Schneider Conext 6848 with AGS to Generac 0064622
canpandave
Registered Users Posts: 2 ✭
I am trying to figure out how to connect the AGS to the Generac.
Any help would be appreciated, or sources?
Off grid 48v system, 2 sets 15x255 watt panels, 2xFlexmax80 Charge Controllers, 2 sets Trojan 6v x 8 batteries, 16KW Generac with transfer switch (Grid long gone).
/d
/d
I'm pretty sure the reason no one has answered this is because you didnt list the type of inverter that goes with the automatic generator starter or the model of the generac
before anyone can answer, you will need to provide those things
12 panels 6 series 2 parallel 2100 watts, 1 XW60-150 CC, 16 trojan 6V batteries 8 series 2 parallel 450 Ah, 1 XW 6848 pro, 1 5500 watt champion inverter generator( I know...I need a 12Kw ) -
He's running a Conext 6848.
I don't use auto start but looking at the 6848 manual you need Conext part # 865-1060-01 (page 1-9) which is their generator auto start box $200 ( http://www.solar-electric.com/catalogsearch/result/?q=865-1060-01+&cat=0 ) and a breaker in the PDP to run the power through
You may be able to directly trigger the generator through the AUX connections (Page 3-5 through 3- 7) by programming it to provide a few watts at 12v when low battery voltage is detected.Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
48v Rolls 6CS 27P
Also needs a device (combox or SCP) to program the settings for the AGS I think .
I am using a Xantrex AGS and a relay. I provide power 120v from the inverter to the Generac N1-N2 leads, through the relay. When AGS desides to run the generator (like low battery or whatever), it opens the relay so Generac thinks the power is out. BUT, it seems like as soon as the grid goes down, the generator starts, ignoring the inverter power on N1-N2. I am not sure why this doesn't work, but it might be in the programming of the Generac. Any thoughts?
On grid
Conext XW+ 6848 Inverter SN M700xxxxx
2x Xantrex XW 80 600 MPPT Battery Charge Regulators
Conext COMBOX connected to the local network SN B130xxxxx
Conext Battery Monitor
Xantrex AGS Automatic Generator Start Control
Generac 20KVA generator
20x Batteries 8A4DLTP-DEKA 210Ah batteries
24x Roof Mounted REC 255W panels
I used this and the gen works fine
Which wires did you use from the Xantrex AGS and what generator type did you set in the AGS?
- 234 Forum & Website