Lead acid end amps
 
            
                
                    mountainman                
                
                    Registered Users Posts: 442 ✭✭                
            
                        
            
                    In winter What are the consequences of a daily  extended absorb and end amps less than 1℅                
                2kw array 6 345 q cells  make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
        
        
        
      6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Comments
- 
            Assuming flooded and Vabs high enough for some gassing, I would expect some extra water loss, heating, and maybe some extra grid corrosion?
 If not temp compensated and the bank is cold though, summer absorb voltage may not be high enough to gas.Off-grid.
 Main system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
 Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
- 
            mountainman said:In winter What are the consequences of a daily extended absorb and end amps less than 1℅
 Much will depend upon how long the "extended absorb" time is. For many PV systems, excessive absorb time is not an option in winter. End amps can be specific to the manuacturers particular design, so this is best ansered by them.
 I always have more questions than answers. That's the nature of life.
- 
            I have tried to over size my system
 With an average 800 watt hour daily usage. And Nearly 800 watts of pv.
 And over 4 Dec sun hours
 Except for several over cast days.
 charging doesn't seem to be a problem.
 Was wondering how bad over charging
 Might be for the batteries.
 By 10:30 I'm usually at 1℅
 by around noon with absorb set for 3 hours
 Im seeing 2 amps on a 400 ah bank.2kw array 6 345 q cells make sky blue 60 cc
 6 230ah GC @36 volts
 18 amp accusense charger. 3650 champion
- 
            What are the manufacturer's recommendations for absorb parameters for your battery brand?Remember that a little extra time in absorb and a good amount of time in float tends to help your batteries balance to each other. This, in turn, tends to help reduce the natural imbalance between strings. Keep it within reason, monitor your water consumption - and your batteries will serve you wellUndercharging is the enemy and you are avoiding it!MarcI always have more questions than answers. That's the nature of life.
- 
            Manufacturer says 2.58 volts per cell
 Hold for 2-4 hours then stop.
 Sg should be 1.275
 Im not sure if the electronics in my old camper could take 15.5 volts?
 So I set vabs at 2.482kw array 6 345 q cells make sky blue 60 cc
 6 230ah GC @36 volts
 18 amp accusense charger. 3650 champion
- 
            
 With lower Vabs, you will need to increase the absorb time, so you really need to monitor the Sg.mountainman said:Manufacturer says 2.58 volts per cell
 Hold for 2-4 hours then stop.
 Sg should be 1.275
 Im not sure if the electronics in my old camper could take 15.5 volts?
 So I set vabs at 2.48
 Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
 || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
 || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
 solar: http://tinyurl.com/LMR-Solar
 gen: http://tinyurl.com/LMR-Lister ,
- 
            Does any gc battery manufacturer other than us battery.
 Recommend a 15.5 daily charge
 I thought that was eq volts.
 I haven't equalized in 6 months
 SG says I haven't needed to.
 And i have read that eq is hard on Batteries.
 It was overcast yesterday.
 Today was clear all day
 floating by noon
 With vabs set at 14.9
 At 5:30 pm My SG is.
 1.275 1.270 1.265 1.265
 2kw array 6 345 q cells make sky blue 60 cc
 6 230ah GC @36 volts
 18 amp accusense charger. 3650 champion
- 
            US Battery is 15.5 recommended absorb?
 I think recommended on my US Battery flooded L16s is 2.45vpc (25°C) = 14.7 @12v bank.. Actual charging is generally higher with temperature compensation on my cool/cold banks.Off-grid.
 Main system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
 Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
- 
            From us battery website                        2kw array 6 345 q cells make sky blue 60 cc website                        2kw array 6 345 q cells make sky blue 60 cc
 6 230ah GC @36 volts
 18 amp accusense charger. 3650 champion
- 
             
 2kw array 6 345 q cells make sky blue 60 cc
 6 230ah GC @36 volts
 18 amp accusense charger. 3650 champion
- 
            Maybe I'v misinterpreted their instructions?2kw array 6 345 q cells make sky blue 60 cc
 6 230ah GC @36 volts
 18 amp accusense charger. 3650 champion
- 
            The charging recomendations are based on grid supply, in an offgrid application it is not possible to achieve the amount of time required, therefore higher amperage charging rates are needed to to compensate for the window of opportunity available. There are some who recommend higher voltages to premote saturation within the limited window of opportunity, however that differs depending on depth of discharge, no two systems are identical.
 One needs to monitor the parameters of their particular system to gain knowledge, it's actually more complicated than simply following recommendations as there are so many variables associated with lead acid, there is generally no monitoring system to prevent errors, which is the reason I've personally abandoned the obsolete technology. Having said that it is possible to dance on the head of a pin and have success, but there are more failure reports than success or so it seems, most news is bad news. There is a place for lead acid where environmental conditions favor their use, outside that there is little reason to consider a more advanced technology, my opinion naturally.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
 Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
 5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
- 
            The above method uses a lower absorb (2.4vpc) then a sort of mini-eq at the higher voltage than I use. As McGivor says, this may be preferable with grid charging.
 With solar, higher absorb voltage (2.45vpc) gets my banks to very close to full more often than a lower Vabs would, and I can EQ opportunistically and only as needed. US Battery would call that 2 stage charging.
 Much of the year, the first way would take too long for me. I'm guessing it would also mean a fair bit more watering.Off-grid.
 Main system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
 Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
- 
            
 Are you using the US 1800 XC2 6 Volt 208 AHr Golf Cart battery ?mountainman said:Maybe I'v misinterpreted their instructions?
 Then per US Battery, their recommended 3-Stage charging cycle is ...
 Bulk = Constant Current @ 21 Amps until 14.7 Volts
 Absorb = Constant Voltage @ 14.7 Volts until down to 6 Amps
 Finish = Constant Current @ 6 Amps for 2 - 3 hour or when less than 24mv dv/dt per hour
 Float = 13.02 Volts
 Equalization = Constant Voltage @ 15.3 Volts until hourly SG stop increasing
 https://www.usbattery.com/wp-content/uploads/2019/03/usb_1800_data_sheet_2019.pdf
 Note: Temperature compensated
 Note: The above amps is per string ( I think, you have 2 strings )
 When does your SG stop rising?mountainman said:In winter What are the consequences of a daily extended absorb and end amps less than 1℅
 a) If the SG does not stop rising before "sunset" then you may be slightly under-charging
 b) If the SG is constant for the last hour of good sun, then you are reaching 100% SOC
 c) If the SG is constant for many hours in Absorb Mode, then you are only slightly over-charging
 If you have a different % DOD every morning and/or
 a different number of Sun-Hours every day, then the answer may be ... a, b or c.
 Your "extended" Absorb charge will take longer to reach 100% SOC than
 the suggested US Battery "Bulk + Absorb + Finish" charge cycle
 With only 2 amps flowing into a 400 AH Battery bank ( 1 amp per string ) at Noon,
 then that is not that much more than FLOAT.
 I think, it is difficult for your configuration to adversely over-charge your 416 AH 12 Volt Bank in the winter
 The "Finish" charge, recommended by US Battery, is a mini-Equalization - they claim it extends the overall life.
 Trojan also recommends a "Finish" chargemountainman said:Does any gc battery manufacturer other than us battery.
 Recommend a 15.5 daily charge
- 
            Thanks all I think I'M finally getting my answer. There is no set and forget it.
 Each days sun and my usage is different.
 So there is no definitive answer.
 You just have to keep the hydrometer stuck in the battery till you bust the bulb.
 Hence the term dancing on the head of a pin.
 2kw array 6 345 q cells make sky blue 60 cc
 6 230ah GC @36 volts
 18 amp accusense charger. 3650 champion
Categories
- All Categories
- 232 Forum & Website
- 140 Solar Forum News and Announcements
- 1.4K Solar News, Reviews, & Product Announcements
- 199 Solar Information links & sources, event announcements
- 899 Solar Product Reviews & Opinions
- 256 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 656 Solar Water Pumping
- 816 Wind Power Generation
- 624 Energy Use & Conservation
- 620 Discussion Forums/Café
- 313 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed