solar panel started to melt, my fault or faulty solar panel
2 groups of 2 (2S2P) I have more but I was just doing a simple test at the moment
4 x 100 watt panels https://www.amazon.co.uk/gp/product/B07YKQZ2N3/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1
I have a 40A controller https://www.amazon.co.uk/gp/product/B07FRM17DM/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1
12v battery Trojan 1275
I had it going through most of the day without a problem then suddly a spot on the brand new solar panel (just one of them) started to melt
I was within the limitations but 1 solar panel set did start to get some shading which about 1.5 hours in I noticed it.
any ideas if this was a fault of mine or just a bad solar panel
Comments
-
-
That's bizarre! I'm guessing that there must be a defect in the silver conductor, and it started acting like a fuse, getting hot enough to melt. I would say it's a flaw in the panel.
System 1) 15 Renogy 300w + 4 250W Astronergy panels, Midnight 200 CC, 8 Trojan L16 bat., Schneider XW6848 NA inverter, AC-Delco 6000w gen.System 2) 8 YingLi 250W panels, Midnight 200CC, three 8V Rolls batteries, Schneider Conext 4024 inverter (workshop) -
thank you for your reply MichaelK I will carry out the same test again tomorrow and hope it is just the one panel. (obviously not using that one) I will update on here my results. just in case someone else has the same issue as I did.
I will check here again before doing the test just in case someone thinks of anything.
thanks again for your reply -
Are you able to return them? Flexible panels are reputedly inferior to ridgid glass ones, if they could be returned that would provide an opportunity to make the switch, unless it's impossible to use ridged of course.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Very likely the flaw won't affect the output in the event you have a big issue in the returns process.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
I have been extreamly lucky and getting replacement and a refund woop woop.
Mcgivor. Thamks for your input as these are on a greenhouse the weight is a bit of an issue especially when I have built a wooden tilting frame.
Littleharbor. Question for you, if I hadn't returned the panel if it was reconnected wouldnt the imperfection carry on arcing and burn an even bigger hole. -
You are correct... When you see signs of overheating, arcing, melting, hole in rear/front let moisture in--With more problems, etc... There are major problems and eventually the panel will fail and possibly start a fire (worst case).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks BB for replying. I would be with you on that one.
With regards further testing with a new panel in place of the broken one. I have not occurred any problems as of yet.
I am doing another test today to see if any problems happen but I'm feeling confident it was a panel issue.
Thanks again for all the replies, you guys are amazing. I'm so happy to have found this forum and the amazing support. -
fodbrothers said:I have been extreamly lucky and getting replacement and a refund woop woop.
Mcgivor. Thamks for your input as these are on a greenhouse the weight is a bit of an issue especially when I have built a wooden tilting frame.
Littleharbor. Question for you, if I hadn't returned the panel if it was reconnected wouldnt the imperfection carry on arcing and burn an even bigger hole.
I have handled thousands of used panels over the years and have seen, possibly hundreds of these type of flaws in panels. While they may look bad the area shouldn't continue to grow and will likely have minimal effect on output provided the flaw remains localized and the tabbing remains intact. Each individual cell has many dozens of traces for the current to flow through and the arcing, if that's what this is, from what I've seen wouldn't have spread across the cell. Then again, just my opinion and observation.
It's great that you were able to get a full replacement and obviously the best way to go. Your small system size is the only reason I would even give the reply I have. My only other suggestion for the future would be to find a way to support conventional, glass and framed panels they should give you reliable service up to and beyond the life of their warranty.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Hi littleharbor2
Thank you very much for the reply
The panels are awful I have now had 3 panels burn in places and 1 misshapen
Very crazy.
I will be going to glass ones
Do you recommend any. I will be buying from amazon UK
I am also a little confused with max system fused.
I always thought this was a limitation of the panel and some just say it's not but you need to put a fuse in.
A bit of clarity on this would be great.
I don't want to make any mistakes
Thanks again for all your guys help -
-
have you tried to roll or curl those panels. they still have silicon wafers that don't flex
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
no Mike, I have tried to keep them strait as possible.
-
I was surprised to learn thin silicon wafers do flex, I don't understand it myself as I would think a crystalline based material would easily fracture.
https://www.electrochem.org/dl/ma/203/pdfs/1014.pdf
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
One of the issues with silicon cells (as little as I understand/recall), there can be defects in the cell where (I guess) the breakdown voltage is lower in spots, vs the rest of the cells. If you put the panel under sun (and do not draw current for charging?), those defects can overheat and cause damage to cell and surroundings.
Of course, other connection problems (solder failures, delaminiation, water corrosion, cracks in silicon, etc.) can also cause hot spots.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
fodbrothers said:Hi littleharbor2
Thank you very much for the reply
The panels are awful I have now had 3 panels burn in places and 1 misshapen
Very crazy.
I will be going to glass ones
Do you recommend any. I will be buying from amazon UK
I am also a little confused with max system fused.
I always thought this was a limitation of the panel and some just say it's not but you need to put a fuse in.
A bit of clarity on this would be great.
I don't want to make any mistakes
Thanks again for all your guys helpfodbrothers said:Hi littleharbor2
Thank you very much for the reply
The panels are awful I have now had 3 panels burn in places and 1 misshapen
Very crazy.
I will be going to glass ones
Do you recommend any. I will be buying from amazon UK
I am also a little confused with max system fused.
I always thought this was a limitation of the panel and some just say it's not but you need to put a fuse in.
A bit of clarity on this would be great.
I don't want to make any mistakes
Thanks again for all your guys help
The max fuse rating is for each panel, or string of panels. You only need over current protection in systems with 3 or more strings. While not required, it's still a good idea to have a fuse , or better yet a DC rated circuit breaker on each string. This gives you the ability to shut down any one or all strings for system maintenance/shut down. etc.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
so would 2 of these be ok https://www.itstechnologies.shop/collections/solar-panels-buy-online/products/320w-ja-solar-mono-percium-lw-black-frame-solar-panel
im a little confused with regards to controller limits
https://www.amazon.co.uk/gp/product/B07FRM17DM/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1
as the max charge power and the max pv array.
obviously I dont want to make a mistake.
cheers in advance again -
The nice thing about MPPT controllers is that you can over panel them and they will merely limit output to their rated output current. I would run these in parallel if you are charging a 12 volt battery, series, if a 24 volt battery.
Here's something you might like from the mfg. of that controller.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Ok great
Thanks for the info.
I'll get them panels I just wanted to know what the difference was.
Will it limit the charge then ?
I wouldnt get near them limit (Watts ) in reality anyway
I just wondered what was the difference
And of the panels are good
Yes its a 12v battery -
fodbrothers said:Ok great
Thanks for the info.
I'll get them panels I just wanted to know what the difference was.
Will it limit the charge then ?
I wouldnt get near them limit (Watts ) in reality anyway
I just wondered what was the difference
And of the panels are good
Yes its a 12v battery
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Return them and buy a new solar product. I bought from qwik batteries 3yrs back. Still its on condition. You can go for solar panels from them and also they even supply solar batteries.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed