Please critique my plans
Comments
-
ZebraStripes said:I have picked a battery capacity that should take care of us in both of these scenarios.Storage: Fortress Power 16.5kWh Lithium BatteryInverter/Charger: Schneider XW+ 6848ZebraStripes said:Panels: 24 Canadian Solar 355W Poly Panels in two strings of 12MPPT: Schneider XW 80A MPPT (I believe I only require 1,...ZebraStripes said:1. I am also considering these Peimar panels (https://www.altestore.com/store/productos-solares-en-puerto-rico/pr-paneles-solares/peimar-grid-tie-solar-panels-puerto-rico-p41241/#PR-PEI330P-EACH) because of their lower price and immediate availability (Have to wait on Canadian Solar panels to get here). Thoughts? Worth the wait on Canadian or will the Peimar suit me just fine?ZebraStripes said:2. The inverter manual suggests that it only be used with battery banks of at least 440Ah, but the Fortress battery only has a capacity of 360Ah. Will this be a problem / Why does the ah capacity of the bank matter here?
Lithium's don't suffer from this voltage sag, so I think you would be okay, granted the minimal capacity already discussed.ZebraStripes said:3. What's the most foolproof way to make sure I am buying exactly what racking I require? The altE warehouse is quite a drive from here, so I only want to make the trip once if I can.
Draw wire> write length, gauge of wire AND CONNECTORS!!!
draw junction box> write the junction box down, INCLUDING THE CONNECTIONS
When you are all done, buy an extra30% of each wire as well as connectors and crimping tool!
Then, make friends with someone at altE or where ever you buy stuff, so they can send you the 3 water proof wire restraints you forgot...lol.
Seriously you might have a 'pre wired' power center built, expensive, heavy, but more likely 'plug and play'.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Thank you for your well thought-out reply.1. We have a 1HP well pump that I'm a bit worried about, and we plan to also run some mini splits during the day when capacity allows (IE excess energy being produced). At night, our needs are very minimal and the battery should have no problems keeping up with us. The battery is supposed to have 16.5 usable kWh (18.5 total).2. Right now, our daily use fluctuates between 11 and 13 kWh. But we don't use our AC much at all. We are *HOPING* that during the hottest part of the day, once the battery is charged back up, we can use our excess production to power a mini split.3. We plan on expanding our energy generation/storage to our casita next year, and I was hoping we might be able to tie that into this inverter rather than going with a second one. However, if we would be better off with the smaller inverter and just adding a second inverter for the casita, I'm definitely open to that.4. Thank you for explaining the charge controller sizing. I originally had planned on two (One per string) but then talked myself into needing only 1 due to the voltage requirements. I didn't really understand what the 80A represented in their specs.5. Pen and paper was my plan for the racking. Glad to hear someone else say it.I know I can go with a pre-wired system, but this is a learning experience for me. Once I have my parts picked out and sized correctly (With the help of you very very smart people here), I have no problem doing the installation. This is the part that makes my head spin
-
You are talking about the 600 volt version of their charge controller aren't you.
QUOTE: "Schneider XW 80A MPPT (I believe I only require 1, because the total voltage going down the line will only be 12*24=288V, right? And if so, that's well within the parameters of the MPPT" Where are you getting your numbers from?. While these may be considered 24 volt nominal panels that's not the way you calculate your input voltage.
Canadian Solar 355 watt panel, 46.8 Voc. x 12= 561.6 volts. Add a chilly bright morning and you are watching lots of very expensive magic smoke float away.2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:You are talking about the 600 volt version of their charge controller aren't you.
QUOTE: "Schneider XW 80A MPPT (I believe I only require 1, because the total voltage going down the line will only be 12*24=288V, right? And if so, that's well within the parameters of the MPPT" Where are you getting your numbers from?. While these may be considered 24 volt nominal panels that's not the way you calculate your input voltage.
Canadian Solar 355 watt panel, 46.8 Voc. x 12= 561.6 volts. Add a chilly bright morning and you are watching lots of very expensive magic smoke float away.See, this is why I'm here - To learnI had originally written down that I wanted two of the 80A 600V charge controllers. Then today, while going back over the plan, I couldn't figure out why I wanted two, so I changed it back to one. So just to clarify - I would be good with two strings of 12 each, each running into their own MPPT, right?
-
Absolutely not! The voltage I just showed you in a series string of 12 will be lethal . You could run TWO strings of 6 panels into each controller. Whether it is cost effective for you to use such high voltage controllers is something you need to figure There's plenty of 80 amp controllers on the market with Voc. limits of 150, 200 and 250 volts. You will, With two strings save on fusing and combiner boxes but you pay a premium for the 600 volt controller. The 150, 200, 250 Voc. controllers will require fusing and combiners.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
I really appreciate you taking the time to try to help me. I apologize if my questions sound stupid - I am still learning and realize that I have a ton to learn.Can you explain why having two strings of 12 would be bad? If the CC is rated for 600V and the string is putting out 561V, what is the problem?Additionally, the smaller Schneider CC, it seemed like even at 6 panels per string, I'd be over the limits for it, as it states the maximum input voltage from the array is 150V.Again, I do appreciate the help, just trying to figure out all of the little things that go along with this.
-
ZebraStripes said:1. We have a 1HP well pump that I'm a bit worried about, and we plan to also run some mini splits during the day when capacity allows (IE excess energy being produced). At night, our needs are very minimal and the battery should have no problems keeping up with us. The battery is supposed to have 16.5 usable kWh (18.5 total).ZebraStripes said:2. Right now, our daily use fluctuates between 11 and 13 kWh. But we don't use our AC much at all. We are *HOPING* that during the hottest part of the day, once the battery is charged back up, we can use our excess production to power a mini split.
...whit lithium, there is minimal to no voltage drop, so it looks like this will be an interesting problem to overcome. Many people with lithium avoid charging to 100% and stay between 15 or 20% and 90%. There is very little voltage drop so this person was having his battery drained and not having the charge controller pickup the increased demand.
https://forum.solar-electric.com/discussion/354791/why-isnt-the-charge-controller-using-the-panel-to-feed-loads-when-the-battery-is-charged#latest
Yeah, I've enjoyed wiring up the system's I've done, and even when helping others. I always grab some 'S' clips and grounding lugs (not used as often these days, people going with WEEB(?) systems) When I go and check out other peoples systems being installed. Something you might consider are the wiring clips to keep the wiring clean, There are UL black wire ties, but they may only last 8-10 years, Stainless Steel 'S' clips will clip 2-4 wires to the frame of a solar panel and are made different if you are using PVwire or USE2(which is thinner) They are hand to have around, I have always heard that even the UL nylon Zipties become brittle and fail after 8-10 years, but I admit to using them for keeping wires coiled and things neat.
https://www.altestore.com/search/go?w=Search+Products&p=Q&ts=v2&w=clips&p=Q&ts=v2&x=0&y=0
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
You need to adjust the 561voc string voltage for record low temp at your location. Max voc is usually at ~dawn, which is also about when record low temps are recorded. In PR, maybe not a big issue (though a <10% buffer is skinny to me), but certainly a potential issue in colder climates.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Estragon said:You need to adjust the 561voc string voltage for record low temp at your location. Max voc is usually at ~dawn, which is also about when record low temps are recorded. In PR, maybe not a big issue (though a <10% buffer is skinny to me), but certainly a potential issue in colder climates.
Edit: Just found an article describing how to calculate Max VOC. Somehow this is the first time I'm coming across this. Thanks @Estragon
-
The colder the panel the higher the voltage. It's not that the panels are potting out any massive amounts of power first thing in the morning. They are putting out very little actually BUT, they will put out very high voltage first thing in the morning. You need to find the temp. coefficient stats for whatever panels you are going to use. Then you need to find the coldest typical temps for your area. Look up ASHRAE, I believe to get the weather info and calculate the voc. @ that low temp.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
So I just did the maximum VOC calculations for those canadian solar panels and the record low for this spot, and came up with 595.08 maximum VOC. Cutting it a little close I guessSo what's the solution? 4 strings instead of two? And then two 80A charge controllers, each handling two strings?
-
That would work. I don't know how those charge controllers work on 250ish. vmp. I would hope they don't need max smoke to operate efficiently. What is the voltage range on them?
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Not sure if you will be making your own cables?
Officially you should use the Code compliant tools, but I know what a good crimp looks like and choose to use a cheaper tool. These days they make cheap tools that function similar to the code compliant tools. with the dies being pressed together straight up and down. These work better than the tools that are hinged (like the cheap tool I bought 10+ years ago) I know I've used them both!
Don't buy this!
Go for something like this instead;
Link;
https://www.amazon.com/VIKOCELL-Crimping-Connector-Terminal-Crimper/dp/B0727P5PK7/ref=sr_1_8
Shows the 2 different types in operation;
https://youtu.be/fTUWW1sXJf8
Also important if you are going to make your own cables, be sure to get the higher strand wire, The cheapest stuff is often USE2 7 strand wire, it's a PITA to crimp, I got to the point I just fanned the wire out clipped 1 of the strands, then careful made sure the others were 3 x 3 into each side of the crimp.... Seriously! PVwire is typically(always?) 21 strand and much easier to crimp.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
littleharbor2 said:That would work. I don't know how those charge controllers work on 250ish. vmp. I would hope they don't need max smoke to operate efficiently. What is the voltage range on them?
-
Photowhit said:Not sure if you will be making your own cables?
Officially you should use the Code compliant tools, but I know what a good crimp looks like and choose to use a cheaper tool. These days they make cheap tools that function similar to the code compliant tools. with the dies being pressed together straight up and down. These work better than the tools that are hinged (like the cheap tool I bought 10+ years ago) I know I've used them both!
Don't buy this!
Go for something like this instead;
Link;
https://www.amazon.com/VIKOCELL-Crimping-Connector-Terminal-Crimper/dp/B0727P5PK7/ref=sr_1_8
Shows the 2 different types in operation;
https://youtu.be/fTUWW1sXJf8
Also important if you are going to make your own cables, be sure to get the higher strand wire, The cheapest stuff is often USE2 7 strand wire, it's a PITA to crimp, I got to the point I just fanned the wire out clipped 1 of the strands, then careful made sure the others were 3 x 3 into each side of the crimp.... Seriously! PVwire is typically(always?) 21 strand and much easier to crimp. -
The blue one works great. Done many hundreds of crimps, if not tens of hundreds. Photowhit is right about the other type. They don't work as well. There's some tutorials on youtube walking you through crimping the MC-4 connectors. Good thing they're cheap because you're bound to do a few wrong while you're getting the hang of them. Once you snap in the contact you cannot get it back out. Remember, Male contact into female MC-4 housing and Female contact into male housing. I say male and female housings because the male isn't necessarily the positive and vice-versa. The male on the back of the solar panels is the positive but when you are making extensions the female connector connects into the male output and has a male connector on the other end or whatever type on termination you require for the combiner, charge controller, etc..
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
@ZebraStripes
Attached is instructions on how to set up the Schneider for use with Fortress batteries if you don't already have info.
Question, why the 600V controller, is there a large distance between the array and controller? That apart from minor savings in wiring and combiner equipment would be the only benifits, the cost is ~ 3 times that of a 60-150's having the redundancy of multiple controllers can have benifits albeit at the expense of minor complexity, also consider multiple arrays at different orientations to extend solar hours, this will be less taxing on the batteries.
VERY IMPORTANT
Budget for lightning protection, SPD devices are essential in tropical climates and make sure the clamping voltages are suitable for the equipment, both AC and DC sides1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
An unfair comparison of an 80 amp controller and a 60 amp. The price difference is more like 2/1. The OP will need at least 2 controllers either way. The 80 amp also has multiple fans and fan speeds that may help in a hot climate. Either way they both are excellent products.
The 80 amp is just far easier to install and change later. A good case for having one of each also!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
mcgivor said:@ZebraStripes
Attached is instructions on how to set up the Schneider for use with Fortress batteries if you don't already have info.
Question, why the 600V controller, is there a large distance between the array and controller? That apart from minor savings in wiring and combiner equipment would be the only benifits, the cost is ~ 3 times that of a 60-150's having the redundancy of multiple controllers can have benifits albeit at the expense of minor complexity, also consider multiple arrays at different orientations to extend solar hours, this will be less taxing on the batteries.
VERY IMPORTANT
Budget for lightning protection, SPD devices are essential in tropical climates and make sure the clamping voltages are suitable for the equipment, both AC and DC sides
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed