Is there such thing as a inverter/charge controller that can have these features?
Is there something out in the market than can do all of the following?
1. Accept solar panel input (meaning you hook your solar panel to it and run on MPPT to charge your battery bank)
2. Input 24/48 volt battery bank and it invert power
3. Connected to the GRID to use power and pass grid as grid support mode BUT DOES NOT FEED THE GRID. But it can pass power through from the grid so it can sustain bigger load.
4. If battery is low charge the battery using the grid
5. Split phase (for US use)
I know hybrid inveter such as the Outback Radian and Conext SW can do all the thing, except it is not a MPPT charge controller, meaning it doesn't take solar input direct.
Thank you.
Comments
-
Victron makes some "Easy Solar" models that do what you want with out the split phase. Might see if they have or are developing one for the US market. I they make some 120v charger/inverters and they can be configured in a split phase (they likely have a single unit, but I'm not that familiar with them.) Maybe this will help...Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
There seem to be plenty of these for other than USA 120/240 Vac.
http://www.ebay.com/itm/Hybrid-Solar-Inverter-SP5000Brilliant-Plus-5KVA-4000W-Built-in-3MPPT-charger180A-/162208413445?hash=item25c45ff705:g:v6EAAOSwM4xXakTF
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Unfortunately, a split phase would be a must.. .since I have both 120/220 that I want to run on.
-
Any particular reason you don't want to use a separate charge controller?I know hybrid inveter such as the Outback Radian and Conext SW can do all the thing, except it is not a MPPT charge controller, meaning it doesn't take solar input direct.
-
bill von novak said:
Any particular reason you don't want to use a separate charge controller?I know hybrid inveter such as the Outback Radian and Conext SW can do all the thing, except it is not a MPPT charge controller, meaning it doesn't take solar input direct.
1. Cost saving, you wouldn't need all the extra box, breaker, fuses... ect.
2. The monitoring... since different brand of charge controller and inverter can not talk to each other... it would be hard to monitor both...
3. Cleaner install....
-
There is always the MidNite Solar B17 Inverter/Charger/CC.
This is still in development, and will probably be available late this year. It will not be inexpensive, as it is really a high-end, scalable product line.
FYI, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Vic said:
There is always the MidNite Solar B17 Inverter/Charger/CC.
This is still in development, and will probably be available late this year. It will not be inexpensive, as it is really a high-end, scalable product line.
FYI, Vic
Also, what's inexpensive? To some people 5,000 is inexpensive. But to me, 5k take a long time to balance out the cost.
-
Hi jimmyaz,
Yea, these will probably represent a very good value, but I did use a double-negative, saying, "they will NOT be inexpensive".
They should have every capability -- Grid-interactive, off-grid, etc.
Yes, they are very modular, so one can add what is needed at the beginning, and add more capability later. And the amount of ability to add additional modules later, will probably come in several sizes, etc.
BUT, this product line will be in the same price range as similar-sized top-notch inverter/chargers in the market now, like the Outback, Schneider Conext, etc, and the ability to increase power levels at a later time, may well add some premium (aka, a bit more cost) in the initial configuration, especially if the initial system is a bit on the smallish size.
Just thought I would throw this out there ...
Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
jimmyaz said:
1. Cost saving, you wouldn't need all the extra box, breaker, fuses... ect.
2. The monitoring... since different brand of charge controller and inverter can not talk to each other... it would be hard to monitor both...
3. Cleaner install....
-
I did not think the Midnite unit would handle different input voltages?
The only system that I could think of that would handle different input voltages was the Heart Transverter, it will do PV input but will only do battery banks from12-36 volts... and won't do split phase, to my knowledge.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Photowhit said:I did not think the Midnite unit would handle different input voltages?
-
bill von novak said:Photowhit said:I did not think the Midnite unit would handle different input voltages?
Inverter input... We were discussing the new Midnite inverter system.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Darn... I am now facing the decision to wait for the B17 or get the Conext SW set up...
If I only I know the pricing of the B17, would be much easier....
-
Also add Outback Skybox. You going to have to wait a bit longer. The Conext line for advanced batteries should have pricing at the end of February."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Dave Angelini said:Also add Outback Skybox. You going to have to wait a bit longer. The Conext line for advanced batteries should have pricing at the end of February.
Also, does anyone know if the current Conext 4048, what's the power rating for the bypass? I see on the data sheet it said 30amps, but I call Conext last week and the guy told me 60amps. Is it 30amps per phase total 60amps?
thanks all
-
The CSW is 30 amps either for the NA split phase model or the rest of the world. The XW+ is 60 amps.
There is some info in my thread here. The pricing info is really for the batteries as the "bridge is not scheduled until 2nd half of 2017.
http://forum.solar-electric.com/discussion/351297/conext-bridge-for-xw-li-ions-from-lg-and-hoppecke-announced-for-2nd-half-2017#latest
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Dave Angelini said:The CSW is 30 amps either for the NA split phase model or the rest of the world. The XW+ is 60 amps.
There is some info in my thread here. The pricing info is really for the batteries as the "bridge is not scheduled until 2nd half of 2017.
http://forum.solar-electric.com/discussion/351297/conext-bridge-for-xw-li-ions-from-lg-and-hoppecke-announced-for-2nd-half-2017#latest
-
If you do some reading on the subject you will find that most inverter/chargers are rated at the AC amps in/out.
It is the transfer of power. I also think you are confusing the fact that when a panel is sized, there is room for more circuit protection than the panel is rated for as by "code" it is assumed that you will not run everything at once. If you did, the main circuit breaker in the panel would trip. The Inverter is only going to supply it's rated power + the internal battery charger. In bypass mode a CSW can pass 30A @ 240vac."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Dave Angelini said:If you do some reading on the subject you will find that most inverter/chargers are rated at the AC amps in/out.
It is the transfer of power. I also think you are confusing the fact that when a panel is sized, there is room for more circuit protection than the panel is rated for as by "code" it is assumed that you will not run everything at once. If you did, the main circuit breaker in the panel would trip. The Inverter is only going to supply it's rated power + the internal battery charger. In bypass mode a CSW can pass 30A @ 240vac.
Now I have dout that my 3tons AC condenser could start with just the 30amps... On theory it should, because currently on my main panel a 30amps twin breaker is installed. But I am worry that, if I connect my kitchen line in and possibly if the microwave is running, then it probably isn't going to be enough .
Thanks Dave for answering all my dumb question.
-
A CSW is 30 amps in max. The output can be from the inverter or the grid/generator but not both. There is also self consumption software to use the solar only. The CSW can't sell power like the XW+ can. The CSW can run from 120 or 240 grid/gen which is nice for some as the XW+ is only 240 in from grid/gen.
I have a couple XW's that have never had any AC input
There is an internal 30A dual pole breaker in the CSW. But you do need to protect the wiring from your main panel to the CSW so yes another breaker.
You can add a second CSW to increase the amperage or buy the XW+ which is 60A."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Dave Angelini said:A CSW is 30 amps in max. The output can be from the inverter or the grid/generator but not both.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed