is it possible to build a 240V solar system?
hmong2017
Registered Users Posts: 39 ✭✭
I have a 4HP 240V AC Well Pump. We are paying too much to irrigate our farm.
I was wondering instead of changing all of my pump system into a solar pump system, Is there a way to build a 240V Solar System to power my old well pump?
I need 240V AC not 240VDC.
I tried to look up US 240V plug power inverters, but I don't see any. Is it because it's not possible?
If it's possible. Please help create a list of what I need. Thank you.
I was wondering instead of changing all of my pump system into a solar pump system, Is there a way to build a 240V Solar System to power my old well pump?
I need 240V AC not 240VDC.
I tried to look up US 240V plug power inverters, but I don't see any. Is it because it's not possible?
If it's possible. Please help create a list of what I need. Thank you.
Comments
-
Here is some starting information:Re: Working Thread for Solar Beginner Post/FAQDoes any of the above look "interesting"?
Some discussions about VFD (Variable Frequency Drives)... Basically a variable frequency inverter with (typically) three phase output. Used to soft start motors (handy for 3 phase well pumps, or pumps with well head starting capacitor) and can also turn an AC motor into a variable speed motor (very handy for pumping applications).
WELL PUMP and Inverter QUESTION
Wind/solar for large scale pumping etc (out of my depth!)
could use knowledge - using Gould jet pump - transfering from 230vAC to ? DC (new link/thread 10/27/2012)
Help required to design off grid system (information on possibilities to connect "standard VFDs direct to solar panels) (new link 1/13/2013)
And from a new poster, link to solar VFD (looks interesting):
VeichiElectric said:
u really should read this article about solar pumps: http://www.veichi.org/solar-water-pump-inverter.html.
In your case I wonder if a solar PV inverter would help or not.
-Bill
1/7/2017:
Dave Angelini said:
Grundfos has been doing solar water pumping for 30 years in the Americas and over the seas
http://us.grundfos.com/about-us/news-and-press/news/Pumped-by-the-Sun.html
They have some really nice plant tours down in the Fresno area of California.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I'd start by carefully investigating the efficiency of your current system. Pump efficiency, pipe losses, reduced water usage, off-peak rates, lower GPM for more hours, etc. Then I'd look into a grid-tie system.
I am available for custom hardware/firmware development
-
Depending on what state and incentives currently exist, there may be some tax or rebates for installing GT solar.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
A grid tie is great. They are getting harder to get as utilities are taking the incentives away. You can do a zero export system if you only pump during the day. Been doing a few of them lately for pumping.
As the guys have said here, you need a new 3 phase pump and VFD with a good controller built for it.
There are incentives for the pump in this state so conservation is always the first step, if you come back to your thread here...."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
You would at least need a variable frequency drive to start 3 phase pumps that way they can be started with out a huge start up surge.
There are a ton of off grid inverters that make 240v. The host of this forum sells a bunch of them.
You don't have to have a controller made for your well pump, the parameters and inputs that come built in with the drive are more than enough to control a pump.
2 things we need to know is how much money you have to spend.
And how much power do you use?
Maybe 3rd, how much water do you use and how deep is your well?Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
The original poster is probably somewhere in the California Central Valley.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Calafornastand, their's the first problem.
Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
I'm a little confused. There's several responses about 3-phase, but the OP only mentioned 240V. How do we know he needs 3 phase?
If his pump is 240V 2-wire, one of the Schneider split-phase Sw or XW inverters would satisfy.
Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case. -
A VFD which is typically a 3 phase device, it can actually be used with a single phase input to provide 3 phase output, the input could be AC or DC because the VFD is going to rectify an AC input anyway. Using a 3 phase pump is more efficient with lower start up inrush, there are of course other options like DC pumps which need less of the complexity, but may have limitations on total head, without those figures everything is hypothetical.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Horsefly said:I'm a little confused. There's several responses about 3-phase, but the OP only mentioned 240V. How do we know he needs 3 phase?
If his pump is 240V 2-wire, one of the Schneider split-phase Sw or XW inverters would satisfy.
The best solar contractors would do this along with selling a solar system. It makes the whole system look very good on paper when the power bill comes. Too bad the OP never came back...."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Motors over ~1-2 HP and are commonly 3 phase. Both cheaper and more reliable (no starting capacitors, no "extra starting windings" that are not used once the motor is up to speed, etc.)... 3 phase drops to commercial sites is very common.
So, don't know if this well pump is 3 phase, but is a good guess that it is probably is.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I'll take your word for it Bill. I know I've seen 2-wire 230-240V soft-start pumps of 2.5HP from Grundfos. Maybe they are just the exception.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case.
-
Grundfos pump motors can be permanent magnet poly phase with an internal VFD. (Their 900 Watt submersibles are generally this,I believe).
It just depends on the what power is available and which pump motor was purchased.
3 phase with vfd motors are a pretty flexible combination.
BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Horsefly said:I'll take your word for it Bill. I know I've seen 2-wire 230-240V soft-start pumps of 2.5HP from Grundfos. Maybe they are just the exception.
If the OP ever came back, we could maybe find out what he had. Even if he had a 3P pump, adding a VFD to it might not do him much good as this needs to be designed into the system to save max energy. Just adding a VFD might get you a softer start but all of the other factors really need to be addressed for max savings of energy. Like does he really need 4HP and quite a few more.
I get grid people asking me to help them go offgrid and have solar. Since I do not want to have anything to do with utility solar hassles, and there are plenty of grid solar folks who do, I tell them, how much do you want your utility bill to be? It is then a matter of saving the energy that they are wasting. Usually it is something like this here, adding a mini split to reduce the huge load of a forced air ducted system, or replacing a pool pump with a 3P VFD drive. I bill them and no one has to go on the roof! You should see the money people are wasting.
It does take money to start something like this."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Franklin has the line of Fhoton Solar Pump with many options that might be interesting for others who want to run without batteries.
-
NANOcontrol said:Franklin has the line of Fhoton Solar Pump with many options that might be interesting for others who want to run without batteries.
There are quite few solar direct pumps now. The first was grundfos and there are at least 4 that come to mind."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed