Charging battery’s I figured I could charg
I thought I would start a new discussion
I have 3 295 watt solar panels in series now , would that be enough power to float my16 gc215 battery for 48 volts at 430ahs ?
The battery’s have been sitting for 4 weeks now and I have been charging them with 2 car chargers at 12 volt on the weekends to keep them up .
I rigged up the 3 panels to a water tank for now I get sun from 800 when the controler wakes up till about 600 when it tappers off .
I don’t want to risk 3 more panel , I have 3 large bears that like to walk my pavers across the side of the house and it would be easy to just have some one walk of with them .
It looks like it will be 5 weeks before I have the time to put them on the roof .
I figured I can bulk charge from my genarator for now when I get it hooked up .
Could any one tell me how much power my flex power one uses wile inverting ?
It seemed like it drained the battery’s over night kinda fast with a small 20 watt fan and a few led lights
my battery dropped from 100% to 93% in 5 hours then from 93% to 85% over night ?
Seams like a lot ? This was on 8 gc215 ah 48 volt battery’s .
Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
State of charge is difficult to accurately monitor, if done by voltage, very inaccurate, if done by shunt resistor, amps in versus amps out, somewhat accurate. There are some points I would like to make which may seem judgmental, but the intentions are not, don't use a system which is not complete, charging batteries to different levels with car chargers will lead to imbalance, which will rear it's head later on, this can be corrected but best not to develop the problem in the first place. Never underestimate loads, what seems like a minor load can, with the inverter self consumption actually be a major load over time.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Need more details (model number of inverter?)... For a generic view, you can see how low loads on a large AC inverter, the efficiency plumits (basically falls at less than ~2kVW loads for the larger Outback inverters):
http://www.outbackpower.com/downloads/documents/integrated_systems/flexpower_radian/flexpowerradian_specsheet.pdf
Mcgivor I’m not really trying to use the system I thought this was going to move along faster then it is .
I bought the battery’s sooo I’m in the game now .
I have to deal with it .
I think I should have the utility room finished up in the next week or so .
I just need to float the battery some how till I get all the panels on the roof .
So is 885 watts going to float my 430ah battery.
I have a flex power one 3600 watts 48 volt inverter with flex max80cc
I have 24 295 watt panels .
I will put panels on the roof and some on the ground I’m thinking 18 panels on the roof
I will addaseconed CCOut back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
If you don't put any load on it, yes. You can verify by measuring voltage after the batteries sit for say 6 hours with no activity (load or charging).I am available for custom hardware/firmware development
That is good news
so will 3540 watts 12 295 watt panels charge my 430 ah battery ?
If not how many should I use .Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Assuming you have a 48 volt @ 430 AH battery bank (not sure which batteries you have with a quick search):
- 3 * 295 Watt panels = 885 Watts
- 58 volts charging * 430 AH * 1/0.77 panel+controller deraring * 0.01 rate of charge = 321 Watt array minimum Float charging
- 58 volts charging * 430 AH * 1/0.77 panel+controller deraring * 0.05 rate of charge = 1,605 Watt array minimum (weekend/seasonal usage)
- 58 volts charging * 430 AH * 1/0.77 panel+controller deraring * 0.10 rate of charge = 3,210 Watt array nominal (full time off grid)
- 58 volts charging * 430 AH * 1/0.77 panel+controller deraring * 0.13 rate of charge = 4,173 Watt array typical "cost effective" maximum
Brooklyn
Measured in kWh/m2/day onto a solar panel set at a 49° angle from vertical:
For July, the average day's harvest would be around:Jan Feb Mar Apr May Jun 3.31
4.03
4.74
4.94
5.10
5.28
Jul Aug Sep Oct Nov Dec 5.21
5.16
4.93
4.47
3.39
3.08
- 885 Watts * 0.52 off grid system eff * 5.21 hours of sun per day = 2,398 Watt*Hours per day "July"
My 3500w Outbacks are also pigs with small loads. If I leave on overnight to run the AC fridge, my 350ah@48v bank gets to ~85%. I suspect it wouldn't be much better running a few lights and a fan. Running pretty much anything seems to take at least a couple of amps.Off-grid.
Bill All the bears in Brooklyn are in the zoo or on the ball field .
In December I have 2.75 so not to good really ,
I’m hi up and it seams very bright especially with snow on the ground .
My controler is rated for 4000 watts 12 x295 =3540 watts could I add 15 x295 =4425watts ?
How much solar is to much .
Could I add more panels, say a extra ? 12 x 295 watt on a second flex max 80 for low sun days I don’t know how much it would help .
Estragon , 85% seam crazy high , 2500 watts ? I was told the system would draw 800 watts a day , I guess it is what it Is . How much power is the fridge drawing ?
I don’t think my lights , fan , tv and I phone charger draws more then 70/80 watts.
I was running for 14 hours with mixed loads but 10 hrs I had just a 20 watt fan and 2 led lights 6 watts each .
I’ll have to just try my inverter with a light burning for 12 hours and see what I get .?Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Remember:
Watts = Rate (like miles per hour)
Watt*Hours = Amount (like miles driven)
So, from a system point of view, you need to know your peak continuous loads (like 2,000 Watts of peak loads--Well pump, etc.).
And then there is the hours per day you run your load... For example, a full size energy star rated refrigerator/freezer may run 1,000 to 2,000 Watt*Hours per day... An example of what a "mixed cycle" might look like:- 120 Watts * 0.50 duty cycle * 24 hours per day = 1,440 Watt*Hours per day (frost free refrigerator/freezer)
With a larger inverter, it may take 40-50 Watt just turned on (50 watts * 24 hours per day = 1,200 WH per day). Then add the "20 watt load" and ~85% efficiency (20 watts * 1/0.85 = 24 watt on DC bus, plus the 50 Watt tare load--purely an example).
Remember there is also a 50 +/- full cycles to most batteries break in period before they will stabilize, but worry about that later, get those 3 PVs working and add more asap... What are the (manufacturers charging ?) specs that you are using?ps a 20 Watt fan over 14 hours uses at least 280 Watt [*Hours or 280 WH] of power at ~50 Volts = 5.6Ah from your battery or about 9.6Ah for 24 hours.Add all the items together your 80 W yields 80*14= 1320Whr and that is equivalent to a fridge's draw for the whole day in cooler weather[edit: BB.]
I’m not to worried about the % of battery used , after thinking about it I was running on half my battery bank for 14 hrs
my CC went to sleep around 600 and the sun hit the panels at 800 but did not start charging till 930 when It turned on ,
so 151/2 hours really .
I did not want to have to turn my inverter off at night , it’s cool in the house it stays about 67o even when it’s in the 90s for days .
I am hopping to stay with my gc battery’s but I’m making the battery box to fit 16 l16 for more power when we live there full time just in case .
So how much solar power is to much ? I have 66 recesslights 400watts if I turn them all on , I can dim them and save 150 w I think I can live on 3000watts a day plus a frig and inverter loss 5500 watts I think my bank should provide 590 watts for 2 days .
I bought the out back system from our host on there recommendation .
I was hopping to charge the battery’s in the winter on cloudy days run the regular house loads and be able to start my frig and cycle the washer and dryer all at once.
Read post 11 again wattage is not a measure of consumption without a time base included.
edit missed per day, so 3Kwh or 5.5 Kwh per day1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Yes thanks mcgiver 5.5 KWHs per day .Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
@wellbuilt
You ask, how much is too much. It's really determined by the batteries. Your 430 amp hour bank can take a max of about a 60 amps, that's a charge rate of about 13%. 12 of the 285 watt panels would produce this much power under perfect conditions. However, in the real world, the output would be 20% to 25% less, so I would suggest installing 15 panels and tweak the system later if you need to.
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
West branch ,
east penn was not much help .
The girl that answers there tec support line was not very technical , I would ask a question and she would have to ask some one behind the scenes .
She was very sweet but not a lot of help .
I copied some set points from some one on line with the same battery’s figureing he must know more then I do at this point .
Rick Estagon and Mcgiver helped with the set points in a different thread .
The battery’s are deracell gc 215 from sams club .
Rick ,
so you think my fm80 cc would be ok with 295x 15 = 4425 watt of solar ?
The controlers max wattage is 4000 watts ?
The guys at Arazona wind and sun told me that they Regularly use 4700 watts of solar on that controler but he was the only person that has said that .
I don’t want to add a second controler for 3 panels would it be ok to run 2 banks of 9 panels on 2 fm80s and limit the amps on the controler?
This would give me more power on cloudy days and in the Future if I upgrade my batteries are 16 l16 I would already have enough power to charge them .
I bought 24 panels for a good price and I figured I would use 18 for charging battery’s 5 for sucking water from my 800’ deep well and one extra ( just in case some one butter fingers a panel ) the roof is walkable for trades men 9 on 12 .
9 in 12 is walkable? I realize these days everybody uses fall arrest gear but 9 in 12 would be more like rappelling to me.
Yes, it's definitely ok to have 4425 watts on the FM80 and the charge current can be limited if necessary.
With lots of panels relative to bank size, what's likely to happen most days is the bank will get fuller with lower morning sun, likely hitting absorb well before full sun around solar noon. In absorb, the panels won't be producing at capacity anyway unless you're running lots of loads.
I have 18 x 250w panels = 4500w STC for a 350ah bank on a pair of classics and it works fine.Off-grid.
Batteries, weather, season, depth of discharge will all play a part in the equation, having more than needed is useful when the days are short and gloomy, Rick is probably about right given geographic location, during periods of excess a string could always be turned off to reduce current and some controller can limit current to a desirable level. With similar loads in the tropics I'm able to get away with 1500 w rated PV, for what that's worth, probably your peak summer output, in terms of production, only year round. Design for the lowest winter months and adjust accordingly.Raj174 said:@wellbuilt
You ask, how much is too much. It's really determined by the batteries. A 430 amp hour bank can take a max of about a 60 amps, that's a charge rate of about 13%. 12 of the 285 watt panels would produce this much power under perfect conditions. However, in the real world, the output would be 20% to 25% less so I would suggest installing 15 panels and tweak the system later if you need to.
Rick
😂. Little Harbor You guys must be offIce guys .
I’m a builder , I’ve built from the ground up for my hole life and yes we get to the roof .
I am getting to old for shingling but some one has to frame the roof .
I’m having foot problems now so I’ve given up walking on the roof , buuuuut let me help you guys out with this pitch thing .
All you need is some old couch foam 4” thick .
You can drop the couch cushion on the shingles and stand on it , it’s almost like a day off .
Back in the day a 12/12 was workable pushing 60 years old I just can’t risk a fall , but on my house I have no choice .
My sons run a 9 pitch like it a side walk.
I’ve never used a safety harness 😜Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Rick ,
that’s what I’ll do , I’ll add 15 295 watt panels @ 4425 watts on my roof and set up a second array on the ground at some point .
That’s good news I feel better with a little more power .Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
I was in construction my whole life, and, yes, we built from the ground up as well. . Have done literally hundreds of roof jobs. I wouldn't get on a 9 in 12 roof without roof jacks. Where the hell are you going to put your shingles? On a sky hook? How do you keep anything on a roof that steep? You'd have shingles raining off the roof all day long. not to mention dragging silly looking foam rubber cushions around with you.wellbuilt said:😂. Little Harbor You guys must be offIce guys .
I'm not surprised you are having foot problems walking on pitches that steep. Walking on clean plywood is doable with some cleats nailed down but with sawdust blowing all over the place it's quite dangerous. BTW I was out of the business before all this ridiculous fall arrest gear was required in this area.
https://youtu.be/jp_iUVoGIdA
Piece of cake with roof jacks.mcgivor said:Where the hell are you going to put your shingles? On a sky hook? How do you keep anything on a roof that steep? You'd have shingles raining off the roof all day long.
LH we use a feeder , one guy stays on the ridge and slides the roofing down a few shingles at a time to to guys roofing below .
Or they keep the roofing on the tops of there feet.
The guys run up 6 shingleshigh 3 wide.
The silly foam holds the roofing also , laying the shingles on top Over lapping the edge.
My roofers just stand on a 9 pitch even shooting on the first course .
A 12 pitch slowed them down a little .
At 14/12 they use the brackets and ladders .
when I was in my 30s I would walk a 9 or 10 pitch no problem for ply wood or framing
I did not personally roof much after that I allways had my roofers , funny thing is the same guys are still roofing for me today.Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
My cabin, not much over 12/12, I know roofers are crazy... but no...
Every time roofing comes up I love to tell the story about the housing boom in Central Florida in the 1980's. Companies would drive up from central Florida and hire entire crews off of roofs! 50% more money, room and board and a ticket home after 10 days if they wanted to go home. It's no fun working on a roof in the summer time (taring flat roofs even worse) One of those jobs I'd do for my self, but wouldn't do for others. Mason's helper might be worse, but it would be a close thing.
Clearly these things are done differently in different parts of the country. I can't see a good reason to not use roof jacks on any pitch that material would slide off on it's own. They are a piece of cake to use and give you a sidewalk up there to walk on as well as a safe, secure place to stack your material,wellbuilt said:LH we use a feeder , one guy stays on the ridge and slides the roofing down a few shingles at a time to to guys roofing below .
I generally worked solo. When I did have a helper feeding me material I put down as much as 20 squares in a day.
Looking at Photowhit's picture, above, I couldn't imagine working on that roof without jacks
PW very sweet cabin .
That is exactly what I wanted
but in my area it doesn’t make sense , water elec , septic ,road work land permits etc are very expensive .
The zoning in NY calls for 800 sf living space ,my town wants 1300 sf then Wilfy started drawing plans .
I started out with a first floor plan of 1300, to meat zoneing code .
I wanted to leave the second floor unfinished but I had most of the material on hand and ended up adding the stair well
and second floor partitions , roughed in a bath .
I ended up just finishing the second floor , the nice tax lady keeps talking sweet to me 😍 here’s a pic of the front roof before the porch was added , I had the roofers set up sweet , the guys took the brackets off before they started 😳
the gray roofing paper is sticky compared to regular tar paper .
The garage and main house has ice shield over the whole thing , the guys roofed it in 10 hours 33 sq then came back and roofed the porch .
the pic is the day before we roofed it up and the day after .
Little harber , I allways wanted adjustable roof brackets like that mine are mostly fixed 8 pitch 2x8 brackets.
Why Is the aluminum flashing in the valley, it looks like The roofing is weaved very nicely ?
In my area we would roof up the valley with no flashing .
Starting in about 1995 every one used ice and water shield up the valley but it would be stuck to the plywood and roofing felt would be over the top .Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar .
- 621 Discussion Forums/Café