Odd behavior of my system, Low Battery Cut-Off is goofy
Organic Farmer
Solar Expert Posts: 128 ✭✭
We have 4400 watts of solar panels, a 'Four Star' E-panel from wholesalesolar, 'Midnite Classic' 150 Charge-controller, 'Magnum Energy' inverter, a 48VDC / 600AH battery bank
[with twenty-four EXIDE marine deep cycle batteries [27MDCST] in 6 strings with 4 batteries in each string].
My EQ voltage is set to 62.4V
Absorb is 59.2v
Float is 53.2v
Absorb Time is 4 hours
EQ time is 3 hours
BMK is set to 600ah
Charger is set to 30A [I am using grid power]
Battery type is flooded
Charger absorb is 4 hours.
LBCO setting is set at 48.8.
This Sunday I did a 4 hour EQ charge. Today after the sun went behind clouds for a couple hours, the system shut down saying LBCO at 96%, the charge-controller is reading 50.8vdc
So what gives?
Why is it going into LBCO at 50.8vdc when I set LCBO to 48.8vdc?
My EQ voltage is set to 62.4V
Absorb is 59.2v
Float is 53.2v
Absorb Time is 4 hours
EQ time is 3 hours
BMK is set to 600ah
Charger is set to 30A [I am using grid power]
Battery type is flooded
Charger absorb is 4 hours.
LBCO setting is set at 48.8.
This Sunday I did a 4 hour EQ charge. Today after the sun went behind clouds for a couple hours, the system shut down saying LBCO at 96%, the charge-controller is reading 50.8vdc
So what gives?
Why is it going into LBCO at 50.8vdc when I set LCBO to 48.8vdc?
Comments
-
Large loads, especially motors, can momentarily sag the battery voltage which could cause a LBCO, on a 48V nominal system the LBCO setting would normally be below 48V to avoid nuisance cut offs, somewhere around 46V would prevent such issues.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Check the voltage at the DC input terminals for your inverter... Also, try 46.0 volts (11.5 volt @ 12 volt bank) and see what happens (not a bad cutoff voltage for a decently loaded flooded cell lead acid battery bank)--And perfectly OK for testing your LBCO question.What is the load on your inverter (Watts, motor/pump/etc.)?As a starting point, roughly 3,000 Watts would be a good maximum load for your battery bank (and even 3,000 Watts for solar array maximum). You have charging set for 30 amps max? 60 Amps (10% rate of charge) should be OK (if charger is capable) for a a flooded cell/AGM type battery.-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
My SW Inverter also has a Low Battery Cut Out Delay Setting just for this reason, so that if a large load momentarily drops the voltage it will not cut the inverter off. This setting is set in seconds. You might look for a setting like this in the Magnum. I am set to 23v (24v system) and 55 seconds for Low Battery Cut Out Delay.
REC TwinPeak 2 285W 3S-3P 2.6kW-STC / 1.9kW-NMOT Array / MN Solar Classic 150 / 2017 Conext SW 4024 Inverter latest firmware / OB PSX-240 Autotransfomer for load balancing / Trojan L16H-AC 435Ah bank 4S connected to Inverter with 7' of 4/0 cable / 24 volt system / Grid-Assist or Backup Solar Generator System Powering 3200Whs Daily / System went Online Oct 2017 / System, Pics and Discussion -
Thank you, everyone.
-
I changed the LBCO setting to 48.0vdc and we will see what happens next. Our biggest load is our well pump 240vac 7amps, I do not always hear when it kicks on though. So I have no idea if that is what is causing this issue.
Tech support at Wholesale Solar suggests that I record the gravities from all cells, thinking that a battery may have gone bad. Since I have 24 batteries I have been avoiding doing this. If it turns out that I have one bad battery, I hate to consider what the solution would then be. -
Remember there is the conversion ratio, 7A at 240V is 35 A at 24V, simply using nominal voltage. The inrush of the pump could be 10 times the run current, or 350A, for a fraction of a second, this is where a time delay on LBCO is essential. Still thinking 48V LBCO is over conservative, but one needs to find the sweet spot where nuisance gives way to what actually works in a particular situation.
Edit. 7A at 240V is 17.5 A at 48V, inrush 175 A possible.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
How old are the batteries?
The "27MDCST" appear to be Lead Calcium batteries;
Info here includes "Calcium/calcium construction gives accessible maintenance-free performance"
https://www.tractorsupply.com/tsc/product/exide-stowaway-marine-rv-deep-cycle-battery-27mdcst
I didn't see another reference to Calcium in a quick check, but it does say maintenance free design which would indicate Lead calcium.
Lead calcium have a shorter life span in a true deep cycle situations.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
My XW inverter came stock with a 46v cut off @ 60 seconds
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
My system is cutting out when the batteries still have a lot of charge in them.. Im not that great with understanding my system but im assuming its due to low volts or amps. the batteries are getting on the older side but its a lot of money to replace them. Has anyone heard of this battery reconditioning http://smarts919_5589.gr8.com/ is it legit and is it something i could do to my sealed gel batteries to extend their life. Not really looking forward to the replacement cost
-
Batteries have a life expectancy just as we do, so just like there sellers for the alixir of life for humans, there are sellers of the alixir of life for batteries. That's my take on marketing anyhow, when one is old, or a battery is old, both are old it's a natural phenomenon that can't be reversed.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thanks Mate I guess im just hoping for a way to get more life out of my batteries as they are a huge cost and for $47 I thought maybe give it a go. I was hoping someone else had tried it ?
-
Some folks use Desulfators to extend battery life (some folks love them, some folks hate them, many folks don't see any good/bad from them).
I know nothing about this company that rejuvenates lead acid batteries. It started as a kickstarter project for the "battery rejuvenator" charger, and turned into a company that uses the charger to buy/receive old batteries and sell rejuvenated batteries:
https://revoltbatteryexchange.com/
The above (and a little desulfator talk) is from a Candlepower Forums thread:
https://www.candlepowerforums.com/vb/showthread.php?384605-Rejuvinator-Lead-Acid-(Gel-Cell-)-on-Kick-starter
-Bill "your mileage may vary" B.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks for your advice i might give it a go on some other batteries first and see if it is usefull
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed