Morningstar pwm
![mountainman](https://w7.vanillicon.com/70874897ac8ef0f0e9b032d6a2cfb992_100.png)
mountainman
Registered Users Posts: 442 ✭✭
I see Morningstar 45 amp and 60 amp
Pwm controllers. That look like the mppt
Controller. But a friend of mine said he has a Morningstar TriStar 30 amp pwm. Has anyone heard of these? I can't find one listed anywhere
The one Im asking about looks like this.
![](https://us.v-cdn.net/6024911/uploads/editor/rc/m5ws4k1v1eqv.jpg)
Pwm controllers. That look like the mppt
Controller. But a friend of mine said he has a Morningstar TriStar 30 amp pwm. Has anyone heard of these? I can't find one listed anywhere
The one Im asking about looks like this.
![](https://us.v-cdn.net/6024911/uploads/editor/rc/m5ws4k1v1eqv.jpg)
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Comments
-
here's the morningstar lineup
https://www.morningstarcorp.com/compare-products/?product_1=2621&product_2=&product_3=
and the 30A prostar https://www.morningstarcorp.com/products/prostar/
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Yes, MorningStar still has the Tristar MPPT 30 Amp unit. Here is our host's listing:
https://www.solar-electric.com/morningstar-tristar-ts-mppt-30.html
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
So they never made a 30 amp pwm. Like the one in the pic?2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
I wouldn't be shocked to learn someone other than Morningstar made a 30a that looks like MS made it. I've seen other knock off gear whose makers weren't shy about blatently copying.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I am sorry, I missed read your post... You looking for a PWM 30 amp version.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Looks identical to a 45 tristar pwm even has all the Morningstar labels but with 30 amp?2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
A bit off topic. with 100f temperature
What would you recommend as the lowest vmp voltage to charge a 24 volt battery using pwm?2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Im guessing since 12 volt panels are 17-18 vmp. Then would it be 34-36 for a 24 volt battery? Anyone.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
mountainman said:Im guessing since 12 volt panels are 17-18 vmp. Then would it be 34-36 for a 24 volt battery? Anyone.
That's correct for lead acid batteries they need a VMP higher than the maximum battery voltage required to enable current to flow, at higher battery temperatures the voltages required would be lower unfortunately so is the PVvoltage in high ambient temperatures, this is why 72 cell are recommended as the 60 cell panels are marginal, especially with FLA where equalization may be required.
The Morningstar string calculator will clarify this if 60 cell panels are input for a 24V nominal system, however they don't include battery chemistry into the calculation. With LFP the story is not the same, 60 cell panels would work just fine since the voltage required is lower and there is no need for equalization . Perhaps thy should update the calculator to include this, then the use of AGM, which don't need EQ may allow their use. This was a mistake I made in the beginning, although my observations were that it can work, but I did change to MPPT for the 60 cell and use 72 with the PWM.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Look up Fangpusun. They have cloned many Outback, Victron and many other higher end solar products.Estragon said:I wouldn't be shocked to learn someone other than Morningstar made a 30a that looks like MS made it. I've seen other knock off gear whose makers weren't shy about blatently copying.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Fangpusun said that this is no longer available. So probably a knock off.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
-
Was speaking of a 30 amp pwm Tristar2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
mountainman said:Was speaking of a 30 amp pwm Tristar
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
That's what I was thinking my friend must be mistaken about what he has.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed