Comments
-
If you want a 24v automotive type alternator just buy one. Or see if the 12v alternator you have has a 24v regulator.
Or connect the v-sense wire to one 12v battery to trick the alternator into producing 24v.Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
I would like to use the alt that I have , it is rated for continuous use charging large marine battery banks.
I will take the alt to the rebuild shop and see what they can do.
Thanks for the replyOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Could some one tell me how I would run this panel in a 48 volt battery system into a outback flex max 80 charge controler. Please .
Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Into an outback MPPT controller you would need 3 panels series wired for a 48 volt system
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
So we would be looking at vmpp 36.81 x3 =110 . 43 volts in to a 150 volt max charge controler .
It get cold here may be - 20/-30 would I still be ok with these panels ?Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Actually the maximum voltage rating is taken from the open circuit voltage which is 137.25 at 25 degrees Celsius , Standard test conditions (STC). You need the temp. coefficient numbers for those panels (should be on the data label) to calculate the numbers for your lowest expected temps in your area. Sounds like it will be too high. though. If you had a Midnite solar Classic 150 you have Hyper VOC protection which gives you an additional 48 volts headroom on a 48 volt system. Or a classic 200 would give you plenty of headroom although at a lower maximum charging amperage rating. This Hyper VOC is only there to protect the controller. You will get no charging if your array is producing over 150 volts. I'm not sure but ,at some point I believe you will transition to a charging state which would naturally have lower voltage than open circuit voltage.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
wellbuilt said:So we would be looking at vmpp 36.81 x3 =110 . 43 volts in to a 150 volt max charge controler .
It get cold here may be - 20/-30 would I still be ok with these panels ?
http://www.outbackpower.com/outback-support/string-sizing-tool
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
No haven't figured out how to work the string calculator yet sorryOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
-
2 panels in series at 91.50 volts won't charge a 48 volt bank ?Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
-
2 in series would probably be the better choice, close to double battery voltage which many claim to be optimum.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
91.5 would be the Voc. Once you put a load on them the voltage will drop to 73.62. Problem that number is at standard test conditions. In the real world you will only see that number when it's cold outside. When it gets hot, or even warm the surface temps of the panels will get considerably warmer than the air temp and the voltage drops. that's where the temp. coefficient comes into play again. keep in mind that equalizing voltage will run up over 60 volts on a 48 volt bank, regular charging voltage will be upwards of 58 volts. This is the reason the 60 cell panels some people think are 24 volt panels wont work for 24 volt battery charging as a single panel. MPPT controllers want to see 150 to 200 % of the battery voltage to work effectively. Feeding an MPPT controller a 48 volt nominal voltage, which is what two panels in series is, will gain you little advantage over a PWM controller, at least when it's warm out. When it's cold you will see some amperage boost. Anyway that's better than cooking your controller by wiring 3 in series.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
72 cell 36 volt panels 2 in series are not adequate for charging flooded lead acid batteries. Best to use 60 cell 250 to 275 watt panels 3 in series. That's 90 to 95 volts VMP and VOC is not too high. Just last week a friend was using several strings of 4 100 watt panels, string voltage was 75 volts and during 64 volt EQ ( 225AH T-105's) the charge controller was cycling from full wattage to rest every couple of minutes.
The panels could not produce VMP high enough for the MPPT charge controller to maintain the EQ charge voltage.
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Thanks guys , I just found the panels at 100 bucks each new in the box
20 min from my house .
I'll keep looking .
I'm looking for a panel that has a voc of 38-+ to series 3 together to get around 115 volts+- .Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Most 60 cell panels are 30.x VMP and 36.x VOC. Some of the latest 285-300 watt 60 cell panels will be higher.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
> MPPT controllers want to see 150 to 200 % of the battery voltage to work effectively.
Specs I've seen are highly variable and depend on the absolute voltage values. Ie check your specific charge controller. Or consider PWM.I am available for custom hardware/firmware development
-
Of course you can push the max voltage envelope and still charge a 12 volt battery bank but you will give up some efficiency in the voltage step down process while creating more heat and likely shortening the life of the controller.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Hi all ,
I'm getting ready to run some wires at my place , and I need to add a grounding rod .
Can I just use 1/2 rebar or dose it need to be a brass rod ?
I've seen it both ways .
I'm on ledge with 6" to 12" of dirt over a granite ledge .
Could I dig a trench say 10' from the back of the garage and lay the rod in the ground?
How about if I drilled a series of holes 30" deep and zigzaged the ground rod between them .
I could of grounded to my footing when we poured the concrete but I did not have the lugs or wire at the time.Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
You can also use ground plates buried in your shallow soil... These are copper and, I am sure, not cheap:
http://www.tlpinc.com/products/grounding/ground-plates.html
If this is not inspected... I would think about using buried lengths of "L" Blue or "K" Orange lettered copper pipe (red is thinnest, Orange is thick wall copper pipe. "M" is read letter and the lightest grade for interior of home copper piping). Bury a few 10 foot lengths of copper pipe in a star pattern. And make all of your connections at the center of the star (or 1/4 circle of star pattern--the point of the star closest to the wall/building/where your ground wire comes to earth).
Running 6 awg for 10 feet is note great for lightning grounds... It has higher "impedance" and the lightning will try to find another path rather than follow 10-20+ feet of 6 awg cable. (lightning has "higher frequencies" and behaves differently than 60 Hz or DC current--Higher frequencies tend to want to leave the conductor (magnetic field forces electron flow to the skin of the wire). If you have to make a run, 3/4" copper pipe should be better (or get true lightning rated braided grounding cable).
If you have dry soil, they even go as far as back-filling with bentonite clay and a dry well to add water to reduce resistance. This is a nice catalog with lots of lightning attachments and fittings. Note that they are using something like 2 AWG minimum copper cabling (building less than 75 feet tall--I think) for their grounding.
https://www.erico.com/catalog/literature/E1147C-WWEN.pdf
I am in no way a lightning expert--Just some ideas.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I do have some 20 g copper flashing 12"x 15' left from a job.
If I rolled over one edge of copper flashing and clamped it to a 7' piece of ground rod then bent the rod at 90o to stand up out of the ground with the proper lug connection to attach my ground wire , would that be OK .
Some of the plates are 30"x48" 20gadge copper .
I also have a bunch of 3" wast line that could be pounded flat and run out away from the house in a fan shape ( half a star ) starting at the wall with the ground rod bent in a l shape standing up for ground lug .
Maybe braze the ground rod to one lenth of pipe and bolt thru all three pipe endsOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
20 gauge sheet metal is about 0.0375 inch thick. Those were 0.250 inch [1/4"] thick copper plates I linked to.
K wall 3/4 pipe is 0.065" thick (just one wall).
I would not be a fan of 20 gauge copper buried for long life.
3" pipe would not be bad (copper or iron?).
- BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I have similar conditions and used a couple of grounding plates, one for array and one for cabin. They're about a foot square by 1/4" thick and have a connection lug bolt. About $20 from the orange box store IIRC.
I buried them in small depressions where the ground is less likely to dry out.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
The pipe is copper 3" wast line from the 60s cut out of a building last year it has a thick wall.
bill some of the links were 1/4" but some were 20 gage but I would just buy ground plates if that is better ,
i just need to find them .
Estragon , I know the orange store like the back of my hand and have never seen grounding plates here, but I will look in the am .
I am trying to figure out my utility room now , lots of stuff to go in that room
Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Looks like fun. I am building with adobe, not wood.
-
Adobe , I would like to try that I've been a mason for 35 years.
I built with a lot of stone and concrete but never mud.Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
I lived next to the ocean for a few decades... Just saw so much corrosion, I always planned for the worst.
If they have 20g grounding plates, I cannot say they are wrong.
I am no expert.
- BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I'm going to see what I can get from the ELEC supply house thanks billOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
-
Hi all , I am making some progress , we have been crunching a lot of #.
In the end I have decide to go with a out back flex power one system 3600/48 volt .
It was really a no brainer .
Want to start with 8 gc 215 for now , but upgrade to good RE battery in a few years 400 450 ah .
How much panel do I need for reliable charging in Albany ny for the larger battery .
The panel will be on the roof at 37o pointed south . Thanks in advanceOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
The panels are just 265 watt from AWS .Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
-
Give us your best guestimate of the number of Whrs/ Ahrs you you will use in a day and days of autonomy you desire...
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
I was hoping for around 3200 but looks more like 4000 4200 .
With 2 days storage .
My outback CC will hold 4000 watts and I have room for a array 8 panels wide by 2 panels high soooo I was thinking to run 3 series 5 strings , my quot came in with 265 watts 12 panels .
I don't want to have to add later .
Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed