The Longest Night
Comments
-
Turns out you were on the right track in a roundabout way. Panels are currently feeding 47 volts. I have a problem up on the roof somewhere. The panels normally feed about 80-85 volts. Too bad the wind is now gusting over 30 mph. Less than ideal for roof work.
I just don't know what would cause a 47 volt panel feed. I've never seen 47 volts from a single panel - as I recollect.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
softdown said:It was Outback who warned me (at their web site)about "HyperVOC" than can occur in very cold climates. They said I could only serial two panels. On paper - 3 is fine and I know a guy who does/did installations that way.
...Charging a 48 volt system?
Sorry, feel like I opened a book to a different page.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Completely wrong wiring can throw off weird voltage. But that seems pretty well impossible considering the connections are in watertight boxes. I guess looking at fuses is next. Perhaps something blew some fuses.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
Check voltages directly on the charge controller (Vpanel-in and Vbatt-out) and Vbatt-bus... See if those voltages makes sense (i.e., is the controller getting full&correct voltages. Is current changing the readings (Vpanel crashing, Vbatt "too high", etc.).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Problem solved - more or less. One of the four combiner boxes was putting out about 41 volts. The other three - 82 volts.
Simply by disconnecting the problematic source feeding 41 volts - the CC is now feeding my banks. Cloudy now but it is working.
Lesson - get yourself a BMS (Battery Monitor System) and maybe place the readout on the television or computer or ......
Pretty delicate system. Lost a little something somewhere that effectively took down all the panels to 47-48 volts. That from 80-85 volt strings.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
This usually happens in winter
A battery monitor may help you but really it is alot easier and cheaper to be able to "see" your system. The shot below shows a defrost at 10 pm at night, the solid hours in Absorption, and a missing temp sensor. You probably have most of what you need to do this. Having Soc on a lead-acid battery is overkill and may contribute to another type of failure. Good Luck
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
^^^Got a lot of emergencies going on right now. No way do I think about anything that hooks my stem up to the hackers highway, I mean the internet. No way.
My question now is; How did proper wiring transform into improper wiring? Easy to fix. Diagnosing? That took some time.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
You are misinformed. The monitor does not have to go into internet at all.
You could have seen the input voltage to the mppt from the array and logged it, gone back a week and found the exact hour it failed."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
I must have miswired the array when checking things last time. Surprised it lasted that long.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
This chapter appears ready for closing. The battery banks are up to ~52 volts at 9:30am while being fed 37 amps of power. The voltage is down from the low 80's but the current draw and time of day are the likely reasons for that.
Wouldn't have been a big deal but being sick and sleepless made it kind of grim.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
FWIW - They were being charged with 52 volts at 9:30am. Four hours later and the batteries finally have 52 volts/bank. May take a couple days to get to a full absorb cycle.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
Watch the current too. Ideally at least 10% of bank AH capacity. Or at the very least 5% rate of charge with full sun.Good luck,BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
softdown said:I must have miswired the array when checking things last time. Surprised it lasted that long.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Nasal polyps may be the cause of your problems. I went thru the same futile attempts with pills and sprays. EventuallyNeeded surgery to remove the polyps. It is considered brain surgery and cost $25000.Good luck.
-
tabbycat said:Nasal polyps may be the cause of your problems. I went thru the same futile attempts with pills and sprays. EventuallyNeeded surgery to remove the polyps. It is considered brain surgery and cost $25000.Good luck.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:tabbycat said:Nasal polyps may be the cause of your problems. I went thru the same futile attempts with pills and sprays. EventuallyNeeded surgery to remove the polyps. It is considered brain surgery and cost $25000.Good luck.
I don't feel like the only run to have a runny nose every few years. This one was a full fledged cold for a day - probably stress related. Was running yesterday. Funny how one feels so healthy after a recovery. Perhaps the rest helps in a way.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
mike95490 said:softdown said:I must have miswired the array when checking things last time. Surprised it lasted that long.
Still incredulous that one 42 volt feed pulled the entire array down to a 47 volt feed. Yet all 16 panels were reading 42 volts a couple days ago. They were yielding 37 amps of power at 9:30am yesterday. That sounds about right. I need to check the output at closer to high noon.
The battery bank did not get to 100% SOC yesterday. The bank is probably on the large side. Too bad that batteries can not be stored in a satisfactory manner. I'll bet a battery manufacturer could do well selling dry batteries, without electrolyte, that can be stored until needed.
I suspect the EPA put a few manufacturers down. We only have a couple left with Johnson Controls being completely Mexican mfg. I think. - even their previously esteemed Optima line. Lack of competition always has horrific consequences.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Keep in mind that solar array problems can take alot of time. The many that I have had to repair that others did often start out with my troubleshooting taking me one way. I often get into it and start getting conflicting data.
In the end it often ends up an intermittent internal connection inside a panel. Total PITA and travel time up the ying yang !!
Hint I see you have BP panels. They (the ones in the suit) are one of the prime sources of this kind of failure. They should be scrapped.
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Dave Angelini said:Keep in mind that solar array problems can take alot of time. The many that I have had to repair that others did often start out with my troubleshooting taking me one way. I often get into it and start getting conflicting data.
In the end it often ends up an intermittent internal connection inside a panel. Total PITA and travel time up the ying yang !!
Hint I see you have BP panels. They (the ones in the suit) are one of the prime sources of this kind of failure. They should be scrapped.
Two of the panels were incorrectly wired. Pretty concrete finding. It isn't necessarily over but it "might be".
My dad was a medical electrician for four decades. He always said that intermittent problems are the worst.
My gut feeling is that I have at least a 50/50 chance of having the issue resolved. Really going out on a limb with that prognostication.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Crossing fingers for you!
Intermittent related to temperature is even worse. no do not go there...."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Hard to determine with weather like this: https://weather.com/weather/hourbyhour/l/874b2d082ff2caeaf5d18b4a92a3b4f15c739702c08833b3547c3554ef50d9afFirst Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
Still feel your grape panels are too low a voltage to use with an FM80 with just 4 in series. I read you see 80 volts input, but feel that must be during sweeps and not under load since the VMP is <20 volts per panel...
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Lets relax for a day or two? I just found two panels that were wired incorrectly and apparently throwing everything off. I'll go check right now but clouds are intervening significantly.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
Getting 40-41 amps of power at 10am. Looks good right now. The question is - what will present in 3-4 hours?
I was getting morning charges even when the array was miswired. But the feed voltage was very low. Right now the incoming voltage is about 70 - which is drawn down by the current flow.
I feel generally encouraged by 40-41 amps of charging power. Right now anyway. The definitive answer would likely arrive in 3-4 hours if not for the expected cloud cover.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Photowhit said:Still feel your grape panels are too low a voltage to use with an FM80 with just 4 in series. I read you see 80 volts input, but feel that must be during sweeps and not under load since the VMP is <20 volts per panel...First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
softdown said:Photowhit said:Still feel your grape panels are too low a voltage to use with an FM80 with just 4 in series. I read you see 80 volts input, but feel that must be during sweeps and not under load since the VMP is <20 volts per panel...
I think you are confirming this when you say things like;softdown said:Right now the incoming voltage is about 70 - which is drawn down by the current flow.
The VMP when the panels warm up (NOCT) is likely 92% or less than that of the VMP at STC. So 19.67 x 4= 78.68 x .92 = 72.38 volts lessened by the distance they wattage travels on other lines(wires)... 70 volts is about what I would expect.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Things look better all the time. Approx. high noon readings: 75 incoming volts - 55 charging volts - 42 amps. Feel like a celebratory beer is in order. Doesn't take much to make me feel like celebrating. Waking up? Good enough reason.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
I think the FM80 will still function, but you are likely losing some of the positive aspects of the MPPT type charge controller.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Photowhit said:I think the FM80 will still function, but you are likely losing some of the positive aspects of the MPPT type charge controller.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
Intermittent clouds today - right now readings are consequently askew. Have received ~ 9.6 KwH of energy which seems pretty robust for 1pm.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed