Photovoltaic Conundrum
EEGG
Registered Users Posts: 16 ✭✭
This is a 6 kWh photovoltaic system with 24 X 250w 60 cell Yingli paneles, connected 8 in three string to a central inverter Fronius IG 5100. The inverter is connected to the grid 240/120 V split phase, grounded.
The panels have a cyclic power production. When they reach 5.9 amps and 232v they drop quickly to 1.5/2.0 amps and 242v and climb slowly. Few days the system is fine.
I disconnect each string without any effect. The ground are fine. Connections are fine. No volts between Neutro and Ground. No visible archs or defects on the panels. Polarity is fine. The problem is not present without load in the panels but this observation is only in a short period of time. The inverter is fine, I exchange it with a new one and the problem persist.
I will appreciate any assistance
Regards.
Tagged:
Comments
-
Voltage drop from heat? panels are around 30 vmp? so around 240 volts... What are your NOCT values for the panels and where are you located/what have temps been like?Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
I suspect you also need some 'head room' like off grid MPPT charge controllers, what does Fronius recommend incoming voltage for output at 240V?
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
MPP 150 - 400 V D.C., measurements take it - local temp 86F.
-
-
Photowhit said:I suspect you also need some 'head room' like off grid MPPT charge controllers, what does Fronius recommend incoming voltage for output at 240V?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
-
No the DC Imput in in range. The problem is the fluctuation in the current from the panels.
-
Looks like input voltage is too low, perhaps 2 strings of 12 panels would be better, at around 360V.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Sounds like a MPPT circuit not working right, trying to seek the max setpoint.
Use a clamp - on DC ampmeter to measure each string
Insure each string meets the Max & Min voltages for the inverter input
Something is making the MPPT hunt in a strange manner.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
-
2 strings exceeds D.C. Voltage rating for minimum Temperature
-
The amps in each string is the same, an if I disconnect one by one the problem persist.
-
EEGG said:No the DC Imput in in range. The problem is the fluctuation in the current from the panels.
inverter nominal input 270V, max 500 no load.
Am I missing something?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
The fronius system configuration tool put the actual configuration as optimal.
217.6 V explain the fluctuation in the panel amps output? I don't know -
Suggest try 2×11 panels as a test, see if that solves the problem.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Well, it's interesting, It is an inverter and not a charge controller, but I thought most liked to have voltage above the AC voltage, Fronius says;
"Operating DC voltage range 150 – 450 V "
So that shouldn't be a problem since output is known to be higher. So I would guess we are on the wrong track.
You say "but this observation is only in a short period of time. " and that it's cyclical, but then say in a few days it's fine. Is there a difference of when you can make the observation? a change in the weather? Do you see a serious impact on your daily production?Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Well, it's interesting, It is an inverter and not a charge controller, but I thought most liked to have voltage above the AC voltage, Fronius says;
"Operating DC voltage range 150 – 450 V "
So that shouldn't be a problem since output is known to be higher. So I would guess we are on the wrong track.
You say "but this observation is only in a short period of time. " and that it's cyclical, but then say in a few days it's fine. Is there a difference of when you can make the observation? a change in the weather? Do you see a serious impact on your daily production?
Just thoughts.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
This system is side by side with a similar system, the same capacity and solar panels but with microinverters enphase m215. Some days they produce almost the same +/- 5%. But most of the time the difference is 15 - 20%. They are connected to the same grid and in the same conditions. The inverter is not the problem in laboratory conditions works fine and I exchanged for a new one, the problem persist. The inversor is following the panel feeding the amps change in a cyclical manner. So I check disconnecting each string to insolarte the problem but it keep doing the same no matter the string I disconnect so this is a real conundrum and that's the reason I need help. With out load they are in specs and fine but I keep the readings for half an hour, then when I reconnect the problem reappear.
-
I don't think the inverter is hunting the AC grid, is following the D.C. Imput
-
EEGG said:This system is side by side with a similar system, the same capacity and solar panels but with microinverters enphase m215. Some days they produce almost the same +/- 5%. But most of the time the difference is 15 - 20%. They are connected to the same grid and in the same conditions. The inverter is not the problem in laboratory conditions works fine and I exchanged for a new one, the problem persist. The inversor is following the panel feeding the amps change in a cyclical manner. So I check disconnecting each string to insolarte the problem but it keep doing the same no matter the string I disconnect so this is a real conundrum and that's the reason I need help. With out load they are in specs and fine but I keep the readings for half an hour, then when I reconnect the problem reappear.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Another question, are there clouds passing? Rational, if a shadow passed over one panel, the whole string is affected, with micro inverters, only one would be therefore higher overall production. Just covering all bases.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
No clouds. The test I perform was to desconect one sting at a time and switch it on, in all the cases the problem persisted.
-
So if is a faulty panel has to be at least one in all the 3 strings
-
Unlikely to be one in each string, so must be something common to all. If it's not too cold perhaps try 2 strings, something about the nominal voltage being 270V bothers me, I understand the string calculator says it should work. If you were to input the current temperature as the low and it allows 2 strings there should be no harm in trying and not too difficult to perform.
In the video, the output was at around 2000 watts, when producing more, dose the problem still exist?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Perhaps there is a wiring error in every string, and your voltage is too low. Maybe at the far end of the array where the Skip Wiring reverses ? Have you MEASURED the voltage of the strings ?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
The Fronius calculator values for thr panels you have, differ from the Yingli data sheet, thought you should know.
Read the Web page, link below, it speaks about low input and other relevant things, especially the racking correction factors section, the information regarding operating at the low end of the inverters voltage window may provide some insight, my belief is this is the problem/conundrum lies.
https://www.homepower.com/articles/solar-electricity/design-installation/string-theory
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
If the array voltage drops below the minimum value due to elevated temperatures, inverter or controller power production will stop until the array cools and the voltage rises. So low DC voltage will STOP the inverter?
I am familiar with the concept "the inverters hunt the AC grid" but Do the panels hunt the inverter. (Synchronize) -
The inverter MPPT will "hunt" for the current/voltage that produces max watts. It can adjust for changing voltage on each sweep to some degree.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I just change the configuration to 2X 12 and the reading are stable in 315 v an 13.5 amp no fluctuation.
maybe the Fronius calculator is wrong.
thank you mcgivor and Mike.
i will keep you informed, regards.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed