Outback VFX 3648 Fried???
pabloesguapo
pabloesguapo Solar Expert Posts: 116 ✭✭
System basics:
--18 Kyocera panels, giving approximately 4500watts.
--24 Rolls 6v lead acid batteries, configured in 3 banks of 8, for a 48v system
--Midnite Classic 150 charge controller
--2 Outback VFX 3648 inverter/chargers, providing 30 amps of AC power each
OK, so here's what happened.
My Midnite Classic 150 malfunctioned, and it looks like my batteries are now charged to 104 volts!!!
A multimeter test shows the batteries at 104 volts. The charge controller says ~40ish volts, as does my Outback Mate 2.
I'm wondering how to proceed from here.
Conventional wisdom, such as that is, says those batteries should have exploded.
I have already (almost) installed a brand new Midnite Classic Lite. I have gotten to the point of initial power up, and the MNGP panel (from the old CC. I haven't boxed it up and sent it in for service yet) read battery voltage in the 40volt range, but the display IS flashing "battery over v", something the old malfunctioning unit never did.
Do I try to drain these batteries somehow, to get them back down to an acceptable level? If so, how?
If I can get them down to 48v, read on a multimeter, will my CC and Mate2 then read them to be 0v, and then not function properly?
Has this battery overcharging damaged my inverters too?
Thoughts?
27 Kyocera panels, 6,500w
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generator
Mate3s
  • vtmaps
    I don't think your 48 volt batteries can ever get to 104 volts.  I think you have a measurement error.  Is it possible that you have a wiring error and are measuring a string of 16 batteries (96 volts nominal)?
  • pabloesguapo
    Here's a drawing of my battery configuration. Individual batteries are registering at 11-12v.
    I used two different multimeters.
    Mate3s
  • vtmaps
    Did you measure individual batteries in each of the three strings?
    Also, your wiring diagram is not optimal, it will unbalance your three strings.  Closer to optimal would be to move either the pos or neg combined cable to the other corner.
  • Vic
    Pablo..,
    Agree with vtmaps,  it seems impossible that any 48 V string of GOOD batteries could ever get up to 100 V,  or more.
    This IS an off-grid system,  correct?
    When you are measuring 104 V string voltage,  and 11 - 12 V individual 6 V battery voltages,  are all of the DC breakers,  connected to the batteries in the OFF position?
    Also agree with vt,  that if one/some of your jumpers between battery strings were open,  or making poor connections,  you might see two strings in series,  BUT,  the individual battery voltages should still be in the 6 - 7ish volts.
    Does this system date to around 2012?
    What is the electrolyte level in the batteries?
    Try carefully disconnecting the jumpers between each parallel string,  and perhaps also disconnect the cables connecting the inverters and CC to the batteries,  so that each string is connected to nothing else...   Wait for some number of minutes,  what is the string voltage of individual battery strings?   And individual batteries?
    Thanks for answers,   Vic
  • softdown
    softdown Solar Expert Posts: 4,062 ✭✭✭✭
    As has been pointed out, I'm pretty sure that your battery banks can not get charged above ~60-64 volts. Put your meter on batteries individually.....they will show somewhere between 5 - 7.5 volts...either low or high reading being extreme.
  • softdown
    Your first post called them 6 volt batteries. "24 Rolls 6v lead acid batteries, configured in 3 banks of 8, for a 48v system"
    BB. Super Moderators, Administrators Posts: 33,734 admin
    If digital meter, replace the batteries.
    Get a second meter and verify the voltages.
    Have seen very strange voltage readings from meters with weak batteries and bad meters.
    Dave Angelini Solar Expert Posts: 7,095 ✭✭✭✭✭✭
    Bill, he says he has 2 meters.
     I do remember you and I troubleshooting a system where the user had somehow wired the battery strings in series and had around 100vdc on the inverters. Probably wont hurt them but not a good situation long term.
    I'll be you are looking at the PV array voltage.  4500W of PV would take a long time to overcharge a 48V bank to 100+ V.
  • Desert Rat
    Desert Rat Solar Expert Posts: 147 ✭✭✭
    I recently had a customer here connect eight 12V batteries in series to an Outback 3648. He was thinking that the batteries were 6V. It knocked out the inverter; we had to send it to Outback for repair.
    Sorry, I missed the two meters.
  • pabloesguapo
    Ended up being two bad meters. I tried with a third meter, and everything checked out fine.
    Thanks vtmaps, for the tip on battery wiring. I will move one cable to another corner.
    Mate3s
  • Vic
    Great news,  Pablo.   Meters are inexpensive,   Solar hardware,  not so much!
    Vic
  • pabloesguapo
    now I have to figure out why my generator just will not run. But that's a different thread.
    Mate3s
    Don't be sorry! You were right in the end!
  • softdown
    I sure miss the days when stuff both worked and lasted.
  • softdown
    What are the odds of two meters both doubling the voltage reading?
  • Desert Rat
    Pretty good, if they are Harbor Freight meters!