AC pump wattage and horsepower

I have a 1/2 hp pump which is labeled as 370watts but when I measure the wattage with a metter or read from my inverter, it is around 1000watts.
I have tried this with several pumps and they all pull higher wattage than the HP rated.
Can anyone explain what I am missing?
Note: 1hp pump is pulling 2000watts.
Also the power factor is between 98 to 99%
I have tried this with several pumps and they all pull higher wattage than the HP rated.
Can anyone explain what I am missing?
Note: 1hp pump is pulling 2000watts.
Also the power factor is between 98 to 99%
Comments
My 1/2hp submersible 230V pump, 150 meters (500') from the inverter using #8 AWG draws ~530W which is slightly higher than the rated 374W, but nothing near what you are describing, can you provide further details?
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
i've not dug into the deeper levels, while running to see what the loading / PF is with it.
Conventional Motors & Pumps will all have about the same loading in their HP class:
odd - can't seem to get the image to upload
[fixed duplicate image links--I think. -BB]
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Our 1/2 HP well pump (single phase 120V) pulls just under 1500W when running. I'm a little surprised at you guys saying one only pulls 1000W. Ours pulls about 54A continuous from our nominal 24V battery bank.
Just have to accept what you have and be happy there is water coming out. Many out here are drilling again...
http://members.sti.net/offgridsolar/
E-mail [email protected]
My inverter is Schneider Conext SW 4048 and I monitor the power usage from the combox. I also used a cheap meter from amazon to read the power factor https://www.amazon.com/gp/product/B07ZFR1BRH/ref=ppx_yo_dt_b_asin_title_o00_s00?ie=UTF8&psc=1
I have also connected the pump to grid power and the power reading is the same.
Even running the pump in a big tank with a hose just to test, consumes the same amount of power.
Not all 1/2 HP pumps are the same. Some have less power use because they are made better. Others just gobble the watts but will run for 40 years. I can go buy a Chinese origin 1/2 HP at home depot for $125 that will draw 600 watts. It will be fine for surface pumping but add some lift and it trickles.
The design, spec, and quality are what you have to look at.
http://members.sti.net/offgridsolar/
E-mail [email protected]
https://www.leopump.com/1-11-1-8-deep-well-pump.html
https://www.rcworst.com/blog/How-Much-does-it-Cost-to-Operate-my-Submersible-Well-Pump
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
That is very enlightening. Thank you for sharing.
Would adding VFD to a single phase 1HP pump improve anything?
There are issues with VFD's. They generate a lot of electrical noise, at quite high intensities . Large enough many times to breakdown 600V motor insulation and cause current to flow through the motor bearings. Neither of which is good. VFD's need to be engineered to match the motor and it's load and then proper wiring an suppression techniques employed. Small motors are not too bad, but large ones can cause a lot of trouble