charge rates. None of the Li formulas that I know of, can charge below frost.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • ligwyd
    ligwyd Registered Users Posts: 209 ✭✭
    Power Wall 2 can charge/ discharge at -20 C/ -4 F coldest temp but is not recommended to operate in this cold of an environment.







  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,731 ✭✭✭✭✭✭
    Tesla also has on board temperature control and you have to have a grid connection to keep the battery happy. The grid would power this in cold temperatures BTW.

    Zero warranty for offgrid and I have done a few with a friend who is a Tesla certified installer.

    It actually is a good value for the price but there is zero DIY support from them.
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • Graham Parkinson
    Graham Parkinson Registered Users Posts: 160 ✭✭✭
    Blue Ion 2.0 are about US$1,074 / kWhr - They have temperature sensing that prevents charging in freezing conditions:

    https://www.homepower.com/articles/solar-electricity/equipment-products/living-lithium-ion-energy-storage?v=print

    Offgrid in cloudy PNW

    MacGyver'ed museum collection of panels, castoff batteries and generators - ready for state of art system install .... parade of surviving and dead generators: H650, Ryobi 900, Briggs and Scrap Iron 2000, H2200, H3000, Kubota 3500, Kubota 4500, Onan 7500

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Blue Ion 2.0 are about US$1,074 / kWhr - They have temperature sensing that prevents charging in freezing conditions:
    So, it's winter, cold, dark and the batteries are empty. Run on generator till sprig thaw ?
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,731 ✭✭✭✭✭✭
    I don't think that one needs to do this Mike. Design for a proper battery room that is a conditioned space. Not that hard to do unless one is leaving the home unattended. That is the real challenge to me and some of my clients in places like Alaska and Canada. 
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • jonr
    jonr Solar Expert Posts: 1,386 ✭✭✭✭
    It takes very little energy to heat a well insulated battery box.   So you could wire a single panel directly to a small, thermostatically controller heater.  This resolves the chicken/egg problem if an unattended main bank gets drained and too cold.

    I am available for custom hardware/firmware development

  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,731 ✭✭✭✭✭✭
    Completely disagree! I guess you have never lived in Alaska Jon. 
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net