Batteries give much less power than their capacity

Hi. We've set up a solar and wind hybrid system to our farm. There are 6 panels, each of them 260W 24V and 4x143aH agm batteries. The problem is batteries should give about 6000W but it cannot give even 3000W if there is no wind. After the sunset charge controller shows their voltage about 25.6 volts. Here is the connection diagram :

I'm saying 3000W because the load is constant about 300w and between sunset and sunrise is 10 hours. Also system voltage drops linearly until about 23v. After that it rapidly drops and system shutdowns below 21.6v. During this the voltage of batteries which are near negative terminal(0V), rapidly decreases down to about 9V and the voltage of batteries near to positive terminal(24V) stays around 12V. What might the problem in the system?
Edit: Cables are thick enough. (9awg)
Edit2: We've send the batteries which are near to negative terminal to the technical service and they said batteries are ok.

I'm saying 3000W because the load is constant about 300w and between sunset and sunrise is 10 hours. Also system voltage drops linearly until about 23v. After that it rapidly drops and system shutdowns below 21.6v. During this the voltage of batteries which are near negative terminal(0V), rapidly decreases down to about 9V and the voltage of batteries near to positive terminal(24V) stays around 12V. What might the problem in the system?
Edit: Cables are thick enough. (9awg)
Edit2: We've send the batteries which are near to negative terminal to the technical service and they said batteries are ok.
Comments
If left in the deeply discharged state for very long sulfate will harden on the plates causing loss of capacity and eventual failure.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
9 awg wire is suitable for the power (Watts) from the panels to the charge controller after that it needs to be much larger.as said above...
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Your load is 300 watts (at the inverter?) or is this 30 - 10 watt lights? do we know if there is a power factor? Did you include the inverer's losses (most are @85% efficient other than a narrow area where they peak at 90-94%)
How far is the inverter from the battery bank? There will be losses in the wiring from the battery bank to the load.
You say only "...Only 2 of them (at the bottom) drops quickly..." are these in the same string? Did you wire your battery bank correctly so they have equal resistance for each string? Multiple strings of batteries can be trick, 2 strings are usually manageable, but I suspect this is the crux of your problem! If they are 1 string are they the string with the shortest leads from the inverter?
The simplest way to ensure that they have equal resistance is to wire each string to a common bus bar with equally sized wires.
Most AGM's can be run down to 20% of capacity, there will also be a a bit of voltage sag from the load. Curious what the recovered voltage is after they disconnect and have sat without a load for a while?
300 watts (or 350 watts if inverter wasn't included as part of the load) represents 12.5-15 amp at 24 volt load on a battery bank of 286 ah or about 1/20th of capacity, as the voltage falls, it will represent a larger portion of the remaining battery capacity, hence will discharge at a more rapid rate. As the voltage falls more amperage is drawn for the same wattage and the battery has less amperage in the "bank".
I hope we have established that the batteries are in the southern hemisphere, but I'll ask to cover all the bases, are the batteries warm? 50-80 degrees? Lead acid batteries have diminished capacity as they get colder.
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
1) Your bank is undersized. If you are trying to get 6000 watt-hours (not watts) then you need at least 12KWhrs of battery storage.
2) Your wiring is undersized. 9awg is insufficient for 100 amps. You need 2awg at least.
3) Your bank is unbalanced. Repetitive deep discharges have likely amplified the (originally small) differences between "top" and "bottom" batteries. There is no way to restore the capacity to the lower batteries; the best you can do is monitor them closely (with a voltmeter) until they are replaced, and keep them in balance as best you can via manual means - individual charging or equalization charging.
4) You have insufficient protection. You need a single fuse or breaker either at the + terminal of the battery bank or at the end of a single wire run from the battery bank.
2- Yes at the inverter. Inverter shows the W and VA which are the same which means no power factor.
3- Wires between inverter and battery bank are less than 20 inches.
4- Here is the connection diagram. Blue circled batteries' voltage drops quickly. After we sent them to the technical service, I've connected the remaining 2 batteries in series and the voltage of the battery at the bottom of new connection ,dropped quickly as well.
5- I will ensure that the resistance is equal when I go back to my homecity(I'm in a student in different city)
6- Never tried
7- Voltage drop to 21.6v from 23v in almost 5 minutes. It shouldn't be that fast.
8- Batteries are in average 30 degrees but there is a strafor layer between the batteries and the ground.
I will try to increase the size.
1- I'm trying to get 3000 watt-hours at maximum.
2- I will increase it
3- As I said before at this comment, after sending that 2 battery to the technical service, connected the remaining two in series and again the battery at the bottom dropped quickly aswell.
4- I will connect a fuse but I didn't get that how might it help to increase the power we receive ?
Thanks so much.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
3 - Any time you discharge a pack heavily - even a good pack - one cell/battery is going to die before the other; the voltage will drop precipitously until the pack voltage gets low enough to trigger the LVD of the inverter (20-22 volts.) The pack will then sit there at a low voltage until the sun comes up again. The "high" batteries (sitting at about 12 volts, or 2 volts per cell) won't like being at a low state of charge but won't be damaged much if it's a short time. The "low" batteries (sitting at 9 volts, or 1.5 volts per cell) are being damaged badly by being at such a low state of charge.
It's even worse if it is just one cell. To get that battery down to 9 volts you might have 5 cells at 1.8 volts and one cell at 0V (i.e. almost reverse biased) - and that cell will die VERY quickly.
The next day the sun comes up and all the batteries charge up again. That night they are drawn down again. The low battery, after suffering some damage the night before, is now even lower capacity, and so hits 9 volts sooner - and the system shuts down again. It then sits at 9 volts for even longer, damaging it even further.
That's why one battery will tend to "go south" if the pack is heavily (and regularly) discharged.
To get around this:
a) Always charge to 100% (or as close as you can reasonably come.)
b) Never discharge more than 50%.
c) Run equalizing charges when practical (only on flooded batteries.)
d) Monitor cell voltages rather than pack voltages and then shut down when any one cell goes below a threshold (1.9 volts or so)
e) Never let any battery sit for any length of time below about 11.5 volts.
f) Do regular measurements of SG (for flooded cells) to monitor state of charge; all cells should be roughly equal.
4 - A fuse will not increase energy received, but could save your life (or your house.)
The only wiring issue I see, is that the wind turbine is connected incorrectly. If you have 4 batteries in series and parallel, they should only have one connection point for positive and one for negative. If connected with equal gauge and length wire, it works out even to pull from the positive of one string and the negative from the other string. Like your solar is connected, or like this;
I see no problem and can't really think of one where one battery would be drawn down more than the other in a string, Though I have seen a single battery have issues, to have 2 at the same time would raise flags. a lead acid battery is 2 volts nominal, a 12 volt 'battery' is actually a bank of 6 - 2 volt cells, by creating a 24 volt battery bank, you are just creating a string of 12 cells.
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Did you build the system?
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
I guess I explained the situation a little bit complex. Sorry for that, let me try again
System was built in the beginning of august and there wasn’t anyone living in the farm before the October because cows weren’t bought and farm was empty. So we were turning the lights on to act like there Is a person in there to prevent theft and we were visiting there every day to feed our dogs.
System was working continuous if we use 5 florescent lamps + 2 LED’s and the refrigerator only. If we turn all of the projectors, system would be down when we come back. One day I went to check at 6AM and it wasn’t up. That’s why I said 10 hours. Replaced all the lamps with LED lamps later.
After I built the surveillance system, I’d looked at to Inverter’s LCD in order to check the power usage while all of the lamps, projectors and the refrigerator’s motor was working. It was about 300W (Both Watts and Volt amperes were equal). That’s why I said 300W because it is the maximum momentary power we need.
After we bought the animals, system was cutting the power in about 5 hours if we use all the devices. If we don’t use projectors and surveillance system, it was cutting the power at 3 AM whereas load was less than 70W. So we needed to use generator for an hour every day in order to use only 5 led lamps.
Because the problem is big, an electricity technician came from the manufacturer of the system (Both panels, batteries and the inverter), removed old wires, rebuilt the system with thicker and shorter cables.
System is working better now according to my father. He said that system works continuous without using the generator even if there is no wind at all. If he uses projectors system was down in the morning.
Also he said that when he woke up at 7AM and checked the battery voltage, it was 24.6V while projectors were off.
To be honest, I haven’t checked the system after the technician. I will check the system and measure everything again and post the results in here.
I'm glad you are having better luck, perhaps earlier you had a few cloudy days?
A clamp meter might help with determining the actual load when running. The inverter will use energy by it's self and the reading you are getting from it is likely what it's outputting and not how much energy it is drawing from the battery.
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
hth
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada