Two Aims 6000 Watt 48 Volt inverters to One Sub Panel.
Comments
-
Hi Roy,
Looks like you have more power than you'll need. Not a lot of fans of Aims inverters (efficiency , poor life span) here and 2 - 6000 watt will be much more inverter than you would want to run short of having a bakery! While I can't run everything at once, I have an 1800 watt inverter (had planed on a 3500-4000 watt inverter). I live in a 16x60 mobile home and run a window air conditioner as well as using a water heater (not recommended gas would be better), washer, toaster oven, dehydrator... I have a bit larger array 5000watt, but a much smaller battery @650 ah 24 volt (about a third of yours)
8 battery banks, which I suspect is one battery bank made up of 8 strings, will likely be problematic in the long run. It will work fine until one battery has a problem, then the other batteries will be drawn down trying to bring up the single battery. With AGM's it will be hard to trouble shoot.
Unless you are in a very sunny location, I would suggest discussing your energy needs and uses. I suspect you would be better served with a larger array, smaller battery bank and a single, smaller, better inverter. It reads as if you have already purchased this equipment. If you have a single 6000 watt inverter should be all you need in general, I guess a full size oven running with a water heater would bring it over the wattage, but that's a huge load and you would still be close!
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
A couple of questions:
Do you have any 240v loads, and if so, what are they?
If I understand correctly, your neutral isn't tied to ground anywhere (eg. in the inverter(s)), so is floating?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Hello Photowhit. Not certain how to reply. I have never been accused of building something to small or under powered. Usually it is overkill. I just looked at my monthy electricity use (avg 1200 Kwt) and tried to build something conservatively I thought would allow me to be completely off grid. I had read that inverters could be stacked and after watching several youtube videos I decided to go with Aims. As I said though, I am new to Solar so maybe I should have consulted with someone who had a running system prior to designing mine. I was shooting to have roughly 25 to 30 kwt a day. I wanted to have no issues with ac, refridgerator, freezer and washer/dryer. I do intend to have a lp dryer and my stove/oven are propane. I wanted to have a 100 amp panel and supply the two hot legs from different inverters to ensure the amperage. I have purchased inverters, solar panels, batteries, charge controler, combiner, disconnects to isolate system sections, wire for panels to combiner and through charge controller and to batteries. I also have wire to run service from inverters to sub panel. The Cabin is wired and spray foam insulated with most all the interior walls complete. The spray foam cost me a bit to have done. I can alter my setup I just hope not to have to alter the wiring in the cabin. I have the panels (16) on the barn and I have attached the Inverters to a panel inside the Power Station as I intend to call it. I have not connect anything up as of yet intended to work on it this weekend. I also have 8 more panels so I could have two more arrays but to my understanding I would need an additional charge controller. The Outback can handle up to 4000 watts and I would be around 5500 to 5600 hundred watts.
-
Hello Estragon. I do not have any 220 volt connections, all are 110. I have not connected the system up as of yet. I built a setup that I am currently running a generator to supply the sub-panel with power. I intended to install a ground rod so as to Ground Solar Panels. I need to look at aims wiring diagrams again I do not believe their system allows for a neutral to tie to ground. I will research this tonight and get back to you.
-
I had a quick look at what I think is the manual for your inverters. There doesn't appear to be any way of stacking the inverters in a master/slave sort of way. They use quite a bit of power just being on, 4.16adc according to specs. That's 200+ watts times 2 inverters, even if you're just running a couple of lights and charging your phone, on top of your actual loads. If you feed one to each side of the box, you're likely to have loads on both so neither ever gets to go into power saving search mode. In other words, you're out 10,000 watts of power over a 24hr period to run basically nothing.
My suggestion would be to wire just one inverter into the panel and keep the other as a spare. It supposedly surges to 18000w, so if the window air conditioner is your biggest load, you should be fine with one. If not, it should prompt a re-think of loads for off-grid living.
It also looks like the inverter has a relay based ground-to-neutral switch. Do you have a generator, and if so do you know if it's grounded/neutral bonded?
Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Hey Estragon. I appreciate you looking. I see that despite several months of reading I have made another error. It is not the first. I think I will use the inverters separately for two systems. If I have a problem I will look into a stackable inverter like MagnaSine or others. I thought that I read as long as the inverters were PSW and not MSW they could be run in parallel. Aims seems to have done something different but I have spent quite a bit money to get where I am already. I have eight additional panels that I intended to set up a second system for my Barn but I am now thinking on getting a second Outback charge controller and use all my solar panels to one system and use the two inverters one feeding the cabin and one feeding the Barn with the addition of an additional sub panel. I will use my washer and dryer in the shop and take that load off the sub panel in the house. I do have a generator, a Dewalt 7000 watt. It has a lug for grounding the generator to a grounding rod but I do not know if it is grounded/neutral bonded. I will take a look. Do you have any further suggestions? And do you feel I would be better off changing out the invereters for another brand?
-
Hello Roy, Welcome to the Fourm.
If you could possibly return both of the AIMS inverters, would suggest you doing so. If they have not been mounted, and no knock-outs removed, a return may be possible.
As Photowhit mentioned there have been a number of off-gridders here, who have not been very happy with various AIMS inverters. Although, in fairness, there have been many fewer of these in the past year, or so.
AIMS makes many different inverters, but, if the one that Estragon found is the one that you have, the Idle power consumption is simply astonishingly HIGH. A single one of these inverters would consume in 24 hours about as much as do entire homes of many of us living off grid. It would difficult to imagine in what type of system an inverter with self-consumption would be a good fit.
Regarding your 32 ea AGM batteries, most likely, these 125 Ah batteries are 12 V. If that is the case, then you seem to be planning on running eight strings of four batteries each. This is considered to not be the best design choice, for a number of reasons -- the massive number of interconnections, difficulty in getting the strings to share charge and discharge currents well, the difficulty in choosing THE battery that best represents THE representative temperature of the bank for the RTS/BTS, and so on.
If you could return the batteries, and try to find a battery that meets the design goal of your system, based upon the loads that it will need to supply in a SINGLE string of batteries, you would probably be far ahead.
As you probably know, the off grid systems that perform most reliably for a long period of time, are those what have been carefully designed based upon the LOADs that they need to supply ... easy to say, and a bit time-consuming to do.
Do you know all of the loads that the system will need to supply, how long these loads will be on, the peak total load for the system, and approximately what time of day these loads will run? This will help size everything. Measuring the actual demand of the load on a Kill-a-Watt meter, or similar can be a large help.
Perhaps a bit too much attitude on my part.
A system that would supply 30-ish KWH per day, is a very large and usually a very expensive system, too.
FWIW, IMO, and so on. Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Sorry, if I was harsh, but I think working on a design is important. You what you have so lets work from there. a 48Kwh battery bank (1000amps x 48 volts) would normally like a peak charging rate of 100 amps or 10% of it's capacity, a 3700 watt array will normally produce about 75% of it's panel rating during solar noon (Normal Operating Cell Temperature, NOCT values) so 3700x .75 = 2775 watts ÷ 48 = 58 amps or 5.8 %. With cheap panel prices we often see/spec systems with 13-15% of capacity for a healthy system. If you are in a particularly sunny area you could argue with the small numbers...
...but most places have an average yearly solar isolation of around 4 hours per day, or the max incoming wattage would be around 4hours x 2775 watts or @11Kwh. So even if you were using the energy as it was created you would have 11 kwhs on average. Stored energy comes with an additional @20% cost as only about 80% of the energy presented to the battery is stored. All this before the inverter efficiency, which on the Aims is around 88% peak. (some other peak around 95%)
I don't know if you care, but it doesn't look like Aims has any 6000 watt inverters that are code compliant, I went to their site, and breezed through the manual and didn't see any mention. It isn't required unless NEC needs to inspect your system or you want to carry insurance on the home, in which case I would ask them.
It actually sounds like you have a very well insulated very efficient cabin, I'll bet you will find you have a greatly reduce electrical usage.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
First I want to first thank everyone for the feedback. I wish I had consulted on a forum or met with someone who had a system before I started out.
Due to cost my batteries were purchased on craigslist from a battery shop that was about 300 miles away which I drove and picked them up. They are used batteries but I was assured with proper care that they should last me at least five to seven years. It was my intention that when they needed to be replaced to buy new with a matched set of batteries all produced all having the same batch number and date code.
The panels also were bought through craigslist from a second source that were selling new old stock. They still have there warranty and are brand new panels but were manufactured several years ago and had never been sold. I bought them at about a third of their cost. The aims on the other hand I bought new through Amazon but at going back to the seller today found the date in which I could return them has past.
I have been piecing items together for the last several months. It may be a considerable loss but if it it is detrimental to use the Aims I am willing to purchase an alternative inverter or two.
As to code, being totally off grid I was not as concerned at being technical as much as being safe. I do not wish to act foolishly. I also did not sit down with the chart that I saw online to actually calculate my needs but as I said earlier referenced my former electric bills. I have used all LED lighting in my cabin and researched to buy the most energy efficient appliances to keep the loads down. I realized that the system was not the most efficient due to my purchases and thought that to error on being oversized would be a good thing.
Photowhit, I did not take you as being harsh. But reading your last reply it sounds like you have dealt with many novice builders and having taken the time to be educated about what you are doing. That you are tired of people trying to attempt something without first getting educated themselves. I can understand and appreciate that. I spent what I thought was a good amount of studying prior to starting my build, but see now I still jumped in too soon despite my studies. I have a friend that felt that I was going to be disappointed with solar power meeting my needs and I wanted to be sure to have plenty of power.
Thank you Vic for the advice. Before spending more money what recommendations would anyone make as to brand/size of inverters with my current Solar Power Panels (3700 watts, 4 strings at 96 volts at 9 amps) and or suggestions for battery Brand/size/Bank Configuration for 48 volt system? If you need I can post names and specs of Panels, and Batteries, inverters, charge controllers etc...
Also I have not bought it but do intend to buy a Kil a watt meter to check and verify loads at my outlets. I also have three inline amp/volt meters to install. Again I do appreciate your time. Roy
-
@SrTexRoy said: Photowhit, I did not take you as being harsh. But reading your last reply it sounds like you have dealt with many novice builders and having taken the time to be educated about what you are doing. That you are tired of people trying to attempt something without first getting educated themselves. I can understand and appreciate that. I spent what I thought was a good amount of studying prior to starting my build, but see now I still jumped in too soon despite my studies. I have a friend that felt that I was going to be disappointed with solar power meeting my needs and I wanted to be sure to have plenty of power.
Think we have all made similar mistakes and paid the price of education, suggestions here are offered free of charge to those educating themselves, to prevent the disappointments most have experienced. The best starting point is an accurate inventory of all loads, then move on from there, for example using the Aims unit along with another smaller inverter for off peak times at night, could be one solution.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
SrTxsRoy said:
Also I have not bought it but do intend to buy a Kil a watt meter to check and verify loads at my outlets. I also have three inline amp/volt meters to install.
I think you are realistic and will have an easier time switching to solar than others. Once being on solar we do tend to 'load shift' trying to use the energy when it's being produce and not dipping into the stored energy when we know we have been, or will be needing the stored energy. I don't have a generator, and that can provide some needed relief during long cloudy periods. I didn't ask, will you be using wood or gas for heat? Water heating? This is typical to save laundry as a daytime load, using a front load machine saves energy as well, your gas dry will give you a smoother transition to solar. I like to cook during the day with a crock pot, chili a couple days ago, pulled pork likely Monday...
Something you might look into is using a high efficiency Mini Split Air conditioner. I suspect with your well built, well insulated cabin, air conditioning the whole place would work out well, and have the advantage of less energy use and much less noise.
Many bargain hunters here! So understand the desire to save money. Hard to beat current low prices on new solar panels, 29 cents a Kwh for pallet load quantities, Grade 'A' New, UL listed panels. Thought I got a great deal 5 years ago at 76 cents a watt for new grade 'B' panels. Hard to imaging they can go much lower! In addition their is a 30% tax credit (off any tax liability in the US) Don't think you can take the tax credit on used panels or batteries. In the future you might consider forklift batteries, they are mass produced and offer a pretty good bang for the buck in deep cycle batteries, though they are among the highest maintenance batteries. Wish I knew of a source for inexpensive quality inverters!
Charge controllers are rated at output amps, so your 3700 watt array, even at NOCT values will be maxing out a 60 amp charge controller, I think you can get close to 5000 watts cost effectively on a 80 amp charge controller. You can have 2 (or more) controller feeding the same battery bank. I have 2 now and will have a third shortly, just put up a small east facing array to spread out my charging profile.
Kill-A-Watt meters are great to figure out how much energy is use, particularly on things that have thermostats! Fridge and freezers, Window air conditioners are hard to pin down.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Ready, Fire, Aim. again.
Sadly, there are many gaps in your design.
