does anyone know of a more efficient 3k/6k 12v inverter.
MEK1954
Registered Users Posts: 23 ✭✭
My 12v 4K/8k inverter is consuming 20 amps and my demand is only
2.08 amps is this normal seams a little inefficient to me, does anyone
know of a more efficient 3k/6k 12v inverter.
Mark
Comments
-
MEK1954 said:My 12v 4K/8k inverter is consuming 20 amps and my demand is only 2.08 amps is this normal seams a little inefficient to me, does anyone know of a more efficient 3k/6k 12v inverter.
Do you have the input and output voltage?
If you are using 20 amps at 12.5 volts or 20a x 12.5V = 250 watts. and are outputting 2.08a x 120v= 249.6 watts, Looks pretty good!
Amps is moot a measure of power, just current. Power is amps x volts.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
The AC current and DC currant !! I should have done the math, thanks.
-
A 12v 4kVA inverter is not realistic due to near 400 amp max current consumption. Also cheap inverters often have high no-load idle consumption. Not sure if your 2.08 amp reference is 120 VAC output current or no load inverter 12vdc idle current. If it is no-load DC idle current that would not be unexpected for a 4kVA inverter.
You did not state if it is true sinewave or modified sinewave inverter. If modified sinewave, a Kill-A-Watt like meter will not likely read correctly.
Reasonable 12v max VA rating inverter is 1500 VA. Generally, the higher the power the inverter, the greater its overhead power consumption.
As to your readings, 2.08 amp * 120vac = 250 watts at AC output. DC meter showing 251 watts input. Never would be that good.
250 watts AC power output with 95% inverter efficiency is 263 watts from battery and would be a good efficiency for a smaller inverter but at just 250 watt load on a 4 kVA inverter the idle overhead consumption by inverter will likely prevent achieving 95% overall efficiency.
I specifically stated inverter as VA not watts. Inverters and generators are rated for VA not watts output. Their losses are based on current through their switching devices, transformer, and wiring. Poor power factor loads will impact maximum capability and inverter efficiency.
Motors will have inductive power factor in 0.7 to 0.9 range.
TV's and other electronic equipment may have simple rectifier-filter capacitor power supplies with power factor in 0.65 to 0.7 range. Their AC load current profile is short high current pulses at twice AC line frequency.
U.S. power grid residential service cost is based on real power and doesn't charge extra for poor power factor loads so manufacturers don't put in extra cost to improve device power factor. Europe has more regulations on power factor for devices consuming more then 75 watts. One of worst offenders in U.S. are inverter-based refrigerators, touting high efficiency, with very poor power factors in 0.6 -0.7 range. Terrible for powering by a battery based inverter.
Manufacturers specifically have different unit design for U.S. versus Europe market as they can save a buck or two on manufacturing cost by not including power factor correction for product targeted to U.S. market.
-
I used an AIMS UL listed 12 volt 3,000/6,000 watt inverter for a year and a half with no issues. That thing was (is) a tank. It even ran my 12" chop saw and small welder without complaints. The amperage made me nervous, but it never blew a fuse. I'm definitely happier in 48 volt world, but those wattages at 12 volts are really fine if you manage it correctly.
-
DC 20 amps at 12.5 volts or 20a x 12.5V = 250 watts. and are outputting AC 2.08a x 120v= 249.6 watts,I asked this question before thinking it through so my inverter is more efficient then I first thought.Thank you all for your help.Mark
-
RCinFLA said:
U.S. power grid residential service cost is based on real power and doesn't charge extra for poor power factor loads so manufacturers don't put in extra cost to improve device power factor. Europe has more regulations on power factor for devices consuming more then 75 watts. One of worst offenders in U.S. are inverter-based refrigerators, touting high efficiency, with very poor power factors in 0.6 -0.7 range. Terrible for powering by a battery based inverter.
Manufacturers specifically have different unit design for U.S. versus Europe market as they can save a buck or two on manufacturing cost by not including power factor correction for product targeted to U.S. market.
Being that inverter based refrigerators are generally a small load, typically less than 100W, the effect is minimal since in offgrid as the battery capacity is the primary concern, hopefully the refrigerator is a small percentage of the inverters VA rating, it's high power, poor power factor loads that are of greater concern in offgrid.
Whilst the statement is true for the grid utility supplier who needs to compensate for the aggregate of all poor power factor loads, the benifit of inverter based refrigerators offgrid is an acceptable compromise especially the absence of surge current.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed