New here-glad I found this forum, need advice
invstbiker
Registered Users Posts: 2 ✭
Hello all, question regarding wattage on roof and whats shown on my Mate 3
I have a total of 21 panels for a total of 5805 watts. All panels professionally installed and angled in the correct long and lat.
The maximum I've ever seen with full sun midday is 4.5kW.
Does this mean that the overall system, inverters etc are using the rest or is there some setting I don't have right?
Thanks in advance.
Radian 8kW, Radian 4kW, 2 flexmax charge controllers, 48volt Trojan batteries, Mate 3, 5805 watts on the roof
Thanks in advance.
Hi Invstbiker,
That's about right. The power reduction is due mostly to panel losses due to heat, also wiring and in the charge controllers. It all adds up to about 23%. There are other losses in the battery and inverter efficiency, but that shows up as a difference in load consumption and production.
A very nice system by the way.
I have the GS4048A and am very happy with it.
Rick
4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
We usually apply a.70 to .75 fudge factor to cover all losses from panel to battery to end use here, for off grid, so you are at the higher level , roughly, being grid tied, if you are somewhere that gets minus temps in winter you may see higher output. Others that are GT will have more precise numbers ...
Thanks much, I figured there was some loss but didn't know the +/- % to apply OR if I had a "switch" that I needed to amend. Appreciate the responses!
invstbiker said:Thanks much, I figured there was some loss but didn't know the +/- % to apply OR if I had a "switch" that I needed to amend. Appreciate the responses!
You can look up the spec sheet for your panels, often they publish a NOCT value (Normal Operating Cell Temperature)Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).