float @ 90% SOC
My Classic is entering float with the batts not totally charged (90%/95%). Absorb time is set to 2 hours. Should I just add 30 mm more or are there other settings that need to be changed?
thank guys.
Comments
-
I would add to the absorb time. I think mine is set for 4 hours, but I have a whizbang jr and use ending amps as well.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I have lot of sun here in my location and 2 hours absorb time set. I don't have wb jr. I just take the state gravity of my bank every day until I can reach a good setting for my Classic. During 8 month a year, sun is shinning every single day so it does help. On the other end I do not want to absorb more than necessary.Off-grid. Midnight Classic 200. 2,480W array. Magnum Inverter MS4448PAE. 225Ah*8 @48V Trojan T105RE Smart Carbon. MN bkrs box.
-
How much current is going into the batteries at the end of the 2 hrs? You could check Trojan specs but you likely want to stay in absorb until you get down to a couple of amps or so.
Note that you don' t necessarily have to do this every day. You can set the classic to skip X days. It's important to get the batteries fully charged with a long enough absorb once or twice a week, but you could just bulk and float for a couple of days and have it do a full absorb every third day for example.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
So you advise me to skip absorb let say 2 days with just bulk and float and full absorb for 1 day and so on? Does a full absorb every day damage the batts?
I haven't check the input voltage at the end of absorb. I understand that it should be around 2% of my 225ah batt (~ 5 Amps) so should I set absorb time on that basis? My load during the day is pretty stable.Off-grid. Midnight Classic 200. 2,480W array. Magnum Inverter MS4448PAE. 225Ah*8 @48V Trojan T105RE Smart Carbon. MN bkrs box. -
Seems strange to me to limit or skip absorbtion, my manual, not Midnight, states that absorbtion is the most important stage of charging. Is there not a default setting, usually the engineers who developed the controller have a pretty good idea of what a battery needs.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:Seems strange to me to limit or skip absorbtion, my manual, not Midnight, states that absorbtion is the most important stage of charging. Is there not a default setting, usually the engineers who developed the controller have a pretty good idea of what a battery needs.
They don't know what type or capacity battery you have.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
mcgivor said:Seems strange to me to limit or skip absorbtion, my manual, not Midnight, states that absorbtion is the most important stage of charging. Is there not a default setting, usually the engineers who developed the controller have a pretty good idea of what a battery needs.
They don't know what type or capacity battery you have.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
With regards to capacity, the current would be regulated according to the voltage during absorbtion, bulk is where you wouldn't want to over current, within reason. Is this not a reasonable statement ?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
@mcgivor - it IS important to absorb to mix electrolyte and prevent sulfation, but the idea behind skip days is that it doesn't have to be done every single day. OP is concerned about too much absorb (positive plate corrosion, excessive gassing) and has good sun, so my suggestion would be to increase absorb time to be certain batteries are actually full a couple time a week and float otherwise.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
mcgivor said:mcgivor said:Seems strange to me to limit or skip absorbtion, my manual, not Midnight, states that absorbtion is the most important stage of charging. Is there not a default setting, usually the engineers who developed the controller have a pretty good idea of what a battery needs.
They don't know what type or capacity battery you have.
There will be basic setting, AGM, FLA, ...
But think of all the different types of setups, You can have a 4K watt array feeding a lead acid battery! A weekend setup with a huge bank say 1200ah forklift battery, providing just a 5% charge rate, or a 400ah bank in a cloudy region. A finishing rate of 30 amps or 2-3% of a 1200 ah battery is charging rate for a small battery bank. Best to input a finishing rate perhaps more than a timed charging, and perhaps they might consider that at some point, but I think that varies by type as well. I mostly have had FLA.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
dapago,
Personally, would set the Absorb (called 'Bulk' by Trojan) voltage, as specified in the Data Sheet in the following Link -- 59.28 V, 59.3 should be fine:
http://www.trojanbattery.com/pdf/datasheets/T105RE_TrojanRE_Data_Sheets.pdfFloat is noted as 54.0 V, and EQ V is 64.8 V.
Target SG for full-charge is 1.277.
I, too, use Skip Days -- Skip three, and charge on the fourth day.
BUT. dapago probably needs to find settings that will bring the battery bank to full-charge, before Skipping Days.Be certain to mount the BTS on one battery in the center of the battery bank.
The Temperature Compensation value is -- 5 mV/Cell/C. Would suggest setting Temp Comp EQ = YES.
As suggested elsewhere, would set the Charge voltages to those recommended by Trojan, and watch the SGs to see how they respond. If still not reaching 1.277 SGs, then try increasing the Absorb time by about 30 minutes, for a start:
http://kb1uas.com/mnsforum/index.php?topic=3560.0The Classic Ending Amps function works great, when using the WBjr with a 50 mV 500 A Shunt. CC EA (without a WBjr) can work well, especially if there are no heavy loads that are present near the time when Absorb should be ending. Heavy loads that cycle every few minutes should not be an issue when using CC EA, as long as the heavy load is off for about five minutes or so. Used CC EA for about 5 - 6 years without any problems.
All FWIW, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Photowhit said:mcgivor said:mcgivor said:Seems strange to me to limit or skip absorbtion, my manual, not Midnight, states that absorbtion is the most important stage of charging. Is there not a default setting, usually the engineers who developed the controller have a pretty good idea of what a battery needs.
They don't know what type or capacity battery you have.
There will be basic setting, AGM, FLA, ...
But think of all the different types of setups, You can have a 4K watt array feeding a lead acid battery! A weekend setup with a huge bank say 1200ah forklift battery, providing just a 5% charge rate, or a 400ah bank in a cloudy region. A finishing rate of 30 amps or 2-3% of a 1200 ah battery is charging rate for a small battery bank. Best to input a finishing rate perhaps more than a timed charging, and perhaps they might consider that at some point, but I think that varies by type as well. I mostly have had FLA.Vic said:dapago,
Personally, would set the Absorb (called 'Bulk' by Trojan) voltage, as specified in the Data Sheet in the following Link -- 59.28 V, 59.3 should be fine:
http://www.trojanbattery.com/pdf/datasheets/T105RE_TrojanRE_Data_Sheets.pdfFloat is noted as 54.0 V, and EQ V is 64.8 V.
Target SG for full-charge is 1.277.
I, too, use Skip Days -- Skip three, and charge on the fourth day.
BUT. dapago probably needs to find settings that will bring the battery bank to full-charge, before Skipping Days.Be certain to mount the BTS on one battery in the center of the battery bank.
The Temperature Compensation value is -- 5 mV/Cell/C. Would suggest setting Temp Comp EQ = YES.
As suggested elsewhere, would set the Charge voltages to those recommended by Trojan, and watch the SGs to see how they respond. If still not reaching 1.277 SGs, then try increasing the Absorb time by about 30 minutes, for a start:
http://kb1uas.com/mnsforum/index.php?topic=3560.0The Classic Ending Amps function works great, when using the WBjr with a 50 mV 500 A Shunt. CC EA (without a WBjr) can work well, especially if there are no heavy loads that are present near the time when Absorb should be ending. Heavy loads that cycle every few minutes should not be an issue when using CC EA, as long as the heavy load is off for about five minutes or so. Used CC EA for about 5 - 6 years without any problems.
All FWIW, Vic
Next night the battery is discharged to 80% SOC, following morning the controller reads the voltage and goes into bulk until the absorption setpoint is met, absorbtion takes place and times out, then float. This is using a standard algorithm without user input, would this not be a good starting point, to establish a base line from which to adjust setpoints and timed functions to suit particular needs of a system, if needed, wether it be a daily or weekend use, or specific battery requiments. Sometimes too many interventions can lead to problems and these can sneak up undetected and result in premature battery failure.
In the case of @dapago, it would seem his array is a little too large for the battery, 2480W for 225Ah, so if anything the bulk amperage may be on the high side, but once it goes into absorbtion, the current should drop as the level of charge increases. So if it is possible to limit the bulk charge current would this not be the prudent thing to do? The absorption stage would taper the current down to avoid gassing and terminate when the time has expired, then go into float, assuming there are no large loads which may prompt the controller into going back into bulk.
There seems to be different uses for the term bulk/absorbtion as @Vic stated so I copied the information from a Morningstar manual which are the terminologys as I understand them. So as @Estragon mentioned using absorbtion to mix the electrolyte, is this bulk being referred to as absorbtion, as bulk is more likely to do just that.The TriStar MPPT 150V has a 4-stage battery charging algorithm for rapid, efficient, and safebattery charging.Bulk Charge StageIn Bulk charging stage, the battery is not at 100% state of charge and battery voltage has not yetcharged to the Absorption voltage set-point. The controller will deliver 100% of available solarpower to recharge the battery.Absorption StageWhen the battery has recharged to the Absorption voltage set-point, constant-voltage regulationis used to maintain battery voltage at the Absorption set-point. This prevents heating and exces-sive battery gasing. The battery is allowed to come to full state of charge at the Absorption volt-age set-point. The green SOC LED will blink once per second during Absorption charging.The battery must remain in the Absorption charging stage for a cumulative 120 - 150 minutes,depending on battery type, before transition to the Float stage will occur. However, Absorptiontime will be extended by 30 minutes if the battery discharges below 12.5 Volts (25 Volts @24 V,50 Volts @48 V) the previous night.The Absorption set-point is temperature compensated if the RTS is connected; otherwise,voltages set-points are based on the reference of 25ºC..Float StageAfter the battery is fully charged in the Absorption stage, the TriStar MPPT 150V reduces thebattery voltage to the Float voltage set-point. When the battery is fully recharged, there can beno more chemical reactions and all the charging current is turned into heat and gasing. The floatstage provides a very low rate of maintenance charging while reducing the heating and gasing ofa fully charged battery. The purpose of float is to protect the battery from long-term overcharge.The green SOC LED will blink once every two (2) seconds during Float charging.Once in Float stage, loads can continue to draw power from the battery. In the event that thesystem load(s) exceed the solar charge current, the controller will no longer be able to maintainthe battery at the Float set-point. Should the battery voltage remain below the Float set-point fora cumulative 60 minute period, the controller will exit Float stage and return to Bulk charging.The Float set-point is temperature compensated if the RTS is connected; otherwise, voltagesset-points are based on the reference of 25ºC.Equalize StageCertain battery types benefit from a periodic boost charge to stir the electrolyte, level the cellvoltages, and complete the chemical reactions. Equalize charging raises the battery voltageabove the standard absorption voltage so that the electrolyte gases. The green SOC LED willblink rapidly two (2) times per second during equalization charging.The duration of the equalize charge is determined by the selected battery type. See table 4-1in this section for more details. The Equalization Time is defined as time spent at the equalizeset-point. If there is insufficient charge current to reach the equalization voltage, the equalizationwill terminate after an additional 60 minutes to avoid over gasing or heating the battery. If thebattery requires more time in equalization, an equalize can be requested using the TriStar Meteror push-button to continue for one or more additional equalization cycles.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Mcivor - in your example above of a nearly full bank, cc will see voltage of ~12.8v at rest for a 12v bank. It will go into bulk sending available current to bank at whatever rate the bank will take until voltage reaches absorb setpoint (eg 14.7). If the bank was full, it will get to that voltage pretty quickly, but it still has a bulk stage. The controller will then hold voltage at the absorb voltage until either current drops to set value or timeout.
It might make some sense to limit bulk current, but I don't think it's a big issue unless batteries are hot.
As you and Vic have said, the main thing in this case is to get absorb set to fully charge batteries. OP says he checks sg regularly which should help get there.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Hi mcgivor,
When you said,
"Say for example you had a battery which has no loads and is fully charged at days end, overnight the self discharge is almost negligible, the next day sun up battery is at 99.9% charged, the controller sees the voltage and instead of doing a bulk charge goes immediately into absorbtion, after the time out of absorption, it switches into float",
The above is the way that most CC behave now. There is generally NO Bulk voltage setting, because with PV charging, there is not enough current available to immediately reach the Absorb voltage, so maximum available charge current eventually allows the battery voltage to rise to the set Absorb voltage, and THEN, the Absorb stage begins.
If the only "load" on the battery was self-discharge, then the Bulk stage will be fairly short, as would be the required Absorb. But with a fixed Absorb time set in the CC, and Ending Amps was not being used, the Absorb, would most likely be much longer than necessary.
The Outback, and the MidNite CCs ALL have three stage charging, PLUS EQ. MorningStar IS a bit different, but they all have those "four stages".
Few other CC manufacturers have battery type settings, except for different NiCd, perhaps. Morningstar is the only manufacturer that I know of that has an L-16 setting. Much of this is a hold-over due to their very limited range of charge parameters, due to the use of DIP SWITCHES.
Later, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
I just can not get my mind on that EA function.
What I understood at that point is that EA has priority on absorb time but how and when does EA know to limit the amp going into the batts?
Will EA:
- totally cut the charge and if so until when?
- if set to 1,5% of my batt capacity, limit the charge to 3.5A and if so until when?Off-grid. Midnight Classic 200. 2,480W array. Magnum Inverter MS4448PAE. 225Ah*8 @48V Trojan T105RE Smart Carbon. MN bkrs box. -
be able to read the battery end amps, the current sensor (shunt) has to be in only the battery leg, not the solar/inverter/battery wire,
That way, you are only reading the battery amps, not the solar-inverter amps
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
dapago "...when does EA know to limit the amp going into the batts? "
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
To clarify a bit, if you use a "whiz bang jr" with your classic end amps are measured at the battery. If you don't use a wbjr, you can still set end amps but current will be measured at the controller. At the controller current will be a combination of charging and loads, and the loads may prevent the controller from seeing end amps.
The second way can work okay and is probably better than nothing, but the wbjr and shunt aren't really expensive and is the better way to do end amps.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed