Hi all , quick question
I need to run a wire from my inverter to my generator shed , it’s about 35’ thru the garage and out the wall .
I need to run under ground 65’ to the shed , could I run this wire in conduit or should I buy direct burial cable , I only want to do this once .
I have a roll of 6g wire on hand .
I also want to run some 12 /2 so I have some light and power out
I’m assuming I need some kind of a lead to run from the box on the wall in the shed to the generator and maybe a Power disconnect on the wall of the shed out side
Thanks in advance John
Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
I would use conduit, it's easy to work with, has fittings, and you don't need special cable. The hard part is digging the trench.
I too would use conduit as long as the total included bends are less than 360° between junction boxes.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
As long as you are going to dig a trench, put in two runs of conduit. It is cheap and you just never know what you’ll want to run next...more electric, comm cables, other...Off-Grid in Terlingua, TX
5,000 watt array - 14 CS 370 watt modules - 7S2P. HZLA horizontal tracker. Schneider: XW6048NA+, Mini PDP, MPPT 80-600, SCP. 390ah LiFeP04 battery bank - 3 Discover AES 42-48-6650 48 volt 130ah LiFePO4 batteries -
So I can run regular 12/2 and 6 /2 wire with ground , Do you think that would pass ny state Electrical inspection ?
Around here every one seams to run individual wires black white red and green ?
The reason I’m concerned about the type of wire Is every time I dig up a conduit it’s full of water ?
There is condensation plus water gets in the pipe when the guys are working on it .
How large a generator can I run on a 6 g wire at 100’
I have a 2800 watt Honda now but may move up to a 10000 watt diesel with 240 volt I’m not sure what to do with the extra leg of the genaratorOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Generally speaking, if there are two separate sources they shouldn't be in the same raceway, this becomes a little confusing as one won't be energized whilst the other is, to avoid the ambiguity running each in a separate conduit would eliminate the confusion as both are physically isolated, either way a ground bonding is required in each conduit of a non metallic raceway, assuming PVC
@wellbuilt
The 10000 watt genie is capable of about 42 amps per leg at 240 volts. I believe a 6-2 romex type cable is rated at 55 amps. At 100 feet there is less than 2% voltage drop. Probably not very efficient to load down only one leg of a 240V generator. Might be better to stick with a 120V model. Do you need that much power?
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Hi rick , I probably don’t need that much power , but I really like the kabobs equipment and there are a lot of 10000 watt kabobs diesels around here for sale in good shape for short money .
So how large a genarator could I use on the 6g wire, I know I dident Guess the size of the wire , I must of got the information some where , I may of figured to run one leg of the 240 volt to the inverter and the second to power some 240 volt equipment .
Let me ask you this , is the 6g wire large enough to cover the serge ratting of my 36/48 out back inverter , So 7200 watts ?
I use the 6g wire from the inverter to my panel 3600 watts x2 7200watt serge it’s looking like my wire is to small for the inverter load .😳
Do I need to change out the wire? Thanks for the reply johnOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Yes, it's big enough. The 6-2 cable is more than adequate for your needs. I suppose you could use a 240 to 120 volt transformer if you want to go with a 240 volt generator.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
I just haven’t seen any large 120volt genarators?
Ill just use the wire that I have for now.
and dig in a larger wire if I need it when I live there full time.
The digging is the easy part for me . Thanks every one for the help JohnOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
No you can not use "regular 12/2 and 6/2" in the conduit when running it underground.wellbuilt said:So I can run regular 12/2 and 6 /2 wire with ground , Do you think that would pass ny state Electrical inspection ?
Hi coach dad , that what I was afraid of I’ll have to get some more wireOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
Hi all, I’m still working on my generator shed , I’ve run 2 leads out to my generator shed a 6/2 and 12/3 direct burial cable , the 6/2 I run to my generator the 12/3 is for lights and a few outlets .Do I need outside disconnects before I enter my 8x10 shed ?If i was dealing with a garage I would think yes , a generator enclosure I would think no ?A shed ???I m not sure if the 6/2 generator cable passes power both ways , will my generator plug be hot if I have the breaker on for generator input ? I would hate to have a suicide plug laying on the floor of my shed .I ordered 6/3 cable from my supply house when it came in it was just 6/2 I grabbed it because I would like to get done before it starts snowing but I’m having second thoughts now ?Could I run a larger 6500 watt generator 240 volts in the shed and convert it to 120 volt using both legs of the generator out put .
The only 220 power I mite need will be for the well pump and I plan to run that line to the well head later on when I hook up the pump .
Thanks for the reply’s JohnOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
The feed to the shed 12/3 would be a branch circuit of the main distribution so it doesn't require a disconnect outside. The generator 6/2 would be isolated via the inverter's internal transfer, therefore it wouldn't be powered when the generator is not running.
The circuit breaker for the generator should be at the generator itself being that it is the source, you didn't mention location so thought I'd point it out
Using a 240V generator you should be able to feed that into the inverter's AC input, the inverter output would provide a split phase output giving 120V, assuming that the Outback 3648 is configured as such.
Thanks mcgivor , my generator has a breaker on it , and I have a breaker on the power panel in the utility room .Soooo I need a small one breaker box with a 20 amp gfi breaker or could it be a standard breaker ?
for my 2800 watt Honda generator .Could I just run a 4’ 10 or 12g flexible lead from the breaker box to the generator?
The shed is 8x10 and the generator is in the rear of the shed the breaker will be on a side wall and for now I will have a standard 3 prong plug .I don’t think my out back inverter can take 240 volt from the generator in put line , I do have a grid in put but I don’t think that will work to charge at the same time .Could I step down the power at the generator from 240 v to 120volt and use a larger generator if the need be .Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Actually I'm surprised looking at the specifications that the Outback 3648 accepts only 120V as the input and is a single 120V output, so a transformer would be needed if a 240V generator were to be used to supply 120V.
Since the maximum charging current of the inverter is 45A or 2450VA why would a larger generator be needed other than to power loads in pass through?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
The fx can be series stacked for 240v, but yes, a single unit would be 120v only.
I have a pair of them and a 4kw generator, but I have it wired for 120v output and the inverters parallel stacked master/slave. I use a step-up for a 240v pump. As well as the 4kw, I can alternatively charge with a honda 2000i by throwing an A/B switch in the genshed and reducing max settings on the inverter to avoid overloading.
Maybe the genny can be rewired for 120v instead of using a step-down?Off-grid.
Mcgivor yes I just want to charge battery’s and run a washer dryer , with some lights and radio/ tv on , I don’t think my Honda 2800 generator can do that for me .
Estragon , I don’t own the larger generator yet but I really need to figure out the ins and out now .
Thanks for the reply JohnOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .