Equalization current for flooded batteries questions
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Comments
-
Equalization is only performed on a battery that is fully charged, so the current draw should be comparatively low when the voltage ramps up to the equalization level.
You can set the max current, which the charge controller will achieve by reducing the voltage - but the whole point is to hold the higher Equalization voltage. I don't see a need for limiting charge current, because the increase in current draw will be transitory anyway.
I always have more questions than answers. That's the nature of life. -
Is the EQ temp compensated with a properly working remote sensor? It sounds like either the battery wasn't really full before the EQ, or the EQ voltage is too high relative to temp. IMHO the EQ should only draw more than a small current for a short time (while voltage rises from Vabs to Veq), then just take a couple amps to hold it there.
Also, I assume the 25a is really net to the battery (not including any loads).Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Marc Kurth said:Equalization is only performed on a battery that is fully charged, so the current draw should be comparatively low when the voltage ramps up to the equalization level.
You can set the max current, which the charge controller will achieve by reducing the voltage - but the whole point is to hold the higher Equalization voltage. I don't see a need for limiting charge current, because the increase in current draw will be transitory anyway.
The voltage is temperature compensated, no loads present, to answer questions whilst writing this, the one hour EQ is the curious question, longer slower, or hard and fast, perhaps someone with Schneider experience can shed some light1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Sounds like a question for @Dave Angelini.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
To be clear, I think that you have said that:
Your Morningstar controller would hold EQ voltage, but the batteries only drew 6 amps.
Your Schneider controller holds the same EQ voltage, but the batteries draw 25 amps.
I can't wrap my head around that.
Was the current draw with the Morningstar low because it wasn't reaching the equalization voltage?
If you meant that you only want to hear from people with Schneider experience, I will stop now.
Marc
I always have more questions than answers. That's the nature of life. -
Marc Kurth said:
To be clear, I think that you have said that:
Your Morningstar controller would hold EQ voltage, but the batteries only drew 6 amps.
Your Schneider controller holds the same EQ voltage, but the batteries draw 25 amps.
I can't wrap my head around that.
Was the current draw with the Morningstar low because it wasn't reaching the equalization voltage?
If you meant that you only want to hear from people with Schneider experience, I will stop now.
Marc
The Morningstar reached the voltage but at a lower current for a longer period.
The Schneider reaches the voltage at a higher current for a shorter period,, 1 hour vs 3 hours
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
@ Marc Kurth, sorry, not just people with Schneider experience, although they would be helpful, Amy input is welcome , thanks, your coments are valuable and appreciated.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:Marc Kurth said:
To be clear, I think that you have said that:
Your Morningstar controller would hold EQ voltage, but the batteries only drew 6 amps.
Your Schneider controller holds the same EQ voltage, but the batteries draw 25 amps.
I can't wrap my head around that.
Was the current draw with the Morningstar low because it wasn't reaching the equalization voltage?
Marc
The Schneider reaches the voltage at a higher current for a shorter period,, 1 hour vs 3 hours
But the battery determines the current draw based on the voltage being applied. At any given voltage, a battery will draw exactly the same amperage from whatever is applying that voltage (Assuming that the power is available)
The only way that a charging source can control amperage draw by the battery is to change the voltage being applied to it. A charging source cannot increase the battery charging rate, unless it increases the voltage.
I'm wondering if your battery(s) have developed a partial short. That would explain the higher 25 amp draw at the same voltage that previously caused the battery to draw only 6 amps.
Just thinking out loud, because something doesn't make sense.
Marc
I always have more questions than answers. That's the nature of life. -
It's not making sense to me either. If the change in behavior happened when the CC was changed, it mostly (but not entirely) rules out the condition of the bank.
Have you checked SG at any point(s) in the process? It may help to know if the end of absorb really is at fully charged.
It might also be worth checking actual voltage at the bank and manually working out the temp compensation as a sanity check to be sure the CC is properly compensating.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Perhaps there may have been some oversights on my behalf, including factors such as cell ballance being different during the respective EQ's. It is entirely possible the Morningstar may have begun at a higher current during the first hour without my noticing, as it was not a concern at that point in time, tapering down in the latter stage, hour 3. It would be reasonable to assume the battery will accept all the current it can absorb at a given voltage, baring an internal short, so my observation during the Schneider's 1 hour EQ may merely be anxiety, if the EQ were allowed to continue for 3 hours it may well terminate with a lower current. Should this be the case, it may indicate the battery needs a longer time in EQ than the 1 hour fixed Schneider default, which seems short, all literature I've read indicates a longer cycle. All cells have ballanced SG at 1270, string charge/discharge currents close and individual monoblock voltages within 0.05V, but the battery is nearing end of life.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I would concur with that!
I always have more questions than answers. That's the nature of life. -
I also have the 1 hr Schneider EQ with my 80-600. The current drops as it gets further into the EQ or if after the 1st hr of EQ I program in a 10 minute absorb and another hour of EQ. After the 1st 15 minutes on the second EQ the current continues to drop.
I really with there was a way to program the Schneider to go for a longer (like 3 hour) EQ so I could terminate it manually when SGs evened out.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
-
WaterWheel said:I also have the 1 hr Schneider EQ with my 80-600. The current drops as it gets further into the EQ or if after the 1st hr of EQ I program in a 10 minute absorb and another hour of EQ. After the 1st 15 minutes on the second EQ the current continues to drop.
I really with there was a way to program the Schneider to go for a longer (like 3 hour) EQ so I could terminate it manually when SGs evened out.
Will try a second EQ next time to see if it in fact drops, I would agree with having the option to extend the 1 hour as useful, the engineers who developed it must have had their reasons, perhaps a cautionary one, like no auto EQ capabilities, just a reminder, which personally I think is better, strange things could happen if you are not there to monitor and they usually happen that way.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Flooded batteries that are otherwise is good condition, but seriously need an EQ will require considerably more current (into the battery), than will the same size/age battery that on needs a mild amount of EQing.
Older batteries that are in generally good condition, seem to have EQ currents that are higher on exiting EQ, than those which are young..
Like to watch the measured battery current (Shunt current) when the EQ is done, this can be an indicator of general battery health.
This is relative to batteries that have received a full charge preceding the EQ, and for Veq that is temperature compensated, and for Veq settings that are the same, when comparing Ieq ... in general.
It is certainly true, that just as in Absorption, the battery charge current depends upon the Vabs (or Veq), AND Acceptance of the battery. Increase the Vabs (or Veq), and the measured battery current will increase, and taper over a period of time.
Just my observations, FWIW, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
It might just be end of life drama, but if the battery is accepting 25 amps, I doubt it is getting fully charged. I don't know the size of the battery bank, but from your profile, it's between 200 and 460 ah. so 25 amps represents >5% charge rate. I think I get about a 20 ah into my @660 Ah battery at the beginning of equalizing and I've got a pretty bad cell in it.
I think Marc has already said, the charge controller really only increases the charging voltage to allow the current to flow into the battery. The current is regulated by what the battery will accept.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed