can I use 2 24v battery banks,combine to 48v for inverter but charged seperate at 24V?
patdufo
patdufo Registered Users Posts: 9 ✭✭
I have a 28V DC military generator and want to be able to use 2 24v banks tied together for the inverter but charged seperately from the 28v generator?This will be for cloudy days.The charge controllers would be 48v,do you think that it would work?thanks
  • mcgivor
    edited January 2021 #2
    The problem would be there would be a dead short on the charger on the interconnect of the 48V bank, the only options are isolating the individual 24V groups or using a Schottky diode to prevent reverse current flow. Neither is ideal, however  there are DC-DC chargers available but they tend to be low current, high $$$, what current output is the generator?
    edited January 2021 #3
    If you aren't using the battery bank at the same time you are charging, you could devise a method to charge as a 24 volt battery bank and use as a 48 volt. That would not be an option for most systems.
    I've done this the other way around, charging 2 - 6 volt batteries in series, and using them (at night) as a 6 volt battery bank in parallel. A tiny system for bicycling touring.
    Wired directly - NO
    If you change the wiring each time you wish to charge, then - yes, it's possible.   But I'd advise against it, because of the complexity of the continual re-wiring.   Can't do high amps with schottky diodes - even with many in parallel, you still have too much loss.
    Might be able to rig up some DC circuit breakers with a transfer switch interlock,but still messy
    BB. Super Moderators, Administrators Posts: 33,722 admin
    Just to be clear--2x 24 volt battery bank tied together in series for a 48 VDC input AC inverter?
  • patdufo
    yes
  • patdufo
    ok,a battery isolator couldnt help?Will likiely put in a quick disconect at the inverter and charge with inverter on,this is a 280 amp at 28v DC gen,should charge the 2 24v 1000 AH batteries pretty quick,might have to turn it down a bit(charge to quick)comercial DC gen that I have seen are verry expensive and most not rated for continuos use
    There are devices that can support splitting a 24 volt battery bank into 12 volt loads... Basically, a DC to DC converter that holds the "low 12 volt bank" = (equal) to the voltage on the "high 12 volt bank". Battery equalizer or balancer... There are quite a few for 12/24 volts systems (used on Bus/Truck conversions such as a 24 volt truck chassis and a 12 volt RV package). They are also used on some military vehicles.
    https://www.waytekwire.com/datasheet/extend battery life.pdf
    I looked for 24/48 volt versions--But I did not find any with a quick search (some that are rated a few amps, but no >60 Amp units).
    They are not cheap... As much as a similar AC inverter (or more, since it is a smaller market?)...