More array? More Battery? More Generator?
morpho
Solar Expert Posts: 177 ✭✭✭
Ok, forget the generator I am tired of generators!
so I was looking at the current panel prices (shockingly low) and the LA battery prices (still costly) and I have had a truly horrible grey winter so far and have had to run my little generator way too much for comfort.
So I was thinking (always a bad sign) that if on a grey day I have 5 amps coming in on my 3kw array...what if I just add a buttload of panels...say...quadruple my array. I know there are many things to consider, but if I have 5amps coming in now on a grey day and I quadruple my array...I basically would have the same amps coming in as I have on a sunny day. (throttled back to 25amps to keep my batts happy)
What are the downsides of this tactic instead of a better batt bank?
Cheers.
so I was looking at the current panel prices (shockingly low) and the LA battery prices (still costly) and I have had a truly horrible grey winter so far and have had to run my little generator way too much for comfort.
So I was thinking (always a bad sign) that if on a grey day I have 5 amps coming in on my 3kw array...what if I just add a buttload of panels...say...quadruple my array. I know there are many things to consider, but if I have 5amps coming in now on a grey day and I quadruple my array...I basically would have the same amps coming in as I have on a sunny day. (throttled back to 25amps to keep my batts happy)
What are the downsides of this tactic instead of a better batt bank?
Cheers.
11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face
Comments
-
I sell batteries for a living. But I send more customers down the road with the suggestion to buy more PV than batteries, after listening to their story. The biggest single problem that I see is undercharging of batteries, because people all too often buy more batteries when they don't have enough power.......
There is wisdom in the old adage: "Make hay while the sun shines"
I always have more questions than answers. That's the nature of life. -
+1 for more PV.
I don't suffer from lack of power for 8-9 months a year...but man alive those 3-4 months of darkness!
I try to never let my batteries to get below 80% SOC. Basically use the bank to keep the food from thawing through the night etc...and pray for sun in the winter and if there isn't any I fire up my little generator to fill the gap. Basically, I treat it like I don't have any days of back-up. If I could add panels to the system and put less burden on the generator, now this would be great.11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
Generator : gas costs money, take into account losses you are probably throwing away around 70% of every dollar spent, there is wear and tear, maintenance, not to mention labor and noise.
PV: Sun, what little you have right now, is free, losses don't cost you $, maintenance involves cleaning, will probably outlast the generator, and that deafening silence.....+1 for PV?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I'm 'over paneled' and likely even a bit more soon. I think it's smart, particularly if you can pickup deals as you go along....
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
There are 2 kinds of people, those who want solar, and those who want more.
I spent many years repairing other peoples marine generators. That is the last thing I want to do now!
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
I've overpaneled a bit, but still run the generator. At least panel cost has come down some.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
so far so good..nobody saying outright that I am on a fools errand.
Thanks everyone for your insights.
Hey Mike95490:
I see you have a lister cs 6. How is that treating you?11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
Marc Kurth said:I sell batteries for a living. But I send more customers down the road with the suggestion to buy more PV than batteries, after listening to their story. The biggest single problem that I see is undercharging of batteries, because people all too often buy more batteries when they don't have enough power.......
There is wisdom in the old adage: "Make hay while the sun shines"
Fortunately there are a lot more people now who know the folly of that approach.
SMA SB 3000, old BP panels. -
I can assure you that I still see chronically undercharged batteries on a regular basis. Even a well designed system can suffer from load creep. Over time, typical homeowners always seems to find more "must have" items running on the inverter. Folks who design/build their own don't tend to do this, but others most certainly do.
Non technical homeowners don't tend to watch their battery banks like people here do!
I always have more questions than answers. That's the nature of life. -
Ahhh load creep...Yah I have added a strip of heat tape for my water line that is doing my head in! Sucks 3% from my bank through the night. And the Mrs wanted a TV. So we've got one of those now. STOP THE MADNESS!
11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
Looks like I will too be "paneling-up" in the few months. I'm at a marginally acceptable balance with what I have right now: good weather, sunshine, no problem. But, I don't like powering on the generator either on the gloomy days and I agree with everyone's statements above.
I thought morpho asked a very good question: would more panels on gloomy days proportionally increase the amps going back into the batteries? Anybody willing to opine?Paul
in Georgia
System 1: PV- 410w Evergreen, Mppt- Blue Sky Solar Boost, Batt - 225ah Deka AGM, 12v led house lighting,
System 2: PV- 215w Kyocera, PWM - Morningstar PS30, Batt- 225ah Deka GC's, 12v led house lighting, Dankoff 12v water pump,
System 3: PV- 1.5kw Kyocera, Grundfos 11 SQF well pump, 3000 gal above ground water storage, dom water & irrigation,
System 4: PV- 6.1kw Kyocera, Mppt- Outback FM80-2ea, Inverter- Outback FX3648-2ea, Batt- 804ah GB traction, Grundfos BMQE booster pump 240v, Mitsibushi mini-splits 240v, 18k and 15k -
"So I was thinking (always a bad sign) that if on a grey day I have 5 amps coming in on my 3kw array...what if I just add a buttload of panels...say...quadruple my array"
Are you being serious.....quadruple? I would strongly gear your panel addition, everyone agrees this is the right thing to do, towards optimal winter production. I believe that is latitude plus 15 degrees. Summer optimization is latitude minus 15 degrees of course. Plus the steep panels shed the snow and soak up the winter sun to melt the ice off.
Assuming 45 degrees latitude, (I have no idea), then 60 degree panels would be dynamite from Nov-Feb.
FWIW....only south facing panels gather enough solar heat to melt off snow and ice effectively. East and west panels just suck during northern winters.
If doubling the array doesn't do it, I might take a closer look at a propane genset if you can buy bulk propane during the summer....I paid $1/gallon last August. Diesel just doesn't like weather below ~10-15F.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
The lister is the reliable genset, fired on the 1 compression crank this AM in the snow, Panels covered, was getting maybe 100w from 5KW array, under 1" white reflective snow. Should warm up and slide off later today,
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Looking through the discussion, I think I'll also add a couple panels to one side of our system to bring charging up a little on that more heavily used battery bank.
Winter overcast days and shorter charging hours are tough even here in Arizona.
Ranch Off Grid System & Custom Home: 2 x pair stacked Schneider XW 5548+ Plus inverters (4), 2 x Schneider MPPT 80-600 Charge Controllers, 2 Xanbus AGS Generator Start and Air Extraction System Controllers, 64 Trojan L16 REB 6v 375 AH Flooded Cel Batteries w/Water Miser Caps, 44 x 185 Sharp Solar Panels, Cummins Onan RS20 KW Propane Water Cooled Genset, ICF Custom House Construction, all appliances, Central A/C, 2 x High Efficiency Variable Speed three ton Central A/C 220v compressors, 2 x Propane furnaces, 2 x Variable Speed Air Handlers, 2 x HD WiFi HVAC Zoned System Controllers -
morpho said:"...and I quadruple my array..."
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Size your panels for a grey-day on the winter solstice. You'll be set the rest of the year.
~1.5Kw PV in parallel
Morningstar MPPT-60 controllers (2) in parallel
3 Trojan tr-1275's in parallel 450ah total
Samlex 2,000 watt 12-volt inverter hardwired -
I was thinking more like this...who needs room for a car if you have that much power? No power bill, I'd have enough power to run a 12 month greenhouse...I wouldn't have to actually drive anywhere! EVER!
11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
I know quadruple sounds like a crazy thing to do, but if the cost is roughly equal to the cost of a proper diesel genset, and on a cloudy day I get roughly the same amount of power from the array as I would from the genset and the same amount of power from my current array on a sunny day...well then it seems like a no brainer.11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face
-
Mike:
sweet looking CS 6/1. I love the sound those make. I have often thought about getting one and planting a couple of acres of canola and pressing my own oil to feed the beast.11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
Morpho, you did not mention how the 5 amp array is set up... Is it optimized for winter production, the equinoxes or summer production? if it is not the first of the 3, then , yes, at least 2 more oriented and angled for maximum winter production (on Dec 21) would be my choice..
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
The rack is set for winter and I change it for summer. (I'm at roughly 65º Latitude.)
11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
I have array tilt set for winter, and leave it there, summer there is more then enough sun
here's some numbers to size your panel with
Array 5Kw PV (2 arrays, 2 controllers, 3Kw & 2Kw)
Winter cloudy day 1,010wh (Dec 15 2016) rain
Winter sunny day 17,880 (Dec 16 2016, charging up that flat battery)
And we often have a week of solid clouds
average winter usage 7Kwh (house, shop, 2 fridges, 1 freezer)
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
morpho said:The rack is set for winter and I change it for summer. (I'm at roughly 65º Latitude.)
On the bright side, you could attach panels to exterior 90 degree walls and have good effectiveness with almost no snow/ice.....I would think.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
It's true, my rack doesn't even extend to the suggested angle for the Lattitude.
But, today we have sun and I didn't have to fire up the gen. She will be all charged up and hopefully in float just as the sun sets. Then it starts all over again.11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
and i thought my sunlight was severely limited by the mountains... from Wiki... for 65* N
At this latitude the sun is visible for 22 hours, 2 minutes during the summer solstice and 3 hours, 35 minutes during the winter solstice.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
ha...fat fingers...sorry... 55 degrees, not 65! Typing on a phone is pointless sometimes.
If I were at 65 degrees North I would be rapidly packing up and moving south...way south!
11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
morpho said:ha...fat fingers...sorry... 55 degrees, not 65! Typing on a phone is pointless sometimes.
If I were at 65 degrees North I would be rapidly packing up and moving south...way south!
I once lived near 65N. In the winter the sun is so low it's more like a twilight for the few hours it's out. No trees to get in the way though.
Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Well Estragon, you are a far more hardy soul than I am. I am well past my comfort level this far north.
The sun is low on the horizon for sure and unfortunately/fortunately I don't have an over abundance of trees. Though the aspens are starting to make a go of it now that the cattle are not grazing this little section and I'm sure I'll have to cut some down at some point. For now, I am just happy to see something grow here.
11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face -
Are you factoring in the cost of an extra charge controller or two, and wiring, combining and fusing?
-
Mike...that would be crazy talk!...factoring all the variables! HA!
Well, yes and no. I haven't run the numbers, but I know full well there are added costs.
But, I know I am currently dropping a bunch in gas and oil and parts and wear and tear on the generator.
Regarding more CC: I was wondering if it is possible to have the extra arrays on a switch that I can turn on when the extra power is needed - no different than I do with the generator - On a grey day I would only see 20-30 amps coming at me anyway so I don't know if I'd need another CC at all.
I have the whole thing throttled down so the batteries only see a max of 25 amps on a sunny day. (as per the Deka spec) so it may not be necessary to have the extra arrays on a switch. But I'd have to look into how it actually works.
Or...I just get rid of the fridge and the freezer and the TV...I would undoubtedly lose the wife in there somewhere.
HEY! Things are looking up! ...Just kidding dear. ;-)
11.5 kw array - 3 - midnite solar classic 200's - Magnum MS-PAE Inverter - Magnum ME-RC50 remote - ME-BMK batt-monitor - 2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed