sealed, gel and lead acid setting on charge controller
wast
Registered Users Posts: 41 ✭✭
what happens if u use the wrong setting on your charge controller?? for example if I have sealed batteries and have my controller set for gel or flooded... curious to know what this does to batteries
Some sealed batteries need lower charging voltages. Too high, they can vent gasses with irreversible loss of capacity. Conversely, a flooded battery charged at too low voltage can form hardened sulfate over time, also with irreversible loss of capacity.Off-grid.
Pre-canned settings can sometimes be wrong. Measure the actual voltage coming from the charge controller and match it to the manufacturers guidelines - mystery solved.
+1 on what Marc said. The generalization that the charge controller is doing is dangerous and the "wrong" setting might actually be better for some batteries.
Generally gel and AGM have no way to vent gasses so a lower voltage may be needed. While a higher voltage can help flooded batteries.
Though I do wonder about the rigor of the science behind some recommendations.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
My battery manufacturer recommended I use "sealed" on the mt50 for my 250 ah Agm because it needed HIGHER voltage.
Hence, the suggestion to always set the system up based on the manufacturers spec.....not a generic "type" of battery.I deal with Concorde and Fullriver;Voltages that are great for Fullriver AGM's are not suitable for Concorde AGM's.MarcI always have more questions than answers. That's the nature of life.
Sometimes I do a double take when my Fullriver AGM's are charging at 58.8 volts. Good thing I left a Post It note saying that is recommended.Marc Kurth said:Hence, the suggestion to always set the system up based on the manufacturers spec.....not a generic "type" of battery.I deal with Concorde and Fullriver;Voltages that are great for Fullriver AGM's are not suitable for Concorde AGM's.MarcFirst Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
I'm Surprised that none of you know the reason to set Battery type to the right type of battery. Most PV controllers have several types of charge available.They can use Bulk Charge, Constant Charge, Boost Charge and Float charge. Finally they use a level called Equalization. Equalization is mostly used for Lead acid Batteries that are not Gel. A Gel battery is not supposed to go through Equalization according to Mighty Max Batteries. That is one of the reasons to set your controller to the right type of battery is important.