code for array combiner to cc: disconnect or breaker?
jtdiesel65
Solar Expert Posts: 242 ✭✭✭
I was wondering if a non-fused disconnect is enough. But does code require a fuse/breaker? If each string in the array has a breaker, I'm not sure why one would need a breaker/fuse for the entire array given the wire size is rated for the amperage.
You don't need another breaker unless the single run rating is less than Isc-array rated current.
Having (for example) a combiner box at the array, and a single switch (rated for VDC/Current) or even a rated breaker next to the MPPT charge controller can make servicing a bit easier (local array on/off switch).
I have my combiner breakers outside, on the pole, where the arrays are. I also have a handy breaker inside. When updating firmware or changing the setpoints, often the controller has to be disconnected from the array and then cold boot from the battery. Breakers are only $20, but they sure make things easier.
Fuses are a bit less expensive but their contacts are not rated to "open" a live circuit
thanks.I have combiners with breakers on the arrays. I currently have din mount breakers inline in a midnite panel and next to the charge controllers. But I am rewiring the PV side with some conduit and was thinking about ditching the panel and breakers for a couple disconnects. I'm not a fan of din mount breakers. I already have a couple spare panel mount breakers that would be fine, so I ended up buying an enclosure. I'll put the panel mount breakers in the enclosure (I'll need to cut knockouts for them) and replace the midnite panel.
Just make sure the panel mounted breakers are rated fo DC, as AC breakers are not suitable, with a few exceptions, which are rated for both.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Thanks. They are the DC ones that were cc->battery. I rewired that side of the CC and replaced those breakers with new DC breakers in the Schneider PDP. Originally I had cc->battery breakers in one panel and pv->cc breakers in another. Legacy wiring from long ago.
- 228 Forum & Website
- 618 Discussion Forums/Café
