Do I Have Enough Solar For My Battery?
Veteran52
Registered Users Posts: 3 ✭
I acquired 4, 100W 12V solar panels, parallel, producing 5A each, 21 volts each with a 40A MPPT controller. Is this enough to fully charge a 200AH, or a 250AH, or a 300AH 12 volt AGM battery without sulfation concerns, given the usual 5 hours of average good sun light each day? I need to know before I buy a new battery so I don't waste money on more than I can properly charge yet get as much storage as I can.
Thanks
Comments
-
I run 4 100w 12v panels with a 40A PWM Controller, hooked to 650AH of 12v Batteries. Usually for Weekend Use only. I get by running a Stereo for 12 hours/day. I can even handle a Bar Fridge 24/7 on holidays for 2 weeks. However I do top up with a Genset hooked to a15A Charger for 3 hours every night then.
-
Assuming the battery is not being discharged, then yes it will be sufficient to maintain such a battery, if however the battery is discharged on regular basis below the PV's capacity to replenish the withdrawals, then no.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:if however the battery is discharged on regular basis below the PV's capacity to replenish the withdrawals, then no.
-
So roughly, 400 watts of array, if angled close to your latitude, and without shade, should produce about 300 watts per hour. For your MPPT type charge controller to make best use of the wattage, they need to be wired at least 2 in strings of 2 (2 in series) and 2 parallel strings. 300 watts charging a 12 volt 200amp battery, charging at 14.5 volts will produce about (300/14.5=) a bit over 20 amps for each hour of direct sunlight. Assuming your AGM battery can take a 10% charge rate, you should be pretty good. Without knowing where you are, that's roughly what we look for a 10-13% charge rate.
Please note that use is at the battery, so you need to take into account energy used in your inverter and it's idle use.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Say you use 60 AH per day, and the starting rule(s) of thumb(s) designs would be:
- 60 AH * 12 volts = 720 WH per day of 12 VDC energy
- 720 WH per day * 1/12 volt battery * 2 days of storage * 1/0.50 max discharge planned (longer battery life) = 240 AH @ 12 volts suggested minimum battery size
Two calculations for solar panels... One based on size of battery bank and 5% to 13% rate of charge. 5% can work for weekend/sunny weather usage. 10%+ suggested for full time daily off grid usage:- 220 AH * 14.5 voltage charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 207 Watt array minimum
- 220 AH * 14.5 voltage charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 414 Watt array nominal
- 220 AH * 14.5 voltage charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 539 Watt array "typical" cost effective maximum
http://www.solarelectricityhandbook.com/solar-irradiance.htmlChesterfield
Measured in kWh/m2/day onto a solar panel set at a 51° angle from vertical:
Average Solar Insolation figures
(For best year-round performance)
And lets "toss" the bottom three months (not use your loads as much and/or use a backup genset when needed). That gives us February @ 3.73 Hours as the "break even" month:Jan Feb Mar Apr May Jun 3.29
3.73
4.46
4.94
5.03
5.27
Jul Aug Sep Oct Nov Dec 5.46
5.35
5.30
4.63
3.38
3.03
- 720 WH per day * 1/0.61 DC system efficiency * 1/3.73 hours of sun per day (average February) = 316 Watt array "break even" February
- 400 Watt array * 0.61 end to end DC system eff * 3.73 hours of sun per day (Feb) = 910 WH per day
AGM batteries will be fine too... Just monitor the charging/loaded battery bus voltage to ensure all is going OK (batteries get fully charge several times a week, and don't get discharged below ~12.0 or 11.5 volts under heavy loads).
The above calculations are relatively conservative and intended for an off grid cabin or other usage that needs relatively reliable power. It is a "balanced" system design (battery banked sized to loads, solar array sized to battery bank and hours of sun per day).
One thing you did not mention is what the peak current/power will be... More or less, ideally a C/20 Discharge rate is optimal. C/8 max continuous. C/5 max for an hour or two, and C/2.5 maximum surge current (numbers are for Flooded Cell, AGM batteries can discharge faster/surge more current--But the C/X numbers given should keep the AGM or FLA Batteries happy:- 220 AH * C/20 = 11 Amp discharge (say 11 amps for 5 hours a night, for 2 nights to 50% discharge)
- 220 AH * C/8 = 27.5 Amps for 8 hours (really a bit less) until battery bank is dead (taking bank "dead" is not good--Batteries will not last long)
- 220 AH * C/5 = 44 Am;s for an hour or few hours (5 hours to "dead").. Heavy draw for shorter time frames
- 220 AH * C/2.5 = 88 Amps for a few seconds to a few minutes (starting surge for well pump, refrigerator compressor, etc.).
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Veteran52 said:mcgivor said:if however the battery is discharged on regular basis below the PV's capacity to replenish the withdrawals, then no.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
BB. said:Probably close enough to 240 AH for now.
-
Good Luck to you and thanks !
Remember there can't be any shading 9am to 3pm for what you are doing. NEVER
Also keep in mind there are 2 kinds of people, those who want solar, and those who want more!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
The "solar numbers" for energy harvest--Anything within 10% of the above numbers, is pretty much "exactly the same" (it is surprisingly difficult to accurately measure solar power within 10% accuracy without laboratory instruments).
I.e., ~220 AH +/- 22 AH -- Not really different from 220 AH itself.
And as the folks above said--Almost any shade on a panel/array will cut harvest by 50% to 100%.
If you have shading, look at what it takes to get rid of the shade (move panels, move roof vent pipes, cut trees, etc.). If you have things you cannot move (nearby house, AC power lines overhead, etc.)--Solar electric may not a good fit...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 190 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed