Lead acid capacity in freezing temps
mountainman
Registered Users Posts: 439 ✭✭
My batteries specs are 208 amp hr but only 50% at 0 degrees. Question since at 50% on capacity do I charge on 10% of 208 or 104 amp hrs. One more thing which is worst on a battery bank discharging to 50 soc and charging at c10 or discharging to 75% soc and charging at c 5. On cloudy days charging with generator at c8.
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Comments
-
Cold temps slow down the chemical reactions in the battery ( Li batteries go downhill fast below +40F)
But I know of nobody who changes charge rates with temps. The BTS (battery temp sensor) with many high end charge controllers, adjusts the charging setpoints + & - according to temps, but not the amps. So I dont think I'd worry about it.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
So keep it at as is. Any thoughts on which is worse on battery bank daily 75% soc at 5% charge rate. Or 50% soc at 10% c rate?2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Probably not a huge difference.
Some have argued that both of those are 1x charging cycle. So, from a pure $/ah cycle cost, a 50% discharge is supposed to be more cost effective.
Personally, use the system the way you need it. Don't drive yourself nuts trying to be perfect.
BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
0 Freedom or 0 Canadian?First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
> @mountainman said:
> So keep it at as is. Any thoughts on which is worse on battery bank daily 75% soc at 5% charge rate. Or 50% soc at 10% c rate?
A 75% SOC is probably marginally better, BUT there are other factors to consider. Assuming a cold bank (0°f?), sulfation will take much longer than it would with a hot bank, so going to 50% may not be so bad as long as it doesn't stay there for long (like many days/weeks). Also, charging with a generator from 50-80% or so can be more fuel efficient that charging from 75-100%.
IMHO, you should give a cold (FLA) bank all the current it will take, assuming voltage is compensated for temp by a RTS. The only reason I limit current is to prevent overloading the generator in use. I don't change the limit based on reduced winter capacity.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Thanks everyone. In reviewing my battery specs at 75 soc they should last around 7 years but at 50 soc roughly 3 years so from a money stand point 75 soc would be better. So im gonna add 2 more batterys. On cloudy days in early morn I run a 2000 watt generator on a bulk of c6 35 amps with what I have now or c12 with 4 batteries from a dumb car charger for 2 hrs or so. Until the volts reach 14.8 then let solar take over Even on cloudy days I'll get about 2.2 amps.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Yes the batteries will last longer but will require a larger bank to supply the same Ah as a smaller bank discharged to 50%, that's where the $/Ah comes in, when calculated the actual energy cycled is close, but replacement means they will be new more often, you pays your money and makes your choices, basically a matter of opinion, I'll keep mine to myself.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
My experience with cold batteries is that it doesn't take much to knock them down.
And not much to bring them back up.
FLA at about 0F.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year. -
With the larger bank I'd be able to go a cloudy day without using the gen. I think the gas savings tips the scale for me.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
With a larger bank the PV needs to be able to recharge after a cloudy day, if currently you have the need to run a generator, the need will be still there, only for longer periods, albeit less often.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I understand what your saying larger bank. Needs more pv and longer gen charger time even more gas!!! I'm maxed out on a 30 amp controller so more panels more racking more wire another controller.200 amp hrs in winter isn't enough for me2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Having a 12V system restricts expansion going 24V would allow double the PV on the same conductors, same controller, if compatible, but would require an inverter change, inverter chargers are better than using a car charger, in terms of efficiency. Battery wise, less parallel connections smaller conductors and fuses/breakers. All comes down to needs and of course budget.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I'm in a rv so guess I'm stuck with 12 volts. I use 75 amp hours per day. My panels bring in 100 or so on a good day. But my batteries in these temps are giving 50.My thoughts were with 400 amp hrs I'd be able to get my 75 and still have enough solar to recharge in a day?2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed