Would like to know
1 can you wire up 2 x5000w pure sine wave in verter together and what would i need to do this
2we have a 2.5 kva battery bank if i wire up each inveter seperate to batteries then wire each
inverter to my 240v fuse box do i increase my load capacity or what.
thank you for yr time who ever is able to reply to this question
wiring two 5000w inverters together

Comments
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Regards
Mark
> We dont want to change our systerm all we ashed was if we could put 2 inverters together to gain more power and as we ha e been told it is not possible
Inverters don't make power and more inverters won't make more power. They only change the voltage of the power your bank is storing which is made by the PV array. To get more power add more panels and a bigger battery bank.
The original query was not to increase the overall power but to increase capacity potential of the load, perhaps there is an intermittent large load which exceeds the single inverters ability to support, hense the question can the outputs of the inverters be connected in parallel, that was fundementaly answered, changing the subject is irrelevant.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Putting 2 inverters will simply drain power faster, not make more of it.
Do you have a clear idea of your biggest loads (ie the appliances and their power requirements)? This will help as it may be better to run these on separate inverters assuming the battery bank can handle the loads.
Use the generator for dedicated loads like the cooling only, don't try to run an ac output to a dc input on an inverter obviously.
Any loads needing generator would have to be connected directly to the generator. Connecting the generator to either inverter, will end badly (for the inverter)