Battery pulling down panel voltage???
1.) 2 100 watt panels wired in parallel 25 feet from charge controller using 10 AWG wire.
2.) Morningstar TriStar PWM 60 set for 12 (14.6) volts, 4 feet from batteries using 2 AWG cable.
3.) 2 new DEKA group 31 flooded batteries fully charged before use (210 AH total).
Hope that's enough info for this question.
I discharged my batteries to around 70 percent (1.225 on hydrometer@12.3 volts) and noticed my charge controller only putting out about a volt above my battery voltage (about 13.3 volts). The Amperage was good though around 10.5 amps.
As the batteries were charging (No, there was no load during charging) I did notice the voltage creep up accordingly as they charged. But those batteries were being charged all day up to 13.5 volts (According to my trimetric meter and display on the Morningstar). But when I checked with the hydrometer nothing changed much, still hovering around 1.225.
That's below the 14.6 charge setpoint I put in. When the batteries were charged it went through the PWM mode then into float.
I did shut the system down and checked the open circuit voltage with no load and got 22 something volts on each panel.
My question is, is it normal for a discharged battery to pull the panel voltage down below my setpoint of 14.6 but leave the amps full throttle? I am new to this and this is my first run after much research
If that is normal, that tells me 200 watts of solar power is not nearly enough to charge a 210 AH battery bank. Am I right?
Will more panels bring the voltage up to charge faster?
I tried most of the day yesterday to find an answer and couldn't, so now I'm here on a forum.
Edit: There was no shade on the panels what so ever. Also I live near Detroit Michigan.
Comments
-
Virtuousdesires said:What I am working with (For now):
1.) 2 100 watt panels wired in parallel 25 feet from charge controller using 10 AWG wire.
2.) Morningstar TriStar PWM 60 set for 12 (14.6) volts, 4 feet from batteries using 2 AWG cable.
3.) 2 new DEKA group 31 flooded batteries fully charged before use (210 AH total).
...........
My question is, 1) is it normal for a discharged battery to pull the panel voltage down below my setpoint of 14.6 but leave the amps full throttle? I am new to this and this is my first run after much research
If that is normal, that tells me 200 watts of solar power is not nearly enough to charge a 210 AH battery bank. 2) Am I right? 3)Will more panels bring the voltage up to charge faster?
When a battery is well depleted it will take a long time for the amps to get high enough that the volts starts to rise. When there is enough internal resistance to the Amps available the volts will start to rise and you will enter Absorb phase. This is a lesson in what you get without enough panels... it may take several days for your batteries get filled... You could figure out the number of watts or Ahrs of power you have used and then use 4 hrs of good sunshine per day to estimate how long the recharge will take... But in the mean time go out and find 2 more identical panels.... to add to the setup.hth
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
westbranch said:Virtuousdesires said:What I am working with (For now):
1.) 2 100 watt panels wired in parallel 25 feet from charge controller using 10 AWG wire.
2.) Morningstar TriStar PWM 60 set for 12 (14.6) volts, 4 feet from batteries using 2 AWG cable.
3.) 2 new DEKA group 31 flooded batteries fully charged before use (210 AH total).
...........
My question is, 1) is it normal for a discharged battery to pull the panel voltage down below my setpoint of 14.6 but leave the amps full throttle? I am new to this and this is my first run after much research
If that is normal, that tells me 200 watts of solar power is not nearly enough to charge a 210 AH battery bank. 2) Am I right? 3)Will more panels bring the voltage up to charge faster?
When a battery is well depleted it will take a long time for the amps to get high enough that the volts starts to rise. When there is enough internal resistance to the Amps available the volts will start to rise and you will enter Absorb phase. This is a lesson in what you get without enough panels... it may take several days for your batteries get filled... You could figure out the number of watts or Ahrs of power you ahve used and then use 4 hrs of good sunshine per day to estimate how long the recharge will take... But in the mean time go out and find 2 more identical panels.... to add to the setup.hth
Thanks so much for your reply!
Morning star TS-60 PWM (With display, RTS), 2 DEKA G31 flooded batteries (210 AH), Aims 1200 watt Pure sine inverter, 2 100 watt panels, Bogart Engineering 2030 RV trimetric meter. -
Virtuousdesires said:westbranch said:Virtuousdesires said:What I am working with (For now):
1.) 2 100 watt panels wired in parallel 25 feet from charge controller using 10 AWG wire.
2.) Morningstar TriStar PWM 60 set for 12 (14.6) volts, 4 feet from batteries using 2 AWG cable.
3.) 2 new DEKA group 31 flooded batteries fully charged before use (210 AH total).
...........
My question is, 1) is it normal for a discharged battery to pull the panel voltage down below my setpoint of 14.6 but leave the amps full throttle? I am new to this and this is my first run after much research
If that is normal, that tells me 200 watts of solar power is not nearly enough to charge a 210 AH battery bank. 2) Am I right? 3)Will more panels bring the voltage up to charge faster?
When a battery is well depleted it will take a long time for the amps to get high enough that the volts starts to rise. When there is enough internal resistance to the Amps available the volts will start to rise and you will enter Absorb phase. This is a lesson in what you get without enough panels... it may take several days for your batteries get filled... You could figure out the number of watts or Ahrs of power you ahve used and then use 4 hrs of good sunshine per day to estimate how long the recharge will take... But in the mean time go out and find 2 more identical panels.... to add to the setup.hth
Thanks so much for your reply!
The better way to check the state of charge is after the battery been sitting for a few hour without charging or discharging the battery. This way the surface charge on the plate is dissipated and you will see a truer state of charge.
200 watt of solar panels, will still give you enough power for LED lighting at night or in emergencies and power for other small electrical items/things as long as you watch your power usage a bit.
-
Johann said:Virtuousdesires said:westbranch said:Virtuousdesires said:What I am working with (For now):
1.) 2 100 watt panels wired in parallel 25 feet from charge controller using 10 AWG wire.
2.) Morningstar TriStar PWM 60 set for 12 (14.6) volts, 4 feet from batteries using 2 AWG cable.
3.) 2 new DEKA group 31 flooded batteries fully charged before use (210 AH total).
...........
My question is, 1) is it normal for a discharged battery to pull the panel voltage down below my setpoint of 14.6 but leave the amps full throttle? I am new to this and this is my first run after much research
If that is normal, that tells me 200 watts of solar power is not nearly enough to charge a 210 AH battery bank. 2) Am I right? 3)Will more panels bring the voltage up to charge faster?
When a battery is well depleted it will take a long time for the amps to get high enough that the volts starts to rise. When there is enough internal resistance to the Amps available the volts will start to rise and you will enter Absorb phase. This is a lesson in what you get without enough panels... it may take several days for your batteries get filled... You could figure out the number of watts or Ahrs of power you ahve used and then use 4 hrs of good sunshine per day to estimate how long the recharge will take... But in the mean time go out and find 2 more identical panels.... to add to the setup.hth
Thanks so much for your reply!
The better way to check the state of charge is after the battery been sitting for a few hour without charging or discharging the battery. This way the surface charge on the plate is dissipated and you will see a truer state of charge.
200 watt of solar panels, will still give you enough power for LED lighting at night or in emergencies and power for other small electrical items/things as long as you watch your power usage a bit.
As far as the batteries sitting for a bit after a charge, does the apply to the Specific gravity check as well? I know a voltmeter isn't accurate after a charge.
As far as watching my usage, I bought a 2030 RV trimetric meter from Bogart Engineering, love that little gadget. I think I have to further tweak the settings on it though.Morning star TS-60 PWM (With display, RTS), 2 DEKA G31 flooded batteries (210 AH), Aims 1200 watt Pure sine inverter, 2 100 watt panels, Bogart Engineering 2030 RV trimetric meter. -
You don't need to let batteries rest much for SG. I like to wait for them to stop bubbling before opening caps just to avoid splashing though.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
You don't need to let batteries rest much for SG. I like to wait for them to stop bubbling before opening caps just to avoid splashing though.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Temp compensation would be appropriate would be appropriate if battery is warm/cool for whatever reason, like if ambient is 40C+Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Temp compensation would be appropriate would be appropriate if battery is warm/cool for whatever reason, like if ambient is 40C+1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Could be. Mine are usually quite cool and charging usually just gets them to around room temp.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Yes, depending on location, I'm tropical, so temperatures are generally higher to start with and ambient temperature plays in a negative effect for me, location is a factor.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
PWM controllers connect the PV (a limited current source) directly to the batteries (a nearly infinite sink) so when the batteries are low, the panels will read the same as the battery voltage (the controller is now a direct connection) So battery voltage IS expected to be seen on PV side of things, when batteries are charging at max.
A MPPT controller is "smarter" and works like a transformer, and harvests the voltage delta between battery voltage and panel voltage and is more efficient.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:PWM controllers connect the PV (a limited current source) directly to the batteries (a nearly infinite sink) so when the batteries are low, the panels will read the same as the battery voltage (the controller is now a direct connection) So battery voltage IS expected to be seen on PV side of things, when batteries are charging at max.
A MPPT controller is "smarter" and works like a transformer, and harvests the voltage delta between battery voltage and panel voltage and is more efficient.Morning star TS-60 PWM (With display, RTS), 2 DEKA G31 flooded batteries (210 AH), Aims 1200 watt Pure sine inverter, 2 100 watt panels, Bogart Engineering 2030 RV trimetric meter. -
Considering you can get a thousand watts in 3 to 4 panels @ approx. 50 cents a watt why would you want to use 10 expensive 12 volt panels? You have Way less connections, no fusing or combiner box to buy. The beauty of an MPPT controller is you can save money with the larger, cheaper panels.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
littleharbor2 said:Considering you can get a thousand watts in 3 to 4 panels @ approx. 50 cents a watt why would you want to use 10 expensive 12 volt panels? You have Way less connections, no fusing or combiner box to buy. The beauty of an MPPT controller is you can save money with the larger, cheaper panels.
Also, I did actually plan on buying a combiner box with breakers. I do know when I install the system I would like it to be nec compliant to pass inspection. I don't even know if I should try to pull a permit or not. Probably get fined if I didn't...Morning star TS-60 PWM (With display, RTS), 2 DEKA G31 flooded batteries (210 AH), Aims 1200 watt Pure sine inverter, 2 100 watt panels, Bogart Engineering 2030 RV trimetric meter. -
littleharbor2 said:Considering you can get a thousand watts in 3 to 4 panels @ approx. 50 cents a watt why would you want to use 10 expensive 12 volt panels? You have Way less connections, no fusing or combiner box to buy. The beauty of an MPPT controller is you can save money with the larger, cheaper panels.Morning star TS-60 PWM (With display, RTS), 2 DEKA G31 flooded batteries (210 AH), Aims 1200 watt Pure sine inverter, 2 100 watt panels, Bogart Engineering 2030 RV trimetric meter.
-
Virtuous..,
Here is some info on the operation of MPPT CCs:
https://www.solar-electric.com/mppt-solar-charge-controllers.html/Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Virtuousdesires said:littleharbor2 said:Considering you can get a thousand watts in 3 to 4 panels @ approx. 50 cents a watt why would you want to use 10 expensive 12 volt panels? You have Way less connections, no fusing or combiner box to buy. The beauty of an MPPT controller is you can save money with the larger, cheaper panels.
This isn't something I have shared here for obvious reasons but I sell solar panels and have new 255 to 310 watt panels for 49 cents a watt. Look on your local craigslist. Buy local and avoid shipping altogether.There seems to be a shipload of people selling these days in this price range.2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
> @Vic said:
> Virtuous..,
>
> Here is some info on the operation of MPPT CCs:
> https://www.solar-electric.com/mppt-solar-charge-controllers.html/
>
> Vic
So just for example, my 2 100 watt panels was putting out 10.5 amps at 13.5 volts (Around 150 watts according to the display). If I wired the two panels in series to make 24 volts and used an mppt charge controller set to 12 volts (14.6), what might those numbers look like? More voltage and amps going into the battery? Seems like how that works.Morning star TS-60 PWM (With display, RTS), 2 DEKA G31 flooded batteries (210 AH), Aims 1200 watt Pure sine inverter, 2 100 watt panels, Bogart Engineering 2030 RV trimetric meter. -
@Virtuousdesires
There are a couple of advantages to MPPT controllers, but neither may apply in your application:
1. You can use higher voltage panels, which tend to be bigger and more costly to ship, but which are produced and shipped in high volume, so MAY be more cost effective locally to you.
2. You can wire panels in higher voltage strings, which is an advantage if panels are a long distance from controller. Higher voltage with lower amperage is the same wattage but allows the use of smaller wire for less wire loss.
In a camper/rv application you won't be going far from panel to controller, so if you have to use a bigger wire to minimize wire losses it probably isn't a big deal. That may take care of the second advantage. The first advantage may or may not apply depending on what's available locally.
Using your 500w example - a 100w 12v nominal panel will be around 18Vmp and 100w/18v=5ish amps.
You could wire in parallel, which would be 5*5a=25a@18v=450w. You could use a PWM controller for this, but wouldn't want to go far to minimize wire losses.
You could wire in series, which would be 5*18v=90v@5a=450w. You would use a MPPT controller for this to reduce the ~90v to charging voltage.
Either way, you get 450w +/- out of the panels.
It's not a question of what's "better". It's just what works for the application.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Except your batteries will pull that Paralleled 18 volts down to just above their voltage so that 18 volts goes down to say 12.3 volts while charging and will rise up to say 14.6 when near full. Problem is that voltage differential is lost with a PWM controller. With a MPPT controller it takes that high voltage and steps it down to your batteries desired voltage, (while the amperage rises in unison), without losing any of the differential. You will lose potential power with a PWM controller and your batteries wont see that full 500 , or whatever watts.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Virtuousdesires said:So just for example, my 2 100 watt panels was putting out 10.5 amps at 13.5 volts (Around 150 watts according to the display). If I wired the two panels in series to make 24 volts and used an mppt charge controller set to 12 volts (14.6), what might those numbers look like? More voltage and amps going into the battery? Seems like how that works.
Where are you located?
SolarBLVD.com and SunElec.com are wholesalers, but you can make poor buying choices as they aren't customer service oriented, but have cheapest prices in general, I'll add another if you wanted pallet quantities. Stay away from Thin film panels! If asking for a quote including shipping, be sure to give them all pertinent information, or you may be ignored. With shipping you want to list address, if it's a home or business, if someone will be there, if a lift gate is needed or loading dock...
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
So just for example, my 2 100 watt panels was putting out 10.5 amps at 13.5 volts (Around 150 watts according to the display). If I wired the two panels in series to make 24 volts and used an mppt charge controller set to 12 volts (14.6), what might those numbers look like? More voltage and amps going into the battery? Seems like how that works.Can't tell. The PWM has corrupted the the PV potential output. But taking a long shot, you have 200W @ 18V = 11A Which is pretty close to the 10.5A you currently measure. So, using poisoned numbers, and guessing wildly, you gain at least 1/2 amp, which is about full power from the panels. Exactly what MPPT is supposed to do. Your PWM numbers are surprisingly good.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
since the next step, if he stays with PWM/parallel wired panels, is he could use 3 panels. He will have to go with 4 panels if he wants to go 24V with 2 panels in series with 2 parallel strings... the benefit is that he will get less line loss, small as it will be, with the same, say 10 ga. wire or 4 in series (48V) and get even less loss... using the same wire to the CC. That is another benefit of MPPT, not to mention there should be more Amps into the depleted bank...
Low production days are another potential charging time not achievable if using an all parallel setup.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
> @mike95490 said:
> So just for example, my 2 100 watt panels was putting out 10.5 amps at
> 13.5 volts (Around 150 watts according to the display). If I wired the
> two panels in series to make 24 volts and used an mppt charge controller
> set to 12 volts (14.6), what might those numbers look like? More
> voltage and amps going into the battery? Seems like how that works.
>
>
> Can't tell. The PWM has corrupted the the PV potential output. But taking a long shot, you have 200W @ 18V = 11A Which is pretty close to the 10.5A you currently measure. So, using poisoned numbers, and guessing wildly, you gain at least 1/2 amp, which is about full power from the panels. Exactly what MPPT is supposed to do. Your PWM numbers are surprisingly good.
Just taking the advice of a former RV blogger. Keep the controller close to the batteries and use big enough cable. I hope Sunday is sunny so I can run a voltage drop test from the panels to the controller. I already did this but didn't think to test it under load. Open circuit was just fine. From what I am gathering thus far, it appears that the voltage will drop regardless of cable size because that's how a battery does it (From what I understand from folks here and emailing a blogger).Morning star TS-60 PWM (With display, RTS), 2 DEKA G31 flooded batteries (210 AH), Aims 1200 watt Pure sine inverter, 2 100 watt panels, Bogart Engineering 2030 RV trimetric meter. -
The voltage will drop to battery voltage during charging, which is normal. Voltage drop in the cable depends on current (amps). Higher current = more voltage drop on a given size of wire. You can estimate the wire losses using a table like this:
https://www.solar-electric.com/wire-loss-tables.html/
Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed