Manual generator start vs AGS generator start (and genset safety)
The reason I ask is that I've had a few incidents where manual input of power to AC2 by just throwing the AC2 breaker on a running generator bogs the generator down on qualification by the XW, despite having set the XW Charge AC breaker to the correct initial value.
Never seem to have that problem via the AGS software start route. Does the AGS route into XW charging have a softer start built in, or?
Even via the AGS method I run the startup process under supervision, gradually ramping up the AC breaker setting until the generator settles to each load increment. Wish the AGS or XW software had a linear charging current ramp up function, but maybe I'm missing something....
I'm thinking of adding a POE camera and mic to my fire resistant generator shed to make remotely supervised generator operation observable to confirm generator successful start and operation. That will improve safety of remote starts at our offgrid island site in the PNW. Despite 8 kW of solar and 30kWhr of good LiFePO4 bats we still occasionally need generators in winter.
There's already a 12VDC propane cutoff solenoid that only allows fuel to be supplied when the genset is commanded to be on, and gravity venting paths to route any gas leakage safely outside.
Exhaust is securely routed outdoors, with positive fan ventilation powered by genset and CO/Fire detectors. Looking for a good LAN networked remote reading CO/Propane/Fire alarm, if those exist.
Offgrid in cloudy PNW
Full Schneider system with 18 REC 420W panels, 100A-600V controller, XWPro, Insight Home, six Discover AES Rackmount 5kW batteries, Slimline enclosure, Lynk II, AGS, H650, H2200, H3000 (Propane conversion on Victron AutoTrans with Gen Line 2 wire AGS on AC1), Kubota 4500, Onan 7500 (on second AGS and AC2).
Comments
-
Here are a couple of internet connected CO and Propane alarms found on Amazon:
1) Google Nest Protect Fire and CO $$$ (C$299)
https://www.amazon.ca/Nest-Protect-smoke-carbon-monoxide/dp/B00XJEGEI6/ref=sr_1_1?crid=2TL5GOUINPB5F&dib=eyJ2IjoiMSJ9.WO8gSt3B53TU1foWdzifoyIpHJXZyVq6cPFP6T-Fh78BA6I0oZRxKPu3i4rbrhpZvg0ESYGkbIBBTFJI1yAC9BbqbpFRY-dDqigzvhMirAm8wwY1xLIOuTHNQKR6SpeHU9a2MU1nmK5eA8Ok2Ay7Tmbf6MZOW29C3CxLLkeC-qfK_vrDIzgkIpvQ3S6yZUNPtBzu4XEtk8c9htfISwHf18EUlStmJbvXniak5h3KwFShfhUIWwSiIyzCIeN2Uoup9bZYUSd33uykZmI7UaKDg9uZ0sc5D2VcYcBcXHDqlHg.UZX48ONTIBngsGgHgrJe2jbZaWIl4bnninmL06jTUrY&dib_tag=se&keywords=Google%2BNest%2BCO%2Balarm&qid=1762122827&sprefix=google%2Bnest%2Bco%2Balarm%2Caps%2C139&sr=8-1&th=1
2) Sanfoelek Gas Leak Detector $C38
https://www.amazon.ca/Sanfoelek-Powered-Temperature-Display-Kitchen/dp/B0FP4K1SCL/ref=sr_1_5?crid=2AD53JUCG9WGZ&dib=eyJ2IjoiMSJ9.sbBQVn1TSLFJOVcjvJl1b-Pf9tDVk1LyBbsgkEgIYFyXbRMH7n9C_FcYxe5QPTvOtwwq1aqoVXb-uXbC7mqaSQHhDjTb1O5WbrQ7rgk_O-tpZ1-OsWyeZ_w4E8ah8Z8c-vy-QZ7Z36IbYQTdFXrRHzCCr2ul1a0Av2H5gD7SjID2V2FkjqH68hKu6xMV--EgFEwypt00iOFsLxBIq4mULmoG3gZrn-PEXz1BYYugOaNz-2Z11lVWQDK8r887dF4YV11SxIVPs5-WiaDZtgsF0jxP_ehMTdYyFD2elJcyOLk.H1BTbEMDRLmKYORcqCKbai_OVJ6pIxX_p5UcN8HaMlk&dib_tag=se&keywords=Wifi+Propane+alarm&qid=1762122561&sprefix=wifi+propane+alarm%2Caps%2C161&sr=8-5
Offgrid in cloudy PNW
Full Schneider system with 18 REC 420W panels, 100A-600V controller, XWPro, Insight Home, six Discover AES Rackmount 5kW batteries, Slimline enclosure, Lynk II, AGS, H650, H2200, H3000 (Propane conversion on Victron AutoTrans with Gen Line 2 wire AGS on AC1), Kubota 4500, Onan 7500 (on second AGS and AC2).
-
"Does the AGS route into XW charging have a softer start built in, or?"
My original Outback VFX3648 and the newer VFXR3648 both soft load the genset, whether with AGS or manual. I can't imagine why there would be a difference? I don't know about the Schneider but why would the method change? To me it is easier on both the inverter and the source to soft load.Off Grid. Two systems: 1) 2925w panels, OB VFXR3648, FM80, FNDC, Victron BMV-712, Mate3s, 240 xformer, four SimpliPHI 3.8; 2) 780w, Morningstar 30a, Grundfos switch, controller and AC/DC pump, 8 T105. Honda EU7000is w/AGS. Champion 3100. HF 4550, Miller Bobcat. -
Hi There
In the XW there is a generator warm-up time in the XW settings, but that just provides a waiting period after start till the load is put on. In order to have the generator deal with the load and settle to it's rated power output after issuing a "generator ON" command, I need to manually bump up the load gradually by increasing the "AC2 Breaker" amps.Offgrid in cloudy PNW
Full Schneider system with 18 REC 420W panels, 100A-600V controller, XWPro, Insight Home, six Discover AES Rackmount 5kW batteries, Slimline enclosure, Lynk II, AGS, H650, H2200, H3000 (Propane conversion on Victron AutoTrans with Gen Line 2 wire AGS on AC1), Kubota 4500, Onan 7500 (on second AGS and AC2).
-
FOR EVERYONE READING THIS THREAD there is a miss communication here. Please do not mistake a soft start device for bumping up your inverter output little by little = however that works. A soft start device can not be made by bumping up inverter output. Oh, BTW, what happens to everything else powered by the inverter?Off Grid. Two systems: 1) 2925w panels, OB VFXR3648, FM80, FNDC, Victron BMV-712, Mate3s, 240 xformer, four SimpliPHI 3.8; 2) 780w, Morningstar 30a, Grundfos switch, controller and AC/DC pump, 8 T105. Honda EU7000is w/AGS. Champion 3100. HF 4550, Miller Bobcat.
-
Sounds like you need to limit the DC charge amps, not the breaker size amps. This is often caused by a generator that is slightly out of spec until it warms. Which one does this?
Remember you are dealing with a charger that is built for a 60 amp ++ 240 generator. Yes XWP soft starts but the bad part is when you have a generator problem, XW will not soft stop, after doing this alot, fried relays are next! Be careful ! You could be the next one 😒
I do not understand "bump up the load by increasing AC2 breaker size? Breaker size is a the limit on the load as is DC charge amps. Probably saying the same thing differently."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Hi Dave
If I understand it right, the XWPros seem to have two obvious methods of limiting the generator loading when charging a battery off a genset. I use the first - is the second how you suggest to limit the "DC charge amps"?
Method 1) AC Settings: Setting the "AC2 Input AC Breaker Size" which appears to limit the input draw on each leg of the 230VAC AC2 input to 80% of the entered breaker size amps. At the moment, only my Honda 3000 is setup with the AGS. When I'm using the propane converted Honda 3000 through the Victron Autotransformer I set AC2 breaker to only 4 amps at first for generator startup, then gradually bump that up to 14 amps which gives about 2400 W of charging.
Method 2) Battery Settings/Maximum Charge Rate: "Sets the allowable percentage of the maximum DC output current that is available to the charger" This seems to be intended to be some sort of battery protection current limit. At the moment on my XW this is set to 100% (Does that mean in the absence of other control it would output 60 amps when charging?)
Thanks, Graham
Offgrid in cloudy PNW
Full Schneider system with 18 REC 420W panels, 100A-600V controller, XWPro, Insight Home, six Discover AES Rackmount 5kW batteries, Slimline enclosure, Lynk II, AGS, H650, H2200, H3000 (Propane conversion on Victron AutoTrans with Gen Line 2 wire AGS on AC1), Kubota 4500, Onan 7500 (on second AGS and AC2).
Categories
- All Categories
- 233 Forum & Website
- 141 Solar Forum News and Announcements
- 1.4K Solar News, Reviews, & Product Announcements
- 199 Solar Information links & sources, event announcements
- 899 Solar Product Reviews & Opinions
- 256 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 656 Solar Water Pumping
- 816 Wind Power Generation
- 624 Energy Use & Conservation
- 621 Discussion Forums/Café
- 314 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed