Lifepo4 replacement quandary
mcgivor
Solar Expert Posts: 3,854 ✭✭✭✭✭✭
Having spent much time reading posts on LiPo4 batteries, I've come to the conclusion that's the way I want to progress away from LA technology. Reading between the lines it would seem prysmatic cells are the way to go, the search for cells is overwhelming, I've been in contact with suppliers many of whom are willing to sell the cells but have no BMS system designed and or supplied by them, which means an after market BMS, not that that's a problem, it just when something goes wrong each will blame the other for the failure, should it happen. There is one supplier who has an integrated battery with BMS claiming up to 4 series 4 parrallel with their 12V 180 Ah batteries each of which has its own BMS, not sure how that works, here is the link to the supplier https://www.alibaba.com/product-detail/Polinovel-Latest-HD-12v-24v-180ah_60777826187.html?spm=a2700.galleryofferlist.normalList.11.1cdc65caXXOdg0&s=p Which way to go is the question. Oh yes China supplier, but when in Asia shop in Asia.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Comments
-
they even have a 10 Kwh Power Wall just for you... https://polinovel.en.alibaba.com/product/60807112821-806855448/Power_wall_solar_system_battery_51_2V_140Ah_oem_lithium_ion_battery_10kwh.html?spm=a2700.icbuShop.82.16.28b81a5fwbK2QT
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
looks like they also had an earlier model 9kW http://www.plgenergy.com/newsitem/277057753ps their most recent news postings are from 2015...
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
I wouldn't go for an LFP battery with integrated BMS unless it was from a supplier with a well known track record. I always make the assumption when designing a system that each part of the system is likely to fail during its lifetime and ask myself what would happen if each part of the system failed. Failure of the BMS could at best make the battery inoperable which could be expensive if the supplier doesn't back their products up with a decent warranty. At worst a BMS fault could take the battery out of its safe operating region which would be a safety issue.IMO if you are building a DIY system I think you should be very confident that the if the battery and/or BMS fails that the whole power system will fail safely.With this in mind I have just designed and installed my third LFP system for a friend which uses individual prismatic cells with one of these BMS's. I chose this as
- it is a fairly simple design based around a well know Li-ion battery monitoring chip made by Texas Instruments
- Can be monitored and controlled via bluetooth or USB.
- Is easy to reverse engineer
- Has been working well on our E-bikes for over a year.
- There is lots of user feedback, especially on the Endless Spheres Forum
I would stick to LFP prismatic cells that have a good track record. CALB and Winston prismatics being good examples.SimonOff-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
-
@karrak Thanks for the opinions, the integration of the BMS is a concern for the exact reasons you point out, the advantage of prysmatic cells is the ability to actually check the individual cell voltage by simply removing it from the bank, not easy with a manufactured all in one unit. The question of cell quality is always there, will look into the two mentioned, but it would seem there is a lot of rebranding or outsourcing of cells, price is another factor the quotes I've received so far are almost equal Ah to Ah equivalent ,with LA here in Thailand but given the deeper discharge capabilities cycle expectancy and no partial discharge issues makes them a bargain. However the primary reason is temperature, with ambient temperatures mostly 30°C or above batteries usually above that, LiFePO4 are supposed to tolerate higher temperatures better and cooling them would be easier given the sheer mass of LA. Lots to consider.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
So prysmatic cells it is, ordered them today 32 100Ah cells, will be a 4P 8S arrangement for 24V nominal, most vendors I've communicated with want to build a battery, usually using small cells in a sealed package with the BMS built-in. Did look into Winston and Calb, sent a request for a quote but never got a reply. The company I purchased from Hunan AUK has positive feedback generally from Australia, the price $2000 for 400Ah plus shipping $320. Looking into BMS systems now, it's going to be an adventure, but if it can be done, I will learn.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I have to assume that that is $2000 Auz??Unable to find 100Ah cells on Website, LINK?
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
I've been looking into the same thing. I called around but I found this place to be extremely helpful (for the totally ignorant me) and have a wide range of systems to choose from:I was speaking to Raj.BTW, I've seen a number of people post here about going to Lifepo4 but generally they seem to be talking about using a schneider controller.I have a Morningstar Tristar 60 MPPT that is fully programmable and I am wondering what thoughts are here about using that controller with lithium batteries? Don't mean to hijack so I can start a new thread if that would be better?
12 * 300 W (10 fixed rooftop, 2 movable pole mount), Morningstar Tristar MPPT 60, Magnum 4448 PAE, 64 200Ah CALB in 4p16s arrangement with 16 LED Balancers and a Choice BMS300 (It is lousy and I don't recommend but it provides high and low voltage cutoff) -
Lifepo4 are a lithium (hence the "Li"). They tend to be safer, and in our application, where power to weight & size ratios aren't critical, probably the best choice among the various current lithium chemistries. As for using the Tristar, as long as it can be programmed properly for the particular battery (and bms) under consideration, it should do the job IMHO.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
westbranch said:I have to assume that that is $2000 Auz??Unable to find 100Ah cells on Website, LINK?
https://www.alibaba.com/product-detail/Long-cycle-life-Rechargeable-100Ah-lifepo4_60725516304.html?spm=a2700.7724838.2017115.35.4f7a4665cgN8cb1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
@mcgivor
That is an unbelievably good price. In the states the equivalent would be over $1000 more. And I know you're going to be amazed when you start using then. Did you get a charger to balance them yet? The initial balance is the most critical aspect of using a LFP bank IMO. Mine has been in service a little over 2 years now. Let me know if I can assist in any way with the installation.
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
@Raj174
No not yet, wlii be speaking to the supplier about a BMS, will ask him, you mean a charger to charge each cell individually I assume.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Yes, each cell and then the entire bank is top balanced in parallel at 3.6 to 3.65 volts. It does take some time.
4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
This is a future replacement, I'll take all the time nesesary to learn before switching over, nothing like finding out you got it wrong when you depend on it.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thanks for the link. I suspected Alibaba after going to their website and going in circles for a while trying to get past bicycle battery packs etc
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
If the cells are good, I think all will go well. You just take it one step at a time. When I setup 16 (+1 spare) 195AH cells I balanced them in parallel and then made a 16S bank. Started cycling them and checking for cell voltage deviation. I figured, I would get a BMS if increasing imbalance made it necessary. Well after about 6 months with only 10 millivolts deviation I was satisfied that imbalance was not an issue. I did get a BMS, but just to monitor individual cell voltage with high and low limits. It also monitors bank voltage with upper and lower volt limits. It's like most things that seem like rocket science but it's not. In fact they are very much like any other battery, except for the 80% DOD and the almost total lack of necessary maintenance.
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
The primary job of a BMS is to make sure that no individual cell in the battery goes outside its safe operating temperature and voltage range.There are three reasons that I can see that could cause a cell go out of its safe operating voltage range.
- The battery is not balanced or the cells have differing capacities. With an LFP battery these conditions will only show up when the battery is nearly full charged or fully discharged.
- The charge controller/inverter is incorrectly programmed or a fault in either means that they don't stop charging/discharging the battery when it is full or empty.
- A fault in the battery or battery wiring.
A BMS can stop this occurring in a number ways- Instruct the charge controller or inverter via a hardware/software interface to stop charging/discharging when it detects that any cell has gone outside it safe operating conditions.
- Raise an alarm which requires a person to intervene and shutdown the inverter or charge controller.
- In the event of any cell voltage going too high stop the charge controller charging the battery by preferably disconnecting the solar panels from the controller or disconnecting the battery from the charge controller or in the event of any cell voltage going too low disconnect the inverter from the charge controller.
Two other important functions that either have to be done manually or can be done automatically are monitoring the individual cell voltages and balancing the battery if it goes out of balance.Simon
Off-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
- The battery is not balanced or the cells have differing capacities. With an LFP battery these conditions will only show up when the battery is nearly full charged or fully discharged.
-
mcgivor said:The company I purchased from Hunan AUK has positive feedback generally from Australia, the price $2000 for 400Ah plus shipping $320. Looking into BMS systems now, it's going to be an adventure, but if it can be done, I will learn.That is a good price, the latest batch of 100Ah CALBs i got were ~US$100ea.SimonOff-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
-
Dave said:I have a Morningstar Tristar 60 MPPT that is fully programmable and I am wondering what thoughts are here about using that controller with lithium batteries? Don't mean to hijack so I can start a new thread if that would be better?I had a look at the manual for the Tristar and as far as I can see it can only be stopped by sending commands to it via Ethernet or RS232. This is not necessarily a showstopper but would probably either need a BMS that is compatible with the Tristar or some micro controller like the Raspberry Pi that I use to monitor the BMS and send the appropriate commands to the Tristar. The other option would be a BMS that will preferably disconnect the solar panels or the battery from the Tristar.SimonOff-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
-
Raj174 said:Yes, each cell and then the entire bank is top balanced in parallel at 3.6 to 3.65 volts. It does take some time.In the past I would have agreed with this but it does need special equipment and is time consuming.For the last two off-grid systems I have set up, rather than doing this I used a BMS that would shut down the charge controller if any of the voltages on the individual cells went too high and slowly ramped the charge voltage up starting at 51.0V for a 15S battery (3.40v/cell) and adjusted the balance of any individual cells whose voltage was higher than the average. This balancing could be done with automatic cell balancing or manually.Do not try this unless you have a BMS that will shut down the charging automatically and do it under supervision.SimonOff-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
-
For a long time I've been a fly on the wall, reading much of what Simon @karrak has to say, obviously there is experience behind the information, which qualifies as knowledge. Rick @Raj174 I don't mean to take away from your input and totally understand your rationale, it makes sense, but requires a human, preferably the operator to keep watch, as the BMS. Unfortunately there's times when I'm away, for that reason a BMS that looks after my interests is of importance. There are so many to choose from, many appear to be a PC board without much else, I did find one which, although not the cheapest by a long stretch, seems to offer the features I like. One of them is drive outputs for mechanical relays/contactors with a NO contact rather than electronic switching within the BMS itself taking current readings from an external shunt, Omron has some excellent components for the purpose see pdf. Being involved with life safty equipment in the past, software is generally not an acceptable means of communication from safty standpoint to shutdown equipment, old habits die hard, not that this is life safety, unless there is a fire of course. Here is the BMS I'm considering https://www.alibaba.com/product-detail/2S-16S-100A-continuous-300A-peak_60734485241.html?spm=a2700.details.maylikehoz.13.ba31347bDCnDhF Really appreciate the input, let me know opinions on the BMS proposed.
Ivor1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:Here is the BMS I'm considering https://www.alibaba.com/product-detail/2S-16S-100A-continuous-300A-peak_60734485241.html?spm=a2700.details.maylikehoz.13.ba31347bDCnDhF Really appreciate the input, let me know opinions on the BMS proposed.This is actually a Chargery BMS16and has been around for a while.I think Chargery has a pretty good name. I would look in the Endless Spheres Forum for more information.I agree that linked up to the Omron relays that it would do the job.The one drawback with this BMS is that as far as I can see it doesn't output any data and can't be interrogated from an external source.In this day and age I like to have gear that can talk to external equipment. I have got very used to being able to check up on the three systems I have installed and the one I am currently building remotely via the Internet.This BMS doesn't do cell balancing, were you going to do this manually?Regarding having to rely on software, you are relying on the software in the BMS working correctly. Hardware that doesn't rely on software can also fail to work when it is needed. I am a fan of having pieces of equipment being able to work autonomously but also being linked to other equipment that can check if they are working.SimonOff-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
-
Sometimes a picture is best! Hi Simon! You said it perfectly! Hi Reliability is critical if you expect the life out of these systems.
The screen is from one of the best in the world at this, in so many applications!
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
karrak said:Dave said:I have a Morningstar Tristar 60 MPPT that is fully programmable and I am wondering what thoughts are here about using that controller with lithium batteries? Don't mean to hijack so I can start a new thread if that would be better?I had a look at the manual for the Tristar and as far as I can see it can only be stopped by sending commands to it via Ethernet or RS232. This is not necessarily a showstopper but would probably either need a BMS that is compatible with the Tristar or some micro controller like the Raspberry Pi that I use to monitor the BMS and send the appropriate commands to the Tristar. The other option would be a BMS that will preferably disconnect the solar panels or the battery from the Tristar.SimonThanks Simon, I'd definitely be using a BMS but that is more for balancing among the batteries. If I understood your comment, your issue was that the Tristar wouldn't stop the charge without an ethernet or RS232. That controller is quite programmable. I think you'd just program it to bulk up to the spec voltage (provided by manufacturer) and then set it to absorb at that voltage to complete the saturation and then drop down to whatever maintenance voltage is required or cut off completely whenever the absorption/saturation was complete. If I have this wrong I'd like to hear about it because this is one of the main issues I am trying to understand now. What sort of compatibility issues between the BMS and the Tristar would I need to worry about?The prices McGivor shows look incredibly good. I was looking at a 48V 200Ah system with BMS and miscellaneous cabling etc and I think with shipping it was pushing $7k, which I didn't think was all that bad compared to a LA system where's I'd need around 500 Ah to be comparable and would likely be $3-3.5K.12 * 300 W (10 fixed rooftop, 2 movable pole mount), Morningstar Tristar MPPT 60, Magnum 4448 PAE, 64 200Ah CALB in 4p16s arrangement with 16 LED Balancers and a Choice BMS300 (It is lousy and I don't recommend but it provides high and low voltage cutoff)
-
mcgivor said:For a long time I've been a fly on the wall, reading much of what Simon @karrak has to say, obviously there is experience behind the information, which qualifies as knowledge. Rick @Raj174 I don't mean to take away from your input and totally understand your rationale, it makes sense, but requires a human, preferably the operator to keep watch, as the BMS. Unfortunately there's times when I'm away, for that reason a BMS that looks after my interests is of importance. There are so many to choose from, many appear to be a PC board without much else, I did find one which, although not the cheapest by a long stretch, seems to offer the features I like. One of them is drive outputs for mechanical relays/contactors with a NO contact rather than electronic switching within the BMS itself taking current readings from an external shunt, Omron has some excellent components for the purpose see pdf. Being involved with life safty equipment in the past, software is generally not an acceptable means of communication from safty standpoint to shutdown equipment, old habits die hard, not that this is life safety, unless there is a fire of course. Here is the BMS I'm considering https://www.alibaba.com/product-detail/2S-16S-100A-continuous-300A-peak_60734485241.html?spm=a2700.details.maylikehoz.13.ba31347bDCnDhF Really appreciate the input, let me know opinions on the BMS proposed.
Ivor
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
So Rick other than the Chargery BMS 16 not being able to ballance or communicate with external devices how is it from a quality performance standpoint. My understanding is balancing is not a regular task, but rather a one time affair done before assembly of the bank to ensure all cells are at, or as close as possible, (please correct me if I'm wrong ) to equal SOC, so doing it manually with single cell chargers is possible, albeit time consuming. The remote communication or a access via a PC is not something that interests me to be honest, why I like the fact it has its own display.
Simon, the reference to software control was to do with the use of data to comand a function, specifically with regards to fire alarm systems, where a physical relay contact is required as a fail safe, to shut down ventilation fans for example. Direct digital control , DDC, engineers always wanted to use digital input to their systems to shut down equipment over a LAN network, not fail safe. Also the transmission of alarm signals couldn't be transmitted via a VOIP telco system, it had to be physical land line, that is changing however with the use of multiple communication means to monitor each other, VOIP and cellular as examples, times are changing and physical land lines are fast becoming a thing of the past. The use of mechanical relays to disconnect charge and discharge, as apposed to internal mosfets, or other means, would make it reletivaly easy to include a second BMS simply as a monitor of the primary system, interlocked via a second contact in the relay coil circuit. Perhaps I'm over thinking this a little, but redundancy is not nesesarally a bad thing.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Dave said:Thanks Simon, I'd definitely be using a BMS but that is more for balancing among the batteries. If I understood your comment, your issue was that the Tristar wouldn't stop the charge without an ethernet or RS232. That controller is quite programmable. I think you'd just program it to bulk up to the spec voltage (provided by manufacturer) and then set it to absorb at that voltage to complete the saturation and then drop down to whatever maintenance voltage is required or cut off completely whenever the absorption/saturation was complete. If I have this wrong I'd like to hear about it because this is one of the main issues I am trying to understand now. What sort of compatibility issues between the BMS and the Tristar would I need to worry about?For everyday operation if the battery is balanced and there are no faults or stuffups you are right that just setting the bulk,absorb and float voltages is all you need to do. The problem is that if something goes wrong and one individual cell voltage goes out of its safe operating range the BMS needs some way to shut down the charge controller or the inverter.I think the bare minimum is to have the BMS generate an alarm which a person would act on. Rick@Raj174 and I use this approach with our systems because we have a good understanding of the batteries and keep then under surveillance. For the systems I have installed for friends I have taken a more conservative approach. The system I installed five years ago will disconnect the solar panels from the solar controller if a fault occurs. The two new systems I have just built go one stage further and use a Raspberry Pi micro controller that I have programmed to monitor the BMS and will send commands to the PIP5048 Inverter/charge controller to shut it down. As a further level of protection if this doesn't work the BMS will autonomously disconnect the solar panels from the controller or disconnect the battery from the Inverter. To me this is the gold standard which would require a number of separate failures before there is any safety issue.I would be interested to know what the Electric Car Parts Company has to say about BMS systems and battery protectionSimonOff-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
-
mcgivor said:
The use of mechanical relays to disconnect charge and discharge, as apposed to internal mosfets, or other means, would make it reletivaly easy to include a second BMS simply as a monitor of the primary system, interlocked via a second contact in the relay coil circuit. Perhaps I'm over thinking this a little, but redundancy is not nesesarally a bad thing.The one problem with using mechanical relays is that they use quite allot of power. For your system if you are using the Omron relays I would think you would have to use a G9EC-1 as the main inverter relay and G9EA-1 for the charge controller. Combined these draw ~16W which equates to energy use of ~0.4kWh/day. Maybe a better arrangement would be to use MOSFET switches or can you shut down your inverter and charge controller via external inputs or switches?The BMS I mentioned in in an earlier post uses onboard MOSFET switches to disconnect the battery, will monitor the cell voltages and do limited balancing and uses very little power, in the order of a few mA if not communicating with the rest of the world.The attachment to your post describes the way that I now do my initial balance. I use a bench power supply to boost and a 1 Ohm resistor to drop individual cell voltages. I think the CALB cells that I am in the process of commissioning are all within ~1%SOC balance and am trying to balance them using the onboard balancing circuitry of the BMS even though the balancing current is only ~50mA. It is taking a while not because of the small balance current but because of the lack of sun. For a change we are having a wet and cloudy winter.Simon
Off-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
-
I use a Raspberry in addition to the BMS monitor that I worried would shut down power when I was not home. They both get the can bus data but it takes both to shut down power. I also tested the system with what is called a failed power bridge test. It is basically a short on DC in to the inverter. The first short test tripped the battery breaker. The second short blew the fuse and tripped the breaker. I like both and feel pretty safe. This was all 2 years ago and all is well.
There should only be 2 things that shut down power offgrid, it is a new wrinkle that the battery is a 3rd. My solution takes it back to a dead battery or overcurrent protection causing loss of power. I definitely would not use relays. Just protect your network cables or double them.
Take a look at JEHUGARCIA on Utube for some ideas. I would not do any of this but for hobbyist he is pretty popular. Typical Southern California mindset and he is kind of funny.
https://www.youtube.com/watch?v=e_kTMDToieE&t=3s
Currently testing a second battery / inverter and it's on the bypass of the power distribution panel. This gets us to a completely redundant power system which is nice. Since it is new and has low hours on it I have to watch it alot.
It sounds like you (mcgivor) are still thinking this out? Maybe just wait another year and see? I would not jump into this if you question all the work. As I have said, this (homebrew) is not for my clients and I just do not have the time for it. Good Luck"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
mcgivor said:So Rick other than the Chargery BMS 16 not being able to ballance or communicate with external devices how is it from a quality performance standpoint. My understanding is balancing is not a regular task, but rather a one time affair done before assembly of the bank to ensure all cells are at, or as close as possible, (please correct me if I'm wrong ) to equal SOC, so doing it manually with single cell chargers is possible, albeit time consuming. The remote communication or a access via a PC is not something that interests me to be honest, why I like the fact it has its own display.
Simon, the reference to software control was to do with the use of data to comand a function, specifically with regards to fire alarm systems, where a physical relay contact is required as a fail safe, to shut down ventilation fans for example. Direct digital control , DDC, engineers always wanted to use digital input to their systems to shut down equipment over a LAN network, not fail safe. Also the transmission of alarm signals couldn't be transmitted via a VOIP telco system, it had to be physical land line, that is changing however with the use of multiple communication means to monitor each other, VOIP and cellular as examples, times are changing and physical land lines are fast becoming a thing of the past. The use of mechanical relays to disconnect charge and discharge, as apposed to internal mosfets, or other means, would make it reletivaly easy to include a second BMS simply as a monitor of the primary system, interlocked via a second contact in the relay coil circuit. Perhaps I'm over thinking this a little, but redundancy is not nesesarally a bad thing.
I don't use the balancing method describe in the attachment, I use a single cell charger to get all the cells up to 3.38 to 3.4 volts then put them all in parallel with busbars. Or, if they are already close in balance, charge them in series up to the same voltage then put them in parallel. Once in parallel, they are charged with the 3.65 volt charger until they reach 3.6 volts. The charger I use for this is 10 amp.
IMO this initial balance is good for 2 or 3 years, at least that is what I found with my HiPower cells. A rebalance could be done when necessary, it just involves paralleling the bank as described before. I have tried using the rebalancing method Simon mentioned, manually draining individual cells with a resistor to bring them into balance, but it is a bit too tedious for my liking. So I stick to what works for me.
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
what a fine resource this blog is! i had
not thought about the need for an auto disconnect but I'll contact electric car parts for their perspective and update here.
before i move forward, I'm hoping to find a buyer for my batteries since they should have quite a bit of life left and i can't see just wasting them.12 * 300 W (10 fixed rooftop, 2 movable pole mount), Morningstar Tristar MPPT 60, Magnum 4448 PAE, 64 200Ah CALB in 4p16s arrangement with 16 LED Balancers and a Choice BMS300 (It is lousy and I don't recommend but it provides high and low voltage cutoff)
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed