Moving my family- I need some thoughts on solar to keep food when grid goes down
Comments
-
westbranch- thank you that is a good number to add- What do you think?If power goes off we wait and don't open the fridge for 2 hours lets say. Then we turn on the fridge for up to 6 hours. This would enable us to have a smaller battery bank almost half the size. This gives us up to 8 hours of backup power for the fridge. Only thing that I wonder about in doing this, is this going to make the fridge work harder to cool it down and use more power in waiting. What do you think?
In Niger, trying to keep a LG FMA 102NAMA fridge(This has the inverter compressor) backed up with solar using a Victron Multi-Plus Inverter/Charger Compact 12v 1600w with a 70a charger built in.I want to back it up for 4-8 hours. I am also running a few O2 cool fans and a few Thin Lite LED's of my batteries for when the grid is down so my kids can sleep. -
You have the luxury of not having to go for more than 12 hours without the grid. Can you get that 500 AH battery? Keep in mind it needs to rated at the 20 hour rate to be meaningful for design. Good luck!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
@inthejunglewhat: Take a long hard look at how long you expect to be there and how many ":no power" days you are designing for. Then balance your "wants" with your budget and whether you will transport the batteries when you leave.
For example, if a given battery is rated to give you 1,000 cycles at a 50% depth of discharge, and that will happen every day - then you will cycle that battery to death in 16 months 2.7 years. If you cycle it every other day, then 32 months, etc. twice that, etc.
So if you decide that you will be there for 5 years, and power failures a daily occurrence - that means 1,825 charge/discharge cycles. I sure as heck wouldn't design for 50% DOD! If power failures occur every other day, 5 years will be under 1,000 cycles so 50% might make sense for that battery.
On the flip side, if you are there 3 years and power failures occur only every three days then it's way under 500 cycles - which coincides with an 80% DOD for many batteries. So, selecting a battery bank for 50% may not be the best decision if you are at an economic break point. (Like buying a lousy inverter to save money for batteries)
NO, I'm not saying to size battery banks at 80% DOD. I am suggesting that there is a balance somewhere. If the 500 cycles and a 3 year life requirement were MY system, I might accept a 60%-70% DOD if going to 50% required a lot more battery money! Remembering that you really expect 6-9 hour power outages, but your 250 amp hours based on 10 hours of compressor run time. (6 hours is 150 AH, and 9 hours is 225 ah)
The batteries that I am most familiar with have a 5%-10% higher amp hour capacity rating when they are appreciably above 77 deg F but also a decreased lifespan. With a good efficient AGM design, you need to return 102% to 110% of the energy that you withdrew.
Another point to consider is that having a battery that will happily accept a very high charge rate can be valuable in this type of application. Think about back-to-back power failures with limited hours for charging. An inverter-charger with a 100-120 amp charger would be advantageous with a 400+ ah bank, with the right batteries. That kind of charge rate will ruin some batteries, so do your homework!
I would never suggest under sizing a battery bank, but what does under sizing really mean? In a hot climate, it is quite possible to lose your batteries from heat, before you have reached their cycle life limit. So, always using 50% DOD isn't always the best economic model!
Anyone here please feel free to correct any errors! This is intended to an open discussion not a lecture. (Yes, I used some over simplification because this about helping new people understand the concepts)
Marc
Edited to fix basic arithmetic error caught by vtmaps. (Thank you)
I always have more questions than answers. That's the nature of life. -
Marc Kurth said:For example, if a given battery is rated to give you 1,000 cycles at a 50% depth of discharge, and that will happen every day - then you will cycle that battery to death in 16 months. If you cycle it every other day, then 32 months, etc.<snip>
Anyone here please feel free to correct any errors!
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Good point! My error - thank you for pointing that out. Fixed it.
I always have more questions than answers. That's the nature of life. -
inthejungle said:westbranch- thank you that is a good number to add- What do you think?If power goes off we wait and don't open the fridge for 2 hours lets say. Then we turn on the fridge for up to 6 hours. This would enable us to have a smaller battery bank almost half the size. This gives us up to 8 hours of backup power for the fridge. Only thing that I wonder about in doing this, is this going to make the fridge work harder to cool it down and use more power in waiting. What do you think?
How big is the LG and do you have alink to the model you can get?"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Thank you for all of your help, we have two seasons hot and cool, in the cool power is almost never a problem from the gird. In hot season we can have every other day outages for 1-2 or longer, then sometimes we may go a few weeks and then have an outage. It is hard to tell.
Here is the information on the fridge
LG Model: GN B272SLCL and I will attach the LG spec sheet I found for that compressor.
In Niger, trying to keep a LG FMA 102NAMA fridge(This has the inverter compressor) backed up with solar using a Victron Multi-Plus Inverter/Charger Compact 12v 1600w with a 70a charger built in.I want to back it up for 4-8 hours. I am also running a few O2 cool fans and a few Thin Lite LED's of my batteries for when the grid is down so my kids can sleep. -
I might have missed it but I did not see that model in the tables of the attachment...???
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
I live off-grid in Mexico and have a 425L/16 cu ft LG smart inverter compressor fridge (GT46BGP). I've been meaning to post a report here on it. I don't know which exact compressor model it has, but mine being bigger I'd assume yours might use less power. We've been using this fridge for almost 2 years now and love it a lot. Our previous fridge was propane, and it sucked.
Typical power draw is 66 watts, but sometimes it draws roughly 100, 130, or 170 if I fill it with warm groceries. Duty cycle seems to be about 50%, similar to most fridges,, although I've never actually timed it per se. The startup is smooth and gentle, taking a few seconds to ramp up to the operating watts.
Defrost cycle is where a lot of power goes, 250 watts for roughly 20 minutes. Unfortunately it does this whenever it feels like it and not during sunshine like I'd prefer. I'd imagine that it's possible for the fridge to defrost several times per day, especially if you open the door a lot, and/or you have very high hunidity.
Over the winter months the fridge was averaging 0.75 kwh per day,. In the summer we're averaging 1.5 kwh per day but here it's 98F/37C by day and not too much cooler at night.
I hope those numbers help you out. I'm pretty sure my fridge would run fine on a quality 500w pure sine inverter, but mines on an Outback 3600w/48v. -
Chest freezers are the most efficient because the dense cold air does not fall out when the door is opened. You could get a separate thermometer controller for about $45 (mail order) as memory serves me. This allows the freezer to run at refrigerator temperatures. This has been discussed on the board....i.e.: Convert a chest freezer into a high efficiency refrigerator.
With this high efficiency "refrigerator"....you could operate at 1 degree C and now have a "cold buffer" for a couple hours. Food and supplies last longer as well.
Got to thinking in this direction because I thought your location might be quite warm.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
I have a freezer that I converted with a digital temp control it allows me to adjust the temp to what ever I want I worked great as a fridge now it's a freezer again. It was like twenty bucks from eBay .200ah LiFePO4 24v Electrodacus Sbms40 quad breaker chest freezer to fridge- Samlex PST 1524 - Samlex pst3024 - 1hp shallow well pump-Marey 4.3 GPM on demand waterheater - mama bear Fisher wood burning stove, 30" fridgarair oven ,fridegaire dishwasher Unique 290l stainless D.C. Fridge-unique 120l portable fridge/freezer
-
This is the most suitable option that I have found to date. Wanting a unit that is pre-wired for several reasons.
I found a number for much less. They appear to have a female Euro type power receptacle. Odd considering the units power source is a US type plug.
We discussed this option a year ago. Prices were higher and options were lower. We were also looking at pre-wired units at the time.
https://www.amazon.com/bayite-Pre-Wired-Temperature-Controller-Thermostat/dp/B01KEYDNKK/ref=sr_1_19?ie=UTF8&qid=1471823785&sr=8-19&keywords=pre+wired+temperature+controllerFirst Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
For $25: https://www.amazon.com/WILLHI-WH1436A-110V-Temperature-Controller/dp/B00V4TJR00/ref=cm_rdp_product
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
How long a refrigerator or freezer can go before an unacceptable temperature drop is highly dependent on the thermal mass in it. So fill all unused space with jugs of water (refrigerator) or water + some antifreeze (freezer).
Would be interesting to know if the defrost on the LG could be put on a timer such that it only occurs during sunlight hours.I am available for custom hardware/firmware development
-
LG knows about the defrost Jonr. The smart phone app they have is suppose to incorporate this on the next factory revision.
Their US 22 cu ft version is really nicely layed out my female customers say. It goes on sale for arround a grand several times a year and no more surges and a high end model with good low energy useage."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed