Slow clocks with pure sine wave inverter
terrynew
Solar Expert Posts: 48 ✭✭
All the digital clocks in my house, including in appliances, lose 1-2 minutes a day. This had been ever since I went off-grid nine months ago. I had thought it was just something to suffer through, but recently was told that it may be an inverter problem. The funny thing is that it's a full sine wave inverter (Magnum MA4448PAE), not a modified sine wave one that is known to cause digital clock troubles.
The specs say it outputs 60 HZ +/- 0.04%, which I figure shouldn't account for 1-2 minutes/day loss. Is there a way for me to confirm the frequency without buying an expensive scope or meter?
Any advice would be greatly appreciated. Thanks,
...Terry
The specs say it outputs 60 HZ +/- 0.04%, which I figure shouldn't account for 1-2 minutes/day loss. Is there a way for me to confirm the frequency without buying an expensive scope or meter?
Any advice would be greatly appreciated. Thanks,
...Terry
Comments
-
Re: Slow clocks with pure sine wave inverter
That should be +/- 0.57 seconds per day error.
Assuming your digital clocks use line frequency--that should be enough to "prove" that the inverter is not meeting specifications (by the way, I cannot find a model MA4448PAE inverter--is it is a "MS" model?).
I wonder if the frequency can be "trimmed" to meet specifications (a small justifiable capacitor to tune the frequency)?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Slow clocks with pure sine wave inverter
Measure with a frequency counter! A decent Fluke has one built-in. My favorite Agilent has that and an amazing ohms circuit for finding DC ground problems in noisy circuits. Kind of a 4 wire ohms meter that uses two wires and does a calulation to simulate what a 4 wire meter does. More than you need but nice to know that HP's offspring are definately still the cutting edge!
Simple solution, use battery clocks!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Re: Slow clocks with pure sine wave inverter
I don't use 120 volt AC clocks for a couple of reasons, and suspect most others off grid don't either. First, I know inverters aren't dead on with their frequency, and second, electric clocks are viewed, at least by me, as parasitic loads. My solution? Battery operated digital clocks, then I know the time is right, especially as I have several and can compare -
Re: Slow clocks with pure sine wave inverter
Even on grid, I have a couple "atomic" battery clocks (and even a Casio wrist watch). So far, they work well for me and usually receive the radio signal ever day or two (the clocks/watch need to be kept away from electrical wires/interference to receive WWV after midnight).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Slow clocks with pure sine wave inverter
Oops, you're right, Bill, it's an MS4448PAE.
The battery-powered clock solution will work fine, but I'll have to train myself to ignore any appliance clocks.
I'll see if I can borrow a Fluke or other meter with a frequency counter.
Thanks,
...Terry -
Re: Slow clocks with pure sine wave inverter
A $15 kill a watt meter has a freq meter in it.
I second battery clocks with rechargeable batteries in them. All we ever use.
T -
Re: Slow clocks with pure sine wave inverter
I would be a bit surprised if the k-a-w was accurate to 0.04% --That is only 60Hz +/- 0.024 Hz.
A digital/analog with second hand AC clock + accurate time source measured over a week+ is probably easier and more accurate (average over time) to see a +/- 0.57 second per day frequency error.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Slow clocks with pure sine wave inverter
My k-a-w jumps back and forth between 60 Hz and 59 Hz, spending more time showing 60 than 59, so yes, it's close to 60 Hz.
Like BB said: "A digital/analog with second hand AC clock + accurate time source measured over a week+ is probably easier and more accurate".
A LOT more accurate! But really what's the point, we all know that inverters wonder around their design frequency. Now a $500,000.00 inverter, I'd expect to be a lot more accurate, but a battery operated clock costs much less. -
Re: Slow clocks with pure sine wave inverter
Argh... I've not thought about this. TV's and VCR's and such, wow, I will need a accurate sourcePowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Slow clocks with pure sine wave inverter
I've got one of those "atomic clocks"; receives radio signal from time base.
Doesn't actually work at the cabin; radio signals have a hard time getting in there. :roll:
Sometimes it doesn't get a signal elsewhere either.
Any measuring device is only as accurate as whatever you compare it to; inevitably another measuring device. Or as Ogden Nash said: "A clock is something you check your watch against only to discover the clock is several minutes wrong." -
Re: Slow clocks with pure sine wave inverter
The digital clock on my propane stove top has the same issue. Clock falls way behind but I haven't actually calculated the rate. It's always been off grid so I figured it was a proplem with the stove. I have Magnum MS-4024AE pure sine wave inverter running 21 months now without issue.Off Grid Cabin, 24V 440ah 6V GC battery bank, Xantrex MPPT60-150 CC, Magnum MS4024 inverter-charger, >1200w Solar bank
-
Re: Slow clocks with pure sine wave inverter
I wonder if there is a "trim" cap on the 60Hz master, that can be fine tuned....Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Slow clocks with pure sine wave inverter
Buy a wrist watch. problem solved. or sync your computer..http://www.worldtimeserver.com
this problem of clocks being inaccurate when run off inverters is not new and I have never found one inverter that has an accurate enough frequency keeping circuit. Its just not worth while for the manufacturer to go to the extra effort to use a trimmed crystal for frequency accuracy as most items opperate perfectly at + or - 5hz of 60 or 50 hz. -
Re: Slow clocks with pure sine wave inverter
I use pool.ntp.org for time sync on the computers.
But the stove, microwave and VCR/DVD all have clocks, and same with clock radios . Well, I guess when I move to the ranch, I won't need the alarm clock, my PDA has that function, and cell network updates it's time. But I like all the clocks to read the same, and my watch keeps +- 20 seconds from DST to ST, so it's OK. But clocks loosing/gain minute a day, what a pain. And I'm sure they use the generic TV colorburst 3.xx MHz crystal as their timebase, what a shame if there is no way to trim it.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Slow clocks with pure sine wave inverter
My Magnum inverter goes all over the place when it's not heavily loaded, according to my Kill-A-Watt. I've seen it as low as 45 Hz, but never much over 60. It seems to smooth right out when I apply any load over a few tens of watts. I don't have any clocks that plug into AC so this has only been something of a curiosity to me.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed