Run PV wiring on Power Poles

Question for the group here. I'm looking at doing a large new solar field on top of the hill behind my cabin (much better solar exposure).  It's ~150' from the top of the hill down to my cabin.  The only problem is that it is very steep (too steep for trenching equipment), and the hill is full of granite, so trenching is not an option.  I'm wondering if running the 2-3 PV strings through the air would work - via (2) power poles.  The hill is full of Juniper trees, but none over 30-40', so running the wire over 50' from the tops of the two poles should be free from any obstructions.  Any drawbacks to this?  Does Code allow for something like this?

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,431 admin
    Do you have lightning in the area?

    Otherwise, need voltage/current of array (panel configuration), charge controller, and battery bank voltage (to figure out wire gauge).

    Figure out copper vs aluminum vs MPPT low voltage (100 Vmp max) or high voltage (~400 volts max Vmp) combinations and trade-offs.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Photowhit
    Photowhit Solar Expert Posts: 6,002 ✭✭✭✭✭
    mjp24coho said:
     Does Code allow for something like this?
    Do you have codes to worry about where you are?
    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
    - Assorted other systems, pieces and to many panels in the closet to not do more projects.
  • mjp24coho
    mjp24coho Solar Expert Posts: 104 ✭✭✭
    I don't really have code to worry about (remote off-grid).  However, I'm looking at this for a possible expansion where I would be building a large cabin/home on my property.  If I do it, I'll likely want to make sure I'm code-compliant so that I can get all the necessary property insurance.  The array would be quite large - (60) 265W panels (hence the reason for placing it on the hilltop, where the solar production is greatest and it's out of sight.  I would likely use (5) Midnite Classics (each Classic would have 3 strings with 4 30V panels per string) with a 48V battery bank.  I would use 4 AWG wiring from the combiner to the charge controller (assume 200' one-way).  Lightning is a moderate concern in the area.
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    If lightning is a likely, you want to robustly ground your array frame, so it takes the brunt of the hit.  You will loose some panels (likely the end panels of the top row, and bottom row - where the pointy corners that attract lightning are).
    Think of schemes that will minimize lighting wanting to follow your DC wires down the hill and into your power room.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • mjp24coho
    mjp24coho Solar Expert Posts: 104 ✭✭✭
    Good suggestions on the lightning protection.  Regarding running the wiring above ground on power poles (panels to charge controller) - does anyone know if this is code compliant?
  • Photowhit
    Photowhit Solar Expert Posts: 6,002 ✭✭✭✭✭
    I don't know, I asked about codes since I might consider trimming out a few of the Juniper trees, and ring them (so they die) they have an extensive root system and I would think as good as some poles and the hassle of drilling in rocky area. Just some creative thinking...
    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
    - Assorted other systems, pieces and to many panels in the closet to not do more projects.
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    edited December 2016 #8
    Do a proper job, use neutral support triplex cable with insulators, ground the support at every pole, put a lightning rod on each pole to ground and make the installation look professional, when the time comes to build it may be accepted as is or with slight modification. Usually it's better to ask for forgiveness than permission, my experience with electrical inspectors.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    The generator shed at my cabin was about 400' away on the far side of a steep hill when I bought the place, maybe to keep the noise down. Power lines were just attached to live trees with ceramic insulators and were like that for 30 years.

    Would it make any sense to fuse at the array in case a squirrel chews wire or a tree falls on it and shorts?
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Estragon said:
    The generator shed at my cabin was about 400' away on the far side of a steep hill when I bought the place, maybe to keep the noise down. Power lines were just attached to live trees with ceramic insulators and were like that for 30 years.

    Would it make any sense to fuse at the array in case a squirrel chews wire or a tree falls on it and shorts?
    Likely not.   Just fuse/Ckt breaker back at the controller and use large enough wire.  If you try to fuse at the array, you may get false trips from solar peak power, and consume a lot of fuses.
     A breaker at the controller PV input is handy for testing, and protects the PV wire from a faulty controller
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • HarryN
    HarryN Registered Users Posts: 9 ✭✭
    It might be worth considering to do the entire (PV panels + 48 volt battery system + inverters) in the same location, and wire over the 120 or 240 VAC to the cabin area.  The wire size needed to transmit the same power in 240 VAC will be much smaller than doing it with 48 VDC.  Also if you do it with AC, then it is also possible to compensate for wire loss a bit easier with a transformer.  
  • BB.
    BB. Super Moderators, Administrators Posts: 33,431 admin
    Schneider and MorningStar have some ~600 VDC input max MPPT charge controllers (others too?). You can run the array at Vmp~400 volts in most climates with a 600 VDC input charge controller--Even better than the 120/240 VAC split phase power--Plus you can put all of the hardware and batteries next to the home instead of a long hike out.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • mvas
    mvas Registered Users Posts: 395 ✭✭✭
    Photowhit said:
    I don't know, I asked about codes since I might consider trimming out a few of the Juniper trees, and ring them (so they die) they have an extensive root system and I would think as good as some poles and the hassle of drilling in rocky area. Just some creative thinking...
    The NEC prohibits the use of trees as support between spans of permanent overhead cables.
     Trees are allowed to support temporary and/or holiday lighting.
  • mvas
    mvas Registered Users Posts: 395 ✭✭✭
    mjp24coho said:
    Question for the group here. I'm looking at doing a large new solar field on top of the hill behind my cabin (much better solar exposure).  It's ~150' from the top of the hill down to my cabin.  The only problem is that it is very steep (too steep for trenching equipment), and the hill is full of granite, so trenching is not an option.  I'm wondering if running the 2-3 PV strings through the air would work - via (2) power poles.  The hill is full of Juniper trees, but none over 30-40', so running the wire over 50' from the tops of the two poles should be free from any obstructions.  Any drawbacks to this?  Does Code allow for something like this?
    See Article 225 of the NEC for permanent overhead cable span regulations.
    Most of the rules that apply to an Overhead Service Entrance would apply to here.

    Summary:
    http://ecmweb.com/code-basics/article-225-outside-branch-circuits

    Overhead cable management systems ...
    https://www.cabproducts.com/wp-content/uploads/2014/12/CAB_Cable_Management_White_Paper_9-18-2014_2.pdf