? About 3 135 Watt Panels in Parralel
tcvb
Solar Expert Posts: 44 ✭
Will they need to be protected going to the charger?If so can i just tie them in a junction box?and put the protective device on the feeder going to charger?
Thank's
Tim
Thank's
Tim
Comments
-
Re: ? About 3 135 Watt Panels in Parralel
In general, it is a good idea to place a series protection fuse in series with every (string--whether one or 10 panels per series string) when you have 3 or more parallel strings.
The idea is that the series protection fuse will protect a shorted panel or lead wire from getting too much current from the rest of the panels on the string and cause a fire. Instead, the series protection fuse will open and prevent the over current into the failed string...
One or two parallel strings do not need series protection fuses or circuit breakers.
Many panel specifications will tell you what the series protection fuse rating is required.
For example, a Kyocera 135 watt "12 volt" panel (PDF spec. sheet) with Isc=6.79 has a series protection fuse requirement of 15 amps maximum.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: ? About 3 135 Watt Panels in Parralel
I am going to add the same panel to the 2 I have already (in parallel) and wondered how you actually put the fuse in line? Do you just use an automotive fuse type holder or what?
Mine are paralleled at the pole then run the 30' to a 15 amp fuse/disconnect. But, that won't protect a bad module from the other 2.
So, how does everyone put the fuse in line between each module (string)? Thanks.
Tim -
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
Re: ? About 3 135 Watt Panels in Parralel
I think, it's primarilly a code issue.
It was once common to combine them using a distribution block, NAWS still sells them here; http://store.solar-electric.com/16220-2.html
IMHO glass, silicon and even tedar are not very likely to burn/burst into flames before some fine ribbon wire melts and disconnects the panel.
That said, if it's on your roof and has collected debris and dried out... I wouldn't want to argue with your insurance company.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: ? About 3 135 Watt Panels in Parralel
I'm in the UK,could i use RCD breakers in a domestic fuse box?These are circuits that will trip and stop residual currents leaking back,and they are slotted into a distribution fuse box with a switch for breaking all power to the circuits individually or all at once.
Higgins -
Re: ? About 3 135 Watt Panels in Parralel
Higgins
You should use an RCD on the AC out to the house along with (M)CB`s (circuit breakers) same as you get in your house distribution panel, An RCD protect`s against earth leakage type faults, A (Miniature)CB against over current.
For the DC side, you MUST use proper DC breakers or fuses, they are different internally and it can be extremely dangerous to use AC components in their place,
Have a good one
Tim -
Re: ? About 3 135 Watt Panels in Parralel
Thanks Black swan,do you know where i can source the DC breakers and MCB'S in the UK?I have been looking at a few till it dawned on me that they they were AC types.Also trying to find uk equivalent hardware in place of American eqpt as most of them are on here thanks!
Higgins -
Re: ? About 3 135 Watt Panels in Parralel
Hope the Mod`s don`t mind, a very similar name that I have heard good things about but have never used my-self, http://www.windandsun.co.uk/
Have a good one
Tim -
Re: ? About 3 135 Watt Panels in Parralel
Wow, I wonder who started business first? And infringements? At least there is a big pond inbetweenPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: ? About 3 135 Watt Panels in Parralel
quote from our us windsun site,
"** 2010 is our 31th anniversary - 1979 to 2010. **"
5 year discrepancy. -
Re: ? About 3 135 Watt Panels in Parralel
I don`t use them directly, As I understand most of the OB European equipment now comes through them, Mine used to come (2nd) through Barden UK then onto Europe (Barden are also Rolls European distributors) but Barden (so I am told, try to buy OB through them) now do not deal "much" with OB and punt you on to windsun, politics I presume ?
Tim -
Re: ? About 3 135 Watt Panels in Parralel
Cheers Tim,good link that,
Higgins
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed