battery bank
Comments
-
renesola 300w vmp 36,6 8.2A eff 15.46%
-
Robert you are going to need a 48 volt battery, just to get the maximum amount of power through the charge controller.
The issue is that the battery size is based on the load (A/C units wattage over time of use) You have stated 2900 watts for 3 to 4 hours. However A/C units cycle or if inverter, can run at a reduced speed lowering power usage. It would help to have an idea of how much of the time they are consuming less power. Are the A/Cs installed yet? Is there any way to measure the actual power consumption over a typical 3 or 4 hour period? The difference could be a 3000 dollar battery bank verses a 6000 dollar bank. The A/C may run at full power for the first hour and cycle at 50% for the next three. It depends on insulation and whether the unit was sized correctly for the space being cooled. Once a battery size is nailed down then panel configuration can be determined.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Ok, I looked at the charge controller specs and your best bet is to max out the array. Although it states a max of 3000 watts, you could over panel with 3600 watts because they never output their nominal wattage when it's hot and it never really gets cold there, right? They will make more power when it's cloudy. Can you get 12 volt 250 amp hour true deep cycle AGM batteries? I'm not talking about deep cycle marine batteries, they will not last as long.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
-
Hi Rick For now I would like to know how many panels of that 300w renesola do I nned to charge a 48v/400-500 ah battery bank, need to jnow how many to begin to order them, It is always sunny here.
-
Ok, you will need 12 panels, there may be some debate as to whether the configuration will be 6 strings of 2 or 4 strings of 3 panels, but it will be 12 panels either way. The battery bank will need to be AGM batteries configured to at least 48V 500AH.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
-
robocop said:renesola 300w vmp 36,6 8.2A eff 15.46%1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I agree with mcgivor, If you can find 60 cell panels cheaper, they will work just as well. Probably better, it will give the MPPT charger more headroom to down convert to the charging voltage.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
-
72 cell panels probably make sense for 2 panel strings in the heat if array is reasonably close. If going further or 60 cell panels are cheaper, 3 panel strings makes sense.
The charge controller would run a bit cooler with 72c 2p strings with Vmp ~70v. 60c 2p strings in the heat may be a bit low Vmp for EQ.
I just bought 3 72cell panels for $250CAD (~190USD) each. They were remains of pallet qty used in a larger installation and they wanted to get rid of them.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
For a 5% to 13% rate of charge:
- 500 AH * 59 volts charging * 1/0.77 panel+controller derating * 0.05 rate of charge = 1,916 Watt array (weekend/seasonal)
- 500 AH * 59 volts charging * 1/0.77 panel+controller derating * 0.10 rate of charge = 3,831 Watt array nominal
- 500 AH * 59 volts charging * 1/0.77 panel+controller derating * 0.13 rate of charge = 4,981 Watt array "cost effective" Maximum
And a 3,831 Watt array would produce (fixed array):
http://www.solarelectricityhandbook.com/solar-irradiance.htmlWillemstad
Measured in kWh/m2/day onto a solar panel set at a 78° angle from vertical:
Average Solar Insolation figures
(For best year-round performance)
Lots of sun... Say 6.23 hours per day (Apr). If you have a minimum load requirement--I would suggest that you use only 65% to 75% of the "predicted levels" of output--Allows for variations in weather and temperature. A 3,831 Watt array (3.8 kW+/- 10% is "close enough for solar"--I just copy all of the digits so you can follow the numbers as I use them))--Numbers are long term averages and may not account for local weather patterns (like marine layer):Jan Feb Mar Apr May Jun 6.65
6.95
6.92
6.23
6.58
6.78
Jul Aug Sep Oct Nov Dec 6.74
6.61
6.42
6.41
6.28
6.32
- 3,831 Watt array * 0.52 system derating (all losses) * 6.23 hours of sun * 75% (variations in weather) = 9,308 WH ~ 9.3 kWH per day minimum per day available energy
If your energy usage can vary (less sunny day, less A/C usage)--Without the 75% derating number:- 3,831 Watt array * 0.52 system derating (all losses) * 6.23 hours of sun = 12,441 WH per day nominal (April)
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset - 500 AH * 59 volts charging * 1/0.77 panel+controller derating * 0.05 rate of charge = 1,916 Watt array (weekend/seasonal)
-
Raj174 said:Ok, you will need 12 panels, there may be some debate as to whether the configuration will be 6 strings of 2 or 4 strings of 3 panels, but it will be 12 panels either way. The battery bank will need to be AGM batteries configured to at least 48V 500AH.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
To Raj74 thnks for your reaccion
Do you mean that I can charge the battery bank with 2 or 3 72 cell panel 300w .
-
PH1800 MPK Plus MPPT Series (1-5KVA from MUST company this is the inverter model . plse let me know thx
-
robocop said:
To Raj74 thnks for your reaccion
Do you mean that I can charge the battery bank with 2 or 3 72 cell panel 300w .
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Raj174 said:... So 6 strings of 2 panels per string would work.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
My thoughts are 60 cell panels in strings of 3 would be the best fit from the standpoint of sufficient headroom and not pushing the envelope, at around 90-96 volts1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Be sure to de-rate VMP for temperature (perhaps -4V). One source says to take the charging voltage needed plus a 2V margin for the controller and 2V for possible wire loss. So I get something like 73.2 - 4 -2 -2 = 65 which is greater than 59.
I think it is OK to run close to the limit - as I understand it, if the charging voltage is slightly low, the batteries won't accept as much charge. So the current output from the panels will drop and the panel voltage will rise to above VMP. Ie, the situation is partially self correcting, resulting in slightly slower charging, not no charging. Plus, high temperatures tend to happen when there it lots of sun.I am available for custom hardware/firmware development
-
Best bet would be to check around to see what local pricing and availability is like and go from that. Shipping partial pallet qty likely to be costly.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed