wiring two 5000w inverters together
adeleras
adeleras Registered Users Posts: 15 ✭✭
Would like to know
  1 can you wire up 2 x5000w pure sine wave in verter  together  and what would i need to do this
2we have a  2.5 kva battery bank  if i wire up  each inveter seperate to batteries then wire each
inverter to my 240v fuse box do i increase my load capacity or what.
  thank you for yr time who ever is able to reply to this  question
«1
  • mcgivor
    Wiring the outputs together can be done with the correct type of inverter, however MOST DO NOT ALLOW THIS, if you have the inverters, post the specs, or a link to them, the question cannot be answered without this information.
  • Estragon
    As well as the inverter info, do you have 240v loads?
  • Solray
    Solray Registered Users Posts: 246 ✭✭✭
    Check with the manufacturer of the inverters, they will have all the needed information to help you.
    To wire 2 inverters together, the ones that allow it, have a Sync Cable you connect first.   Very few inverters support doing this though.
  • adeleras
    The 2 inverters have 4 posts on them they are call a power jack pure sine wave power inverter 5000w to 20,000w
  • adeleras
    All power come from our solar panals to controller to the inverter to 24v battery bank and is wired to a 240v fuse box we run totally of soalr power no mains power
  • mcgivor
    Unfortunately parallel connection with those inverters, is not an option, keep the outputs separate.
  • adeleras
    Ok so can they be put on the same barrtry bank or do i need and second battery bank
  • Estragon
    Do you have 240v loads?
  • adeleras
    edited July 2017 #11
    Yes the whole house is on 240v via the inverter
  • adeleras
    Hard wired into fuse box
  • adeleras
    This is our own designed power system
  • nickdearing88
    nickdearing88 Registered Users Posts: 100 ✭✭✭
    Are you outside of North America and using a single phase 230v 50hz inverter? I believe people are thinking you mean 240v split-phase as we use in the US.
    Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter
  • adeleras
    I live in australia
  • mcgivor
    What voltage battery are you using?
  • adeleras
    We have 16 x250w x30.amps 8.9v  solar panals  single phase inverter specs are up the page 2 photos
  • adeleras
    We are using 22 deep cycle batteries at 105aph  each wired up as 24v straight line
  • mcgivor
    Assuming 11 strings of 2×12V, that many strings would be difficult to load/charge ballance.
  • adeleras
    Yes 11 in straight line x2 with 12v  batteries we have had this systerm set up for a year now and never lost power even with a week of rain not much sun we still have 14 to 15 v power in batteries
  • Solray
    If it has worked flawlessly for a year, why do you want to change it at this late date?
  • adeleras
    We dont want to change our systerm all we ashed was if we could put 2 inverters together to gain more power and as we ha e been told it is not possible
  • mmaritz
    mmaritz Registered Users Posts: 15 ✭✭
    I think the safest is to split your loads at the DB to allow each inverter to run separate circuits.  Its not ideal but that works when you can't parallel inverters to supply combined loads.
    Regards
    Mark
    • Main: Infinisolar 3+ (3kv) 48V Grid-Tied PV=3410w NE facing (8x 330W JASolar, 3x 310W Yingli), + Victron MPPT 150/60 @1240w SW facing (2x 310W Renesola, 2x 330W JASolar), Pylontech US3000, Victron BMV 700, 6 string combiner box with PV isolator switch, subDB for inverter supplied power.
    • Draadkar: Axpert 800w, 24V, 8x 12V - 105ah Leisure Batteries 400ah, PV=480 (2x 240W ElChepo), Victron BMV 702 for laptop, relays backup.
    • ICC for management, automated switch over and monitoring, pushing data to EmonCMS and PVOutput.org (Aloe Ridge Farm).
    • Weather from personal weather station using Weather Display.
  • Solray
    Inverters don't make power and more inverters won't make more power. They only change the voltage of the power your bank is storing which is made by the PV array. To get more power add more panels and a bigger battery bank.
  • adeleras
    Yes this makes more sense now thank you all for your time in helping with my questions
  • mcgivor
    The  original query was not to increase the overall power but to increase capacity potential of the load, perhaps there is an intermittent large load which exceeds the single inverters ability to support, hense the question  can the outputs of the inverters be connected in parallel, that was fundementaly answered, changing the subject is irrelevant.
  • Solray
    edited July 2017 #27
    It looked like she said 'put 2 inverters together to gain more power', I must have missed something. lol
    Putting 2 inverters will simply drain power faster, not make more of it.
  • adeleras
    Lolol im a lady noy a men lololol thanks all
  • mmaritz
    edited July 2017 #29
    adeleras said:
    Would like to know
    Hi @adeleras
    Do you have a clear idea of your biggest loads (ie the appliances and their power requirements)?  This will help as it may be better to run these on separate inverters assuming the battery bank can handle the loads.
  • Solray
    edited July 2017 #30
    You can also use a generator to supplement the solar portion when demand exceeds supply.
    Use the generator for dedicated loads like the cooling only, don't try to run an ac output to a dc input on an inverter obviously.
    Your inverters CANNOT be safely wired into one standard electrical panel.  You would have to split the panel internally or use 2 panels
    Any loads needing generator would have to be connected directly to the generator.   Connecting the generator to either inverter, will end badly (for the inverter)
