Schneider Conext SW4048 Stacked Inverters Not Charging Battery Bank
neutronspin
Registered Users Posts: 51 ✭✭
Installed replacement inverters and the charging function doesn't seem to come on. I have the recharge voltage set at 50.0vdc. Right now the battery bank is at 46.4vdc as indicated on the SCP. I am worried that my bank will die completely. I checked all the charger parameters per the manual and they seem to be correct. I talked to the vendor and he said they seem to be correct. The state of charge as indicated on the Conext battery monitor is at 51%. The inverter is in AC pass thru mode and right now not drawing any DC current presently so hopefully the bank will not go any lower. I would think if the recharge voltage is at 50vdc the charger should have come on. Any help appreciated.
Comments
-
I do not know--But would "pass through" mode disable the SW charging system?
Generally, modern inverter-charger systems pretty much use the same "hardware internally" (transformers/FETs/etc.) when charging and invertering. Pass through would seem to "disable" the entire system.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
The battery at 46.4V is very close to death, turn the inverter on ASAP to allow charging, depending how large loads are it may require disconnecting them to prioritize charging.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:The battery at 46.4V is very close to death, turn the inverter on ASAP to allow charging, depending how large loads are it may require disconnecting them to prioritize charging.
-
BB. said:I do not know--But would "pass through" mode disable the SW charging system?
Generally, modern inverter-charger systems pretty much use the same "hardware internally" (transformers/FETs/etc.) when charging and invertering. Pass through would seem to "disable" the entire system.
-Bill -
On the SCP enter SW 4048, scroll down to Charger Settings, check Auto Chg Enable is enabled. On 48V models the default is disabled.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I don't have an SW manual, but the XW manual is pretty dang complete, and covers all the settings and how they work, you only have to read it, and @ 46V, your batteries are dead/dieing/murdered Either read the manual and configure the inverters properly, even set to factory defaults, they should charge the bank properly. Read first, then muck about with the settings.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
So this is posted in Off grid, could it be as simple as the wiring for generator starting?
If you manually start the generator, will it start charging?
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
mcgivor said:On the SCP enter SW 4048, scroll down to Charger Settings, check Auto Chg Enable is enabled. On 48V models the default is disabled.
-
For a conext battery monitor equiped setup, the soc setting should be enabled. Sometimes the soc setting is enabled in a system WITHOUT a battery monitor. If the setup does not have a xanbus networked battery monitor, and the soc setting is enabled, the battery may not charge.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed