10.4 amp air compressor
brewer
Registered Users Posts: 21 ✭✭
I'm a beginner on learning how much draw certain products use. Just got a 10.4 amp air compressor that I want to use on my simple 12 6v battery, 24 volt system I'll only use it when it's sunny.
Is this a reasonably low draw compressor?
Thanks.
Is this a reasonably low draw compressor?
Thanks.
Comments
-
What voltage is the compressor, what capacity are the batteries? These details are nessersary to begin a discussion.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
120V How do I figure battery capacity? I have 12 6V batteries. 4 rows of 4 in parallel.
Thanks -
Remember starting current for motor loads is 10-100 times higher than running current, so the battery and the inverter need to be able to handle that starting current. Compressors are often even harder to start, if they have to start against significant head pressure. Tony
-
brewer said:120V How do I figure battery capacity? I have 12 6V batteries. 4 rows of 4 in parallel.
ThanksOuch. Massive parallel (more than 2 banks) batteries.for 12 batteries, you have 2 in series, and then 6 parallel sets.read up about about parallel issues here http://www.smartgauge.co.uk/batt_con.htmlto figure capacity, you need the voltage & Ah of the battery, like a golf cart battery is often 6v, 200ahif you had those as your bank, each 12v string (2 in series) is 12v 200ah6 of those in parallel gives you 12V , 1200ah. That would properly require about 120A of charge to keep the batteries healthy,That battery bank also can be measured in Watt Hours, and would be 14,400 watt hours total.120A @ 14V = 1680 harvested watts of PV powerIf you had configured that to be a 24V bank you still have 14,400wh but 24V , 600ah, needing only 60A of charge current (Just a single charge controller) and still needing 1680 harvested watts of PV power, but you can use smaller wire gauge.Now, getting to starting that compressor @ 120VAC10A @ 120V (roughly) is 1200 watts. Add .6 power factor, and you are at about 2,000 watts that the inverter HAS to supply out of phase because of the inductive motor. At 24VDC, that's about 85A coming out of the battery, constant (till the compressor shuts off)Starting that mess, 10x is a good number, so your inverter is going to have to be pretty stout to handle the starting load.(that's why I have a 6kw inverter to run a 1/2 hp pump on a 48V system, I cannot afford to not pump 4,000 gallons daily for trees and my livestock water)Your cables have to handle close to 850A dc, while starting, without voltage sag, or your inverter shuts down from undervoltage, not overload. The shorter the inverter cables, the betterDouble those amps for trying this at 12V and you see it's going to be nightmarish.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
If it doesn't have one, adding an "unloader" will help some. But I don't know - maybe every compressor has one. Another approach is a smaller compressor, perhaps with a very large tank (if you need lots of CFM). I see a Dewalt at 2.6 amps.
I am available for custom hardware/firmware development
-
Working with 12VDC to 120VAC is a 10:1 ratio, in other words 10.4A at 120VAC is 104A at 12V, start or inrush is significantly higher which may well overwhelm the batteries which are of unknown capacity at this stage. To add to the equation induction motors generally have a poor power factor which may not affect the battery itself but will have influence on the generation source, the inverter.
Realistically it would be better to use a generator to power the intermittent load of a compressor, but that's only an option, 12V systems should be limited to ~1000W maximum of non inductive loads.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Compressors are "difficult" loads... They typically have high starting surge requirements, and actually do a lot of work (compressing a gas to much higher pressures and lots of volume of air moved). All these make for a very difficult load for solar/battery power.
The other big issue is that Amps and Amp*Hours are a partial power/energy unit. You need to know the working voltage too. As the guys above talk about above:- Power = Voltage * Current (power is a rate, like miles per hour)
- Energy = Voltage * Current * Time (energy is an amount, like total miles driven)
- 10 amps * 12 volts = 120 Watts
- 10 amps * 24 colra = 240 Watts
- 10 amps * 120 volts = 1,200 Watts
- 10.4 amps * 120 volts = 1,248 Watts
- 1,248 Watts * 1/0.50 Power factor starting * 5 starting current = 12,480 VA (similar to, but not Watts) starting load
- 12,480 VA / 2.0 amount of "surge rating" for good AC inverter = 4,160 VA (Watt) minimum AC inverter Rating
Then there is the battery bank... You have a typo in your post... 12x 6 volt batteries or 4x4 batteries in series parallel--Or 16 batteries... Lets say you really have 4s x 3p bank and the batteries are "golf cart" type at ~200 AH each. such a battery bank would be 24 volts @ 600 AH.
Using our rule of thumb for the maximum AC inverter supported by an XX AH by YY Voltage bank... Our typical rule of thumb is a 500 Watt inverter for every 100 AH @ 24 volts:- 600 AH (@ 24 volt) bank * 500 Watts per 100 AH = ~3,000 Watt suggested maximum inverter
- 1,200 AH * 24 volts * 1/0.77 panel+controller deratings * 0.10 rate of charge = 3,740 Watt minimum solar array
- 3,740 Watt array * 0.52 off grid system efficiency * 5.0 hours per day = 9,724 WH per day (this is not a "small system")
- 9,724 WH per day * 1/1,248 Watt load = ~7.8 hours per sunny day
- 1,200 AH * 24 volts (or 600 AH @ 48 volts suggested) * 0.85 AC inverter eff * 1/2 days storage * 0.50 max discharge = 6,120 WH per cloudy day suggested
For construction of a home, typically, a genset (and/or gasoline driven portable compressor) is probably more cost effective during construction, and design/build your off grid solar power system sized for you completed home.
If you are living on site, a small off grid power system (maybe a 1,000 WH per day for lights, laptop computer, cell phone, RV water pump, etc.) is a better option (for overnight quiet time) and use solar+genset to charge during the day when work is done/more energy needed.
If you are running a full size refrigerator (vs a portable smaller propane fridge or blocks of ice), then you are probably looking at a minimum of 3.3 kWH (3,300 WH) of off grid power per day.
I will stop here... Questions, answers? The above is a bunch of guesses for a full time off grid system for long term use... May not apply to your needs.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thank you for all the info. I'll now be researching it all. At this time I'll run the genny for the compressor.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed