Newby Newb. Can you mix 12v and 24v panels into a 12v PMW charge controller?
I think made a mistake... I now see 12v / 24v charge controllers... auto switching.
1.Does that mean I can mix and match 12v and 24v panels ?
2. What is the biggest 12v panel out there? I found a 100 watt panel. If I found a bigger one I wouldn't have to buy a new controller.
Thanks
Comments
-
The biggest "12 volt panels" I have seen were over 300 watts.
The panel voltage going into the controller needs to be the same.
Why do you think you need to buy another charge controller?
Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
Oh, only if I was going to mix and match which sounds like a non starter. Where do I buy these big panels? Thanks
-
One from here, its 285 watt and its voltage is a bit higher than normal for a "12 volt panel" but it will work very well with a real MPPT charge controller.
http://www.solar-electric.com/solarworld-sunmodule-sw285-monocrystalline-solar-panel-33mm.html
Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
I believe the 12v / 24v reference is battery voltage. So if you have a 12V battery bank you get 12V panels (18+ VOC) in order to charge them. Something like 4 100 watt panels in parallel would be a good example. That would charge a 160 to 230AH battery bank at 12 volts.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
-
Raj174 said:So if you have a 12V battery bank you get 12V panels (18+ VOC) in order to charge them.
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Mixing might work, but only at the loss of much of the '24 volt' panels potential energy.
I know evergreen made some 200 watt 12 volt panels, not sure what the largest is currently.
Not sure why you think "...If I found a bigger one I wouldn't have to buy a new controller" You will be limited by the 30 amp capacity of your charge controller. You could have enough panels in parallel to reach that capacity, if they are 30 watt or 300 watt.
The pair of these 165watt panels with your 85 watt panels would max out your charge controller.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Thanks for the correction vtmaps4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
-
oil pan 4 said:One from here, its 285 watt and its voltage is a bit higher than normal for a "12 volt panel" but it will work very well with a real MPPT charge controller.
http://www.solar-electric.com/solarworld-sunmodule-sw285-monocrystalline-solar-panel-33mm.html -
That's actually a 60 cell grid-tie panel, which is 30V. A standard 24V panel will have 72 cells (Vmp~36 volts).
[fix typo. -Bill B.]
4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
?? Vmp is 31.3?
-
Sorry, I guess that is less than typical for a 24V panel.
-
A 60 cell silicon panel will have Vmp~30 volts (1/2 volt per cell). I think Raj174 has a typo (20 volts)--I will fix to prevent confusion.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks again! I think I'll just max out my controller and leave it at that. Dry ice is pretty amazing stuff.
-
Sorry Bill, I was inferring 20V nominal for 60 cells. Just as 24V is nominal for 72 cells.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
-
papab said:oil pan 4 said:One from here, its 285 watt and its voltage is a bit higher than normal for a "12 volt panel" but it will work very well with a real MPPT charge controller.
http://www.solar-electric.com/solarworld-sunmodule-sw285-monocrystalline-solar-panel-33mm.html
A 30 volt panel is an ok choice for a 12v system with real MPPT controller, but its more likely intended for a grid tie setup, series 3 of them up for around 90v and you are good to go.
It would work for a 24v system if you have a good MPPT controller.
A good MPPT controller wont see any noticeable efficiency drop charging a 12v system with a 60 cell panel. If you used a PWM charge controller, that would be a horrible setup. With a PWM controller it would only be like 40 or 50% efficient.
Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
Raj, Oh, you where estimating it as a "20 volt" battery bank... A "different" way of answering the question.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed