So I am putting together a solar electric system that will use 3 270 watt panels to get 810 watts total and those panels will be used to charge a series parallel 24V/460AH bank of four 6 volt titan 105’s. I now need to make a decision on a charge controller. I have narrowed it down to either the Midnite Solar Kid or the Morning Star TS-MPPT-45 but would appreciate any other suggestions as well as any input on experiences using these two units.
1860 W (6) Rensola JC310M, Classic 150, 430AH@24V (8) Deka DSGC15 FLA's, Victron Phoenix Multi 24/2500 Inverter
Powering-20.5 CuFt. Fridge, 1 HP Submersible water pump, UV, Washing Machine, Gas Dryer, Gas Stove, Lights and Receptacles
Off Grid Cottage on lake in Northern Ontario 46˚N
Are they just in series for 24 volts?rp3703 said:
"...a series parallel 24V/460AH bank of four 6 volt titan 105’s...."
I would prefer the TS-MPPT-45, just because, as one of our former moderators was fond of saying "Loads grow" and so do system, it would be nice to have the extra room to add some panels.
I was thinking series & parallel with 4 6V 220AH Trojan's for a 24V 440AH output. So by "loads grow" you mean get an over sized charge controller? The Midnite allows you to run multiple units as the system load increases.1860 W (6) Rensola JC310M, Classic 150, 430AH@24V (8) Deka DSGC15 FLA's, Victron Phoenix Multi 24/2500 Inverter
Off Grid Cottage on lake in Northern Ontario 46˚N -
For that matter why not go with the TS 60 MPPT, and oh yes,, you will expand , it's an evolutionPhotowhit said:
I would prefer the TS-MPPT-45, just because, as one of our former moderators was fond of saying "Loads grow" and so do system, it would be nice to have the extra room to add some panels.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
rp3703 said:I was thinking series & parallel with 4 6V 220AH Trojan's for a 24V 440AH output. So by "loads grow" you mean get an over sized charge controller? The Midnite allows you to run multiple units as the system load increases.
If they are in series +6-+6-+6-+6- = 24 volts @ 220 aamphours
If they are in series and parallel
+6-+6-
+< >- = 12 volt @ 440 amp hours
+6-+6-
At 12 volts, the array might fit on a Morning Star TS-MPPT-45 but you would be better off going to a 60 amp charge controller
At 24 volts, either would work x2 the voltage = 1/2 the amps
amps x volts =watts
watts/amps=volts
watts/volts=amps
10% rate of charge (nominal for full time off grid) of a 440 AH battery bank would be 44 amps... If you ever decide to go a bit more say 13% rate of charge:
- 440 AH * 29 volts charging * 0.77 panel+controller derating * 0.13 rate of charge = 1,277 Watt array
- 440 AH * 0.13 rate of charge = 57 Amps charging current (typical maximum rate of charge)
I don't think his balance of panels to battery bank is bad here, I suspect we have the battery count correct at 4, just not the correct amp hour rating.BB. said:440 AH * 29 volts charging * 0.77 panel+controller derating * 0.13 rate of charge = 1,277 Watt array
Sorry, bad math. Four 6V 225AH T105's wired series/parallel would yield 12V @ 450AH. Bill, you already did my load calculations in this thread http://forum.solar-electric.com/discussion/351661/water-pressure-pump#latest . You came up with 790 Watts and 440 AH.1860 W (6) Rensola JC310M, Classic 150, 430AH@24V (8) Deka DSGC15 FLA's, Victron Phoenix Multi 24/2500 Inverter
Sorry. Quick skim and saw 24 volt.
Continue on!
- BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
So it sounds like the consensus is on Morning Star. With only about $100 difference between the 45 and the 60, I'll probably just go with the 60. Thanks for the help.1860 W (6) Rensola JC310M, Classic 150, 430AH@24V (8) Deka DSGC15 FLA's, Victron Phoenix Multi 24/2500 Inverter
And you get the spiffy web server in it too. Owning both Midnight an Morningstar, my 3rd controller was another MS-MPPT-60mcgivor said:For that matter why not go with the TS 60 MPPT, and oh yes,, you will expand , it's an evolution
If the choice was kid vs ts45, I would go for the ts in this application.
Looking at a 60 for future expansion though, I might consider a MN classic good for 96a.Off-grid.