Aims inverters are not stackable (you know that now)
Used AGM's are nearly always, expired, pulled from float service, Telcom plant backups. You can expect only a couple months service,
Parallel battery banks are not optimum, even more so when low IR agm batteries are employed
The new Magnum PT-100 controller might be a feasible replacement for the 60A controller
Your inverter/charger needs to be generator ready, or you need to have a 240V generator powering a 240 48V forklift or golf cart charger. The charger must be rated for use with AGM sealed batteries, or you have to become the charger brains and monitor when to
terminate the charging.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Again thank you all !! I will sit down with the chart and note my appliances and electric use to see what I need.
The controller I have is an outback 80 amp 150 volt charge controller. (I can purchase another and add two additional 96 volt arrays to bring my total up to about 5500 watts. (each string of panels are just under 1000 watts) I still have (8) panels that are not setup) I have an Eco tank-less water heater that is run on propane and a front load washer. Do not have the dryer yet but it will be LP when purchased. my old one was electric so I passed it on to someone else.
Ok I am going to replace the Aims inverters. Any brand recommended? And is it better to have two stacked to feed the buses or tie the buses together and buy a larger inverter or at least a large one that is split phased? (When starting I thought having two inverters if one inverter failed I still had power. Wanted to maintain the fridge and minimal lighting so to limp along while repairing/replacing damaged equipment.)
After figuring my electrical use/needs I will post my findings and see where I should go next.
Roy
-
@SrTxsRoy
If you can return/sell the inverters, even if you have to eat a reasonable restocking fee, I would do it. They look more appropriate for a large marine application like a big power yacht. If not, just be aware of the big tare loss. If you use one for the barn make sure you turn off all the barn loads when not in use, or better yet, turn off the inverter. You don't want to run the inverter just to keep some electronics in the laundry appliances lit.
As others have pointed out, the batteries are likely to be problematic. It is what it is though, so we should focus on doing the best we can with what we have. On the bright side, you will get a lot of knowledge and experience with loads etc and will be in a much better position to make replacement choices when the time comes.
A big problem with AGM is there is no good way to accurately measure state of charge. We can get a reasonable idea by measuring resting voltage (no loads or charging for several hours) though, so before hooking them up as a bank, I would:
1. Lable each battery with a number to identify.
2. Measure and record resting voltage for each battery.
3. Charge each battery individually and fully. You will probably have to do this again, so get a good multi-stage 12v charger. Note any batteries that seem to charge unusually quickly, unusually slowly, or get unusually warm while charging.
4. Repeat step 2.
If you get this far with no problem batteries there's a decent chance of making a bank that might work for a while. If you find some problem batteries, maybe you still have some recourse to the seller?
The main thing is to get the batteries in as close to the same state as we can, and with no outright bad ones. If they go into a bank with some weaker than others there's a good chance of ruining the weaker ones prematurely. Once in use, you will want regularly measure and record individual battery voltages and repeat the separate charging exercise for weaker ones.
The generator is likely a portable type, on wheels, designed to run tools etc on remote job sites?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
SrTxsRoy said:The controller I have is an outback 80 amp 150 volt charge controller. (I can purchase another and add two additional 96 volt arrays to bring my total up to about 5500 watts. (each string of panels are just under 1000 watts) I still have (8) panels that are not setup)
I don't see a huge load, I think your energy use will be surprisingly low, wonder how you are using close to 40Kwh's a day now. Perhaps you are in an all electric home, In power eaters, electric heat and air are usually #1 & 2, Water heater and refrigeration tie for #3, They account for much of a homes energy use.
In a solar home, there is an advantage, in that air conditioning is most needed when you have a lot of available power. In a tight small home (which you have described), you should be in pretty good shape. When setting things up look for those power hungry things. Old Plasma TV's could use 200+ watt for a large screen, New 55" LED TV's are in the 60-70watt range.
Some odd things do require more energy that you might image. CPAP machines may use upwards to 120-150 watts (and some in the 40-60 watt range) and they typically run at night off stored energy, This can be a load larger than a refrigerator! I suspect most living off grid, just learn to look at the amount of energy each thing uses.
Glad you are looking ahead and developing a system that will meet your needs. I do think it takes some time, some of use came into solar when Solar panels cost $5+ per watt. I suspect, us old timers, all have a pretty good idea of what is currently running in our homes and rarely leave a rom without turning off the light. It's odd for me to have more than a couple light on at any one time. I know people in grid connected homes who seem to turn on lights and leave them on until they go to sleep...
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Split phase house electrical panel.
Can only be fed with a split phase power source ( a 240V inverter)
The split phase panel shares a return wire between the 2 phases, and assumes a large portion of the return current will be out of phase and cancel out, allowing a smaller return (neutral) conductor. Things will burn if the 2 legs are jumpered in the electrical panel.
If you have a split phase panel in, you should/must use a split phase feed. That can be from a Balance Transformer ($500) run off a
single phase inverter, or a split phase 240V inverter. Somethings are not safe to "MacGyver" into working.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:Split phase house electrical panel.
Can only be fed with a split phase power source ( a 240V inverter)
The split phase panel shares a return wire between the 2 phases, and assumes a large portion of the return current will be out of phase and cancel out, allowing a smaller return (neutral) conductor. Things will burn if the 2 legs are jumpered in the electrical panel.
If you have a split phase panel in, you should/must use a split phase feed. That can be from a Balance Transformer ($500) run off a
single phase inverter, or a split phase 240V inverter. Somethings are not safe to "MacGyver" into working.
Mike, I asked here about and switched my 240 panel to 120, I don't think anyone though there would be a problem. Of course I'm only running 15 amp service to it from a 1800 watt inverter.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Rented a trencher today and trenched and piped from Barn to house fore wiring to feed the panel. The two aims inverters I have are split phased 120/240 inverters. And yes I was talking about shared neutral from both inverters tied to the neutral bus for branch circuits. I only intended to run 120 circuits but thought by running two inverters I would have 100 amp capacity on a 100 amp panel.
Mike you suggested the Magnum Charge controller. Is the Outback I have something I should not use? It is rated for 80 amp and 150 volt and can charge 4000 on a 48 volt bank. I can also add another and run them in parallel if I need to add more panels.
(Also note do not jumper buses on panels. Gotcha)
Mike maybe I am miss-understanding split phase. The panel I bought and wired my cabin with is a Homeline Square "D" 12 circuit 6 space 100 amp breaker panel and it is listed as single phase 120/240. But it has 6 circuits that is split with three on each bus for the hot and a neutral bus. Is this different from the split phase you mentioned above?
Photowhit you asked about heat. I have a wood burning stove for when needing heat. I am in Texas and we tend to need more ac through out the year but we do have times that heat is needed. When I retired I moved into my cabin no electric, no heat, no water and no insulation. The first week there winter blew me a kiss with 20 to 30 degree temps through the nights. I had my bed sucking the heat out from my body. I borrowed a propane stove and then bought the wood burner and thankfully it will crank out the heat. Oh and I do have a Samsung 52 in Plasma TV. Other wise everything has been researched for energy efficiency.
Now about panels I thought a string was panels wired together versus individual pans going to a combiner or charge controller/battery bank. I am also a little puzzled about panels being faced differently. I thought you wanted all to face south and dependent on time a year angled about 23 degrees for efficiency also dependent on latitude where panels are located.
Okay Estragon sounds like I need to change the batteries too. So you think that since I already have them use them til I lose them and then buy something that requires more maintenance but will prove to be longer lasting.
As to the generator you are correct I bought it to run tools for building and setting my place up. But I found it to be very efficient. I use roughly 5 gallons and it will last aprox 14 hrs. I have been really impressed. it advertises 10.5 hours on a half load but I have been running my house on it. The only real load though has been the ac. My fridge and stove are being delivered next week. I also do not have my water heater connected yet. It will be LP as so will the Stove.
-
SrTxsRoy said:When I retired I moved into my cabin no electric, no heat, no water and no insulation. The first week there winter blew me a kiss with 20 to 30 degree temps through the nights. I had my bed sucking the heat out from my body. I borrowed a propane stove and then bought the wood burner and thankfully it will crank out the heat. Oh and I do have a Samsung 52 in Plasma TV. Other wise everything has been researched for energy efficiency.SrTxsRoy said:Now about panels I thought a string was panels wired together versus individual pans going to a combiner or charge controller/battery bank. I am also a little puzzled about panels being faced differently. I thought you wanted all to face south and dependent on time a year angled about 23 degrees for efficiency also dependent on latitude where panels are located.
Something I learned here, is you don't necessarily want to have all the power coming in at once. If you were grid connected, where the maximum power in total for the day makes perfect sense, it's not necessarily so with off grid installations. Since you will be using power during the day, and the less stored energy you use the better. It is often nice to have South East and South West arrays. You will still have near max during 'solar noon' but the curve will have longer tails. This is also a better charging profile if you are over paneled. Flooded Lead acid batteries can only charge at about 13-15% of their capacity per hour and the last 10% or so the battery accepts current even slower.
I think the understanding hit me listening to Dave taking about other advantages to solar tracking. Thanks Dave (or whom ever it was) Just yesterday I setup a small South Eastern facing array for just this reason.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
BTW - I'm a big fan of "use what you've got". You have the batteries, I'd charge them up and use them. Worse thing to happen is they fail, best, who knows maybe you get 3-5 years out of them!
I'd hook the Kill-A-Watt up to the plasma and chart it for a few hours. If it very high (I'd bet over 120 watts and suspect even more, depending on when it was made) If you don't need 4K there have been some great deals on efficient 55" LED TVs!
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
For the split phase 120/240 shared neutral - get the advice of an electrician. Don't take my word. I wired my place strictly conventional,
no funny tricks, and the inspector was quite happy on the first round.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Estragon You said to get a multi stage Battery Charger. I searched on amazon and pulled this up: Schumacher SE-1555A 12v. Does this look sufficient or would you recommend something different? I am guessing it may take a while to go through sixteen batteries.
-
Just to be very clear--The hot wires from two different inverters cannot be connected together--AC inverter generally do hot synchronize and having the AC outputs of two inverter paralleled together will not work (magic smoke let out, etc.). There are a few inverters that will sync, but you have to buy those specificity and wire per the instructions.
Regarding sharing a neutral bus bar between two AC inverters... It depends. Most pure/true sine-wave inverters have "isolated outputs" (transformer isolation) and can share a common/ground bonded AC neutral (the white wire in north America).
Most modified sine/square wave AC inverters do not have an isolated AC output. If you ground reference or try to share the AC Neutral and/or earth ground the AC neutral, the inverters will short out and fail (the specific warning is you cannot both have a negative ground battery bank and an earth bonded MSW inverter. The common installation is the ground the DC negative output and let the AC output "float").
And regarding split phase 120/240 VAC power. In North America, we have basically a center taped transformer on the power pole. There is a Black/White/Red connection. We have 120 VAC from Black to White, and Red to White. And 240 VAC from Black to Red. The center tap White is generally tied to ground (cold water pipe, ground rod, etc.) at both the pole transformer and at the house main panel (yes, the neutral is tied in two different locations--In general it works fine because there is no copper cable from the pole ground to the house ground. And since one transformer feeds a handful of houses, each house it tying White to Earth Ground--A bit problematic in theory, but what our code requires).
If you have one 120/240 VAC split phase output TSW/PSW AC inverter--Each hone will need its own 120/240 VAC panel. You can Bond the AC neutral together in the panel, and common ground reference (ground rod/cold water pipe, etc.) together for each panel.
If you have two 120 VAC TSW/PSW AC inverters, you can share one panel (common AC neutral, Black bus bar to one PSW Hot, and Red bus bar to second PSW/TSW AC inverter Hot). And make the two AC neutrals bonded on the same bus bar... It should work OK, but I would suggest not doing it. You will not get 240 VAC from Black to Red with two unsynced AC inverters. So, having a 120/240 VAC split phase main panel is of little practical use.
Also, it confuses the installation. Somebody working on the main panel may not realize there are two AC inverters has power sources--And they could try to pull 240 VAC out later, or get shocked when they only turn off one of the two AC inverter, etc... Just an personal opinion on my side. I do not like complexity/confusion--Years down the road, somebody may get bit.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I was thinking of something like xantrex truecharge on sponsors site. You don't need something capable of a lot of current, maybe a 20a, but you do want something that can give a proper absorb (constant voltage, tapering current) charge at the right voltage for your AGM batteries.
It will take a while. You may find some of the batteries are in pretty good condition (resting voltage at 12.8v in step 2). You want to focus on the weaker ones. I do think it's worth a shot unless you find batteries with a resting voltage less than 12v or soOff-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Okay, just wanted to let you know I am ordering Xantrex Truecharger and will charge up and test batteries.. Sorry I have been off for a couple of days. I am building a form to pour a slab for two 2500 gallon water storage tanks. I do not have city water nor a well at this time. (Well to be drilled next year after I pay Taxes on this year.) I found I could have a tanktruck (4000 gallons) delivered for 750 dollars. Hope to have the form finished tomorrow and pour slab next Tuesday. I received my Refridgerator and Stove today.
Hey Bill I appreciate the info on the panel and split phase. I had no intention of running 220 from the panel just did not want to waste having one half of the panel from being used so I Intended to have two 50 amp inverters in one panel.
I will update after I get my chart filled out.
Thank you all. Roy
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 190 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed