Help sizingsystem

usao
usao Registered Users Posts: 11 ✭✭
I need power at a remote site, off-grid.
What I need is 12v @ 1KW 24/365

This is approx 90A continuous.
I don't need an inverter, 12v DC only.
From what I understand about solar, I need to pull  90A * 24 hours = 2.1 KAh per day from batteries, and that number needs to be 50% of total battery  capacity, so total battery capacity should be around 4.5 KAh
In addition, I need to push 2.1 KAh into the batteries over a 5-8 hour period each day.
If I assume 5 hours, the the solar panels need to generate about 450 A.
I havent found a charge controller which does 450A yet. Looked at Morning Star and others, but they all seem to be in the 60-80A range.
Are my numbers wrong somewhere?

Comments

  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    Sketchy but in the ball park.
    You need multiple Charge Controllers. Most will be in the range you stated.  It is not good practice to push electronics steadily above ~80% of their rating max, strange smoke cab be released and other bad things happen... fire?...
    50% is the max you want to draw so iif this is every day you need a safety cushion as well.
    You also need a huge array(s)
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    usao said:
    I need power at a remote site, off-grid.
    What I need is 12v @ 1KW 24/365

    This is approx 90A continuous.
    I don't need an inverter, 12v DC only.
    From what I understand about solar, I need to pull  90A * 24 hours = 2.1 KAh per day from batteries, and that number needs to be 50% of total battery  capacity, so total battery capacity should be around 4.5 KAh
    In addition, I need to push 2.1 KAh into the batteries over a 5-8 hour period each day.
    If I assume 5 hours, the the solar panels need to generate about 450 A.
    I havent found a charge controller which does 450A yet. Looked at Morning Star and others, but they all seem to be in the 60-80A range.
    Are my numbers wrong somewhere?
    Regarding charge controllers,  see link.
    http://www.morningstarcorp.com/parallel-charging-using-multiple-controllers-separate-pv-arrays/
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • Horsefly
    Horsefly Registered Users Posts: 476 ✭✭✭✭
    edited March 2017 #4
    usao said:
    I need power at a remote site, off-grid.
    What I need is 12v @ 1KW 24/365

    This is approx 90A continuous.
    I don't need an inverter, 12v DC only.
    From what I understand about solar, I need to pull  90A * 24 hours = 2.1 KAh per day from batteries, and that number needs to be 50% of total battery  capacity, so total battery capacity should be around 4.5 KAh
    In addition, I need to push 2.1 KAh into the batteries over a 5-8 hour period each day.
    If I assume 5 hours, the the solar panels need to generate about 450 A.
    I havent found a charge controller which does 450A yet. Looked at Morning Star and others, but they all seem to be in the 60-80A range.
    Are my numbers wrong somewhere?
    I don't think your math is wrong. However, back in January you approached a similar but smaller problem and decided maybe it was too much (http://forum.solar-electric.com/discussion/comment/366513#Comment_366513 ).  I'm guessing that if that one was too big to justify, this one is even more so.

    Anyway. 4,500AH battery bank at 12V, will have to get recharged per a 12V bank rate, like at 14.4V or so. Assuming typical losses along the way (wiring derating, panel derating, charge controller derating), you probably need to assume about 70% efficiency getting to those batteries. So:

    4500AH * 14.4V / 0.70 * 0.10 (10% charging rate per hour) = ~9.2KW of panels. That's lots of panels. 

    You are right, that is too much to push through a single charge controller. You would need to split that array up into something like 10 separate charge controllers. 

    This big of a problem doesn't seem to be something anyone tries to solve with a 12V system. More likely a 48V system. I see you can't do that, but it makes the problem (e.g., number of charge controllers) at least 4x as big.

    This is all assuming you can cobble together a 4500AH 12V battery (yikes!). Needless to say, your continuous 90A draw would mean you were intentionally drawing down your batteries to 50% DoD every single day assuming there was nothing but bright sun outside. You'd need a pretty good backup generator for all those days that didn't have plenty of sun.

    I'm not a pro at this and I am generally keen to try and solve a problem, but... Your problem seems like one to walk away from and find a different approach.

    Steve
    Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case.
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    12V @ 90A 24/7 is a wrong number.   You need to consider a 48V @23A system, and then downconvert to 12V at the final usage point.
    You won't save any solar panels, but you will save on charge controller costs and copper costs.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • usao
    usao Registered Users Posts: 11 ✭✭
    Im still trying to figure a way to do this, perhaps on a smaller scale. I may shoot for a 500W, 250W or other and just run on a smaller scale.
    I figured that if I had the numbers for 1KW, then I could easily scale up/down and reach a number I could work with.
    I did find a 2V battery (http://www.rollsbattery.com/wp-content/uploads/batteries/2YS62P.pdf) which might work.
    Im a vit confused about how to get a 12V draw out of a 48V source though. Would I need to use an inverter to go to 220 then a PSU to get back down to 12V? Seems like a lot of loss inbetween.

  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    To get 12v for loads from a 48v system you would use a DC-DC converter, likely one that outputs constant 12v out from variable (eg) 40-65v input to allow for varying battery charging voltages.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭

    usao said:
    Im still trying to figure a way to do this, perhaps on a smaller scale. I may shoot for a 500W, 250W or other and just run on a smaller scale.
    I figured that if I had the numbers for 1KW, then I could easily scale up/down and reach a number I could work with.
    I did find a 2V battery (http://www.rollsbattery.com/wp-content/uploads/batteries/2YS62P.pdf) which might work.
    Im a vit confused about how to get a 12V draw out of a 48V source though. Would I need to use an inverter to go to 220 then a PSU to get back down to 12V? Seems like a lot of loss inbetween.

    Without defining the loads, it's near impossible for anyone to suggest a solution, it's all speculation, there are many ways things can be done, but without details ,suggestions are just shots in the dark, no offense implied.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • oil pan 4
    oil pan 4 Solar Expert Posts: 767 ✭✭✭✭
    The extreme aversion to saying what the loads are makes me think it's something illegal.

    Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.

    Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.

  • usao
    usao Registered Users Posts: 11 ✭✭
    oil pan 4 said:
    The extreme aversion to saying what the loads are makes me think it's something illegal.
    Not sure what you mean by "extreme aversion to saying what the loads are".
    Im looking for a way to keep bitcoin mining equipment running as the profitability goes down over time.
    Mining rigs use a lot of electricity and their revenue drops over time. Electric costs are a significant component which often renders rigs break-even or worse even after a few months, meaning I can no longer mine and am forced to turn off.
    If I can get something going which will allow me to keep them running for a much longer time their revenue generation lifetime can be greatly extended. Most mining rigs run on 12V. My smallest rig uses 40W and my largest rig uses 1KW. I have a total of 10KW currently running my garage. I have a 50A @ 208 circuit dedicated to my rigs.
    So, that is why im flexible on the loads as I have a variety of rigs I could use in this way.
    I already know the cost of the solar setup is way more than the revenue, thats not the point for me. Rathe having a solar setup of some sort is (in my mind) always a useful thing to have for other purposes, for example, im considering a chevy spark and have looked at the tesla powerwall also.
  • Photowhit
    Photowhit Solar Expert Posts: 6,006 ✭✭✭✭✭
    usao said:
    Im looking for a way to keep bitcoin mining equipment running as the profitability goes down over time.
    So if we can say with a certainty that the cost of solar will be higher per Kwh than the cost of grid then your hunt would be over?
    This will pretty much always be the case.

    Might hunt for lowest cost of electric in the US, some places charge less for higher usage... If you were to try to do cheapest solar and you didn't have to store energy and just use grid tied energy to offset higher prime daylight energy times...

    Not sure how you are doing bitcoin mining without internet, I thought the loading and bundling of transaction would require pretty good internet service. ...but it's not my end of the pool.
    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
    - Assorted other systems, pieces and to many panels in the closet to not do more projects.
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    @usao said  Electric costs are a significant component which often renders rigs break-even or worse even after a few months, meaning I can no longer mine and am forced to turn off.

    I already know the cost of the solar setup is way more than the revenue, thats not the point for me. 
    Sorry I'm a little confused by the two statements made, they seem contradict one another.
    As @Photowhit suggested, grid tied would be the only economic solution.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Assuming grid tied would run about $2-3/watt and grid power at 0.25/kwh (pretty high), breakeven is 2000/.25=8000hrs. At 4hrs/day that's about 6 years ignoring cost of funds and depreciation. To get a real number you would want to find out how the local utility handles grid-tie buy/sell rates and billing. IMHO, there's also a risk that utilities may strand investment in grid-tie if it gets big enough to start causing significant network issues.

    If you really are remote and off-grid like you said in your first post, initial cost, depreciation, and end to end system power losses will all be higher. If the numbers don't work well with grid power, there's no way they work off-grid.

    If I was going to run a server farm commercially, I'd locate it somewhere with cheaper power and climate for lower cooling costs (eg Manitoba in Canada).
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    An interesting article about bitcoin mining and cost of power:

    https://www.washingtonpost.com/news/worldviews/wp/2017/03/10/bitcoin-mining-is-big-business-in-venezuela-but-the-government-wants-to-shut-it-down/

    CARACAS, Venezuela — Venezuela has become widely known as an economic basket case in recent years. But with its cheap electricity and volatile national currency, the country has at least one competitive advantage: It’s a good place to make the digital cash known as bitcoin.

    Bitcoins are increasingly accepted online for buying real-world goods and services. And, unlike the Venezuelan bolivar, the virtual currency has been going up in value.

    Making bitcoins is known as “mining,” but it requires a powerful computer instead of a pick and shovel. Those computers produce bitcoins by creating elaborate algorithms, but they also suck up a lot of electricity. In many countries, the cost of running a “mining terminal” can run higher than the value of the actual bitcoins.

    That’s not the case in cash-poor, oil-rich Venezuela, where state-subsidized electricity is so cheap it’s virtually free. But Venezuela’s government isn’t pleased. It’s cracking down on bitcoin mining, even though the country has no laws on the books outlawing the currency or its manufacture.

    In November, Venezuela’s secret police raided the house of two brothers in Caracas and found more than 90 mining terminals. The agents demanded $1,000 in bribes for each machine, according to the brothers, who spoke on the condition of anonymity because they fear arrest. The brothers said they paid the bribes to stay in business...

    And a history about a major Bitcoin exchange... Basically the rise and fall of MtGox:

    https://en.wikipedia.org/wiki/Mt._Gox

    -Bill

    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • usao
    usao Registered Users Posts: 11 ✭✭
    mcgivor said:
    @usao said  Electric costs are a significant component which often renders rigs break-even or worse even after a few months, meaning I can no longer mine and am forced to turn off.

    I already know the cost of the solar setup is way more than the revenue, thats not the point for me. 
    Sorry I'm a little confused by the two statements made, they seem contradict one another.
    As @Photowhit suggested, grid tied would be the only economic solution.
    There's no right answer here. I have a lot of fun with bitcoin and at the same time I really like the idea of off-grid solar.
    I know the 2 ideas are somewhat contradictory in that bitcoin mining is not environmentally conscious yet at the same time I am into environmentally conscious activities such as setting up recycling for businesses, composting and growing my own veggies and peppers and other activities.
    The other reason I said "remote" was just to re-enforce the idea that I wanted to use 12V only without the inverter in between the batteries and the mining rigs. In my mind it was simply short hand for saying I wanted stand-alone setup, but in the end I had to give the full blown explanation anyhow, so im sorry for that. I really didn't expect it to become a big issue, and I guess that's my bad.
    After all that said, ive decided to start small. Ive ordered a morning star SS-20L-12V, and will get batteries this week from a local supplier. Im going to start by verifying that I can run one of my older Gridseed mining rigs using the batteries through the load ports on the Morningstar for 24 hours. Thats a total of 2.4KWh/day, and I will recharge using a battery charger during off-peak hours. If that works, ill start shopping for some panels to generate 2.4KW in 5-8 hours (I live in AZ so get lotsof sun).
    Again, sorry for all the confusion, I was trying to keep it short and simple Q&A just to validate my ideas, but that didnt work.
    Also, I know the investment outpaces the revenue, but I also figured at some point I could start using the solar system for other purposes over the coming years.
  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Good plan... start small and get some real world experience with solar and batteries. I'm glad I did - avoided a lot of mistakes that way.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    No problem... We try to look at the needs in full. Just designing a "cost effective" solar power system powering a black box does not always work out well. Load calculations and conservation are a very important part of a successful solar design.

    Plus we are always curious about what other people are using solar power for. B)

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset