Parallel with SLIGHTLY different Voltage
Ive done research and I know that putting panels with different voltages together isnt advised. BUT every time I find an exemple, its with really big differences.
So
I have 5x 48w panels = 3.02A 15.9V rated ( 3.35a 19.8V max)
but 1x 100w panel = 5.9A 17V rated ( 6.5a 21.6V max)
I run a 12v system ( 12v Charge Ctrl ) so i got them all In parallel
Questions;
1 - Its not 18v with 36v OR 12 with 24v ( double the V diff ). We re talking about 1.1V. In my case, Is it as bad as everybody says on the internet ??
2 - The real reason of my post is that I am thinking about buying an other Panel to the lot; 1x 90w 5.17A 17.4V rated ( 5.58a 22.58v max)
--- which would make a 1.5V difference with my 5x 15.9V. I am scared its going to draw down the New 17.4 making it see too many Amps and
wearing it down faster
3 - I feel limited to that one panel because all others are around 18v rated making 2.1v higher, which scares me. Should I worry ?
4 - am I wrong to think that the charge control being PWM so my understanding was that it limited the panels to what was needed thus making okay to
mix my voltage a bit???
Thank you all for your help!!
Comments
-
-
Within 10% you'll be fine. they are all 12 volt nominal panels. The lower voltage ones are older cells. PV cells have gradually gotten more efficient, resulting in higher voltage and current. Without even asking I'll bet they are all 36 cell panels.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:Within 10% you'll be fine. they are all 12 volt nominal panels. The lower voltage ones are older cells. PV cells have gradually gotten more efficient, resulting in higher voltage and current. Without even asking I'll bet they are all 36 cell panels.
Yes they are all 36cell which is why i felt compelled to buy an other 36cell panel.
Also I really neen the Question 4- answered. Does a pwm ctrl only regulate the V output or what the panel makes too ?_____________________________________________[3p3s 48w 15.9Vmp] [Flooded 2x 6v 150ah][Victron 50/100 700wMax MPPT] -
The voltage will find a balance point somewhere between the two, perhas ~16.5V connected in parallel
Question 4. The PWM controller will pull the input voltage down to a voltage slightly above battery voltage, as long as the input voltage capability is higher than the maximum charge voltage required it will work. Say maximum battery voltage requirement is 15V and the input is 16.5V this would work, usually the battery voltage during charging is 12-14.4V as the voltage reaches the absorption stage, the current will drop, at 15V (equalization voltage not regular voltage ) there should be very low current so voltage is not generally an issue on healthy batteries.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
KhellSk said:littleharbor2 said:Within 10% you'll be fine. they are all 12 volt nominal panels. The lower voltage ones are older cells. PV cells have gradually gotten more efficient, resulting in higher voltage and current. Without even asking I'll bet they are all 36 cell panels.
With your panels the only time you will have an issue would be if you were to series wire them due to a large difference between current output. since you are using a PWM controller and parallel wiring all your panels, you're fine as long as your controller is rated to handle the current output of your array.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
mcgivor said:Question 4. The PWM controller will pull the input voltage down to a voltage slightly above battery voltage, as long as the input voltage capability is higher than the maximum charge voltage required it will work.
Still, while full sun shining on it, My understanding is that would bring down the voltage WITHIN the panel thus raising the amperage? This would wear down the panel faster.
If not this would mean I could buy a 60cell @ 20v rated and get more for my money instead of buy a 36cell_____________________________________________[3p3s 48w 15.9Vmp] [Flooded 2x 6v 150ah][Victron 50/100 700wMax MPPT] -
Stay with the same 36 cell format is the best advice I can offer, a 60 cell module generally has a VMP of around 30V which may overcome the voltage output of the 36 cell modules creating feedback, thus reverse biasing the smaller modules into becoming heaters. Personally in the past I've connected various modules together in parallel, but they were always the same format, never tried your proposition, so not saying it wouldn't work, just have some doubts on the outcome.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
KhellSk said:
Still, while full sun shining on it, My understanding is that would bring down the voltage WITHIN the panel thus raising the amperage? This would wear down the panel faster.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
mcgivor said:Stay with the same 36 cell format is the best advice I can offer, a 60 cell module generally has a VMP of around 30V which may overcome the voltage output of the 36 cell modules creating feedback, thus reverse biasing the smaller modules into becoming heaters.
On one hand I people you saying that Amps cannot be exceded even if shorted. On the other hand what littleharbor2 said.
So yes. I will stick to 36cells modules but they are pretty rare and most of them a lot newer with a higher voltage like littleharbor2 said in his 1st post. 18v and 19v. I guess needed to know if 18 19v would fine(giving me more buying options) or
if I should sacrifice watt and money to find one closer to 16v_____________________________________________[3p3s 48w 15.9Vmp] [Flooded 2x 6v 150ah][Victron 50/100 700wMax MPPT] -
I wouldn't pay more for 16v. Slightly higher should work fine IMHO.
You do want PWM, as hot panels on a still day may not have enough voltage headroom for MPPT.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
KhellSk said:mcgivor said:Stay with the same 36 cell format is the best advice I can offer, a 60 cell module generally has a VMP of around 30V which may overcome the voltage output of the 36 cell modules creating feedback, thus reverse biasing the smaller modules into becoming heaters.
On one hand I people you saying that Amps cannot be exceded even if shorted. On the other hand what littleharbor2 said.
So yes. I will stick to 36cells modules but they are pretty rare and most of them a lot newer with a higher voltage like littleharbor2 said in his 1st post. 18v and 19v. I guess needed to know if 18 19v would fine(giving me more buying options) or
if I should sacrifice watt and money to find one closer to 16v
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
KhellSk said:Still, while full sun shining on it, My understanding is that would bring down the voltage WITHIN the panel thus raising the amperage? This would wear down the panel faster.
Current cannot increase beyond the Isc spec on the panel sticker (Isc = Amps Short Circuit)
No. You have made an incorrect assumption based on your imagination and not electronic engineering realities.If not this would mean I could buy a 60cell @ 20v rated and get more for my money instead of buy a 36cell
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
A 60 Cell panel would be Vmp~30 volts.
Vmp-cell is roughly 0.5 volts per cell... times X cells in series gives you Vmp-panel
The difference in current between Imp and Isc is something like 10% more current for Isc.
However, remember the definition for power is Power=Voltage*Current...- Power = V*I = 0 Volts * 1.1 Imp (more current with shorted panel output) = 0 Watts
And when you look at a 60 Cell vs 36 cell group of panels... Say they are both 200 Watts, and the 60 Cell panel will give you 5% more current at 18 volts Vmp (of a 36 cell panel)...- 200 Watts / 30 Vmp = 6.67 Amps @ 30 volts
- 18 Volt Vmp battery/Vpanel * 1.05x6.67 Amps (running high voltage panel at lower current) = 126 Watts
And, the way solar panels work, the "excess current" that is not used, actually "leaks" back through the cell... Remember that silicon solar cells are just diodes, and when Vcell (open circuit) exceeds ~0.6 volts per cell (Voc-panel~21.65 volts for your 36 cell panel), the current simply flows through the "forward biased" junction.
Panel costs are, mostly, based on $$$/Watt. And at a first estimate, a 200 Watt "12 volt" panel would cost the same as a 200 Watt "24 volt" panel.
However, there are other issues... One is that the higher the current in a panel, the more copper you need to conduct the current without getting high losses... So a lower voltage panel (all same wattage), will have more copper in it (not a big factor?).
The other $$$/Watt driver has been volume/automation/process improvement/product demand. "Grid Tie" Solar panels (Vmp typically 30 or 36 volts, but other voltages have been used), are cheaper because they are more popular (supply and demand).
For GT solar power systems, panel voltage is not a big deal... Nominally strings are around 200-400 volts for central inverter systems. Roughly 10 * 30 Vmp panels in series is Vmp-array~300 volts).
For battery systems, if you match (tend to be more expensive) "12 volt" (aka Vmp~18 volt) panels to a PWM controller (PWM controllers are very cheap compared to MPPT controllers), this tends to be less expensive for smaller systems (tends to be 400 Watts or less).
For larger systems, using "cheap" GT Solar panels (about 1/2 the $$$/Watt vs 36 Vmp~18 volt panels), the cheaper solar array brings the system cost down and "covers" for the more expensive MPPT controllers.
There are other reason that MPPT controllers plus "higher voltage" Vmp-arrays (longer cable runs from Array to charge controller) that can save a bunch of money on copper cable runs, and some other advantages.
20+ years ago, panels where probably in the $10-$20 per Watt range... Today they are in the $2 to $0.50 per Watt.
Saving 5x 48 Watt old panels (that are probably still good), vs just buying one 240 Watt panel (20 years ago, worth 2,400-4,800 new; today worth around $120 new--It does "hurt")--Saves a bunch of wiring and mounting--But at the cost of new panel+MPPT charge controller+shipping/taxes vs what you already have...
We have people all the time trying to figure out how to mix and match new/old panels, or how to find a replacement for an old/broken panel--And it is usually a pain. What was available/purchased 20 years ago is not the same as today. Many times, it was better to find a new home for the "orphan" panels (small 12 volt RV system, friend that needs some panels, Craig's List) and just move forward with a new 2018 system.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB.
Thanks for your effort
Yes i agree it would have been worth going new of if didnt have much to begin with.
But i been given 3x 48w-15.9v
And bought 2 more for for 20$ each and then found a 100w-17v for 60$. Pretty cheap i think for the wattts and siemens quality.
First, I thought i would be fine with 240w for my application but the. I started consuming more.and having less and less sun as we went through fall. So i bought the 100w. Now i know i still have room on my chrg ctrl and cloudy weeks are a b*tch. Plus all my panels are facing SE. So i wanna move 1 and add 1 to the SW corner.
My issues is resolved now. Thanks to mcgivor and littleharbour2 i know the information about not mixing diff voltage panels are meant for higher differences like 60cells with 72. I now know that by staying within 10ish % and with 36cells for the new panel, everything going to be alright.
Nowhere else could I have gotten more help and that technical. So i want to thank you all for your help!
what motivates you guys to help us noobies ?_____________________________________________[3p3s 48w 15.9Vmp] [Flooded 2x 6v 150ah][Victron 50/100 700wMax MPPT] -
@KhellSk asks,
what motivates you guys to help us noobies ?
Helping others is a positive thing to do, sharing information is a two way street, at some time we were all at the beginning, the recipients of information passed on by others, so it's only fair to reciprocate with the passing the baton on to others. Perhaps someday you'll be in the position to share your aquired experience with other beginners.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Tired of seeing folks ripped off by slick sales persons, which gives solar a bad name.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
It's a two way street for me here. I learn, as well as help and share information. It's good for the industry as a whole that people understand how this works as opposed to getting frustrated and giving up, thinking that solar won't work due to a bad experience.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
You can put a 60 cell panel in parallel with a 36 cell. But it will waste watts and would require a blocking diode on the 36 cell panel.
I am available for custom hardware/firmware development
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed