Schneider Energy Monitor
faccnator
Registered Users Posts: 35 ✭✭
Solar is bringing in 347W, battery is bringing 158W,
and the load is 74W. Never shows the battery being charged from Solar. Any ideas? -
Also the MPPT is in float and the battery monitor is showing 82% charge. What am I doing wrong?
Is this a new install? You may have the shunt miswired. Is the sun out as the input voltage is too low?"we go where power lines don't" Sierra Nevada mountain area
faccnator said:Also the MPPT is in float and the battery monitor is showing 82% charge. What am I doing wrong?First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
I’ve looked at the shunt 100 times and I swear I have it wired the correct direction but I’m going to swap the leads for good measure. I’ll report back
Now the flow
is backwards
Why is the DC input to the MPPT so low 53.3V, this should be somewhere closer to 100V, battery 51.2V float? float should be ~54V,.assuming 48V nominallead acid.
How are panels configured and what are the specs?
What are the settings for th MPPT?
What battery type is in use?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
McGivor, that was at dusk. This is now at night. With the swapped shunt leads. This is even more wrong.
faccnator said:McGivor, that was at dusk. This is now at night. With the swapped shunt leads. This is even more wrong.
That would make sense being evening didn't notice the time on the screen shot first time, but those are indeed some strange numbers on the graphics, appears the shunt is either not calibrated correctly or faulty.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Just to be sure... are there any negative wires other than the shunt to battery wire on the battery side of the shunt (eg. DC loads, meters, other inverters)?
How/where is the system grounded?Off-grid.
This morning. Rewired the shunt. Check the negative wires. Why doesn’t the battery monitor know when the mppt is charging?
Just thought I would follow up. I had the solar charge controller wired to the wrong side of the shunt. Everything has been working great for a week now! Thanks for all the help everyone!
- 228 Forum & Website
- 653 Solar Water Pumping
- 618 Discussion Forums/Café
