MPPT 80 600 CC down
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total
Comments
-
Hi Masterjoe,
62.7 with 82 F batteries is an EQ voltage.
Have asked you two times before ... ;
Thank you for answering the questions that were asked before ... "do you have one or two MPPT 80-600s?". So, you have ONLY ONE..
IMO, on a 24 V system you need TWO of them with your 18 ea 250 W PVs. This is 4500 W STC of PV. With normal de-rating of about 75% of STC PV output during solar peak, that is about 3375 W of output. On a 24 V system, this would yield about 140 Amps of potential output to a battery that is at 24 V. Your MPPT 80-600 will handle ONLY 80 AMps maximum. You are short one Charge Controller, and are wasting about 50% of your potential output. AND, there is some chance of damage to your single MPPT 80-600.
Cannot speak to the error codes.
MidNite Solar makes some very good Surge Protective Devices (SPDs).
Why not ask your "Installer" about the potential output from the PVs verses the capabilities of a single MPPT 80-600 ?
Good Luck, VIcOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
I apologize for not answering the questions. I was also thinking about the fact the system can produce 4500w of PV but Charles insists we only need one. He says 18 panels in 2 strings of 9 is 300v each separate to the charge controller that can handle a max of 600v. Well I am going to insist that I get a second CC. We have peaked out at 2404 so far and I don't see getting 3375. I am experiencing alot of days now where there is either absolutely no output from the pv, or I get a max of less than 100 watts and produce less than 1 Kwh. I will look into the surge protective devices, but it does not seem that what I experienced was a surge or that would have been a separate over voltage fault. We go from system status of 25.6 to 9.9?? Very strange.4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
Hi Masterjoe,
Look, I am not an expert, at all in Grid-Interactive systems, like yours. But it seems that simple math would dictate using two CCs.
Somewhere, perhaps a bit hidden on the Schneider site, is a String Sizer for the MPPT 80--600, which should tell the story.
Earlier, some here have had some questions about the capabilities of your Installer. If my read on the system is not in error, then I, too, will have significant questions about how capable "Charles" really is ...
In the manual for the 80-600, believe that they state the MAXIMUM amount of PV power that is permitted on your CC -- there is s limitation either in Watts, or Mac current - Amp, IIRC. This limit is there, because, under certain conditions, that 80-600 might have trouble protecting itself, if there is too many PVs connected to it, and it could possibly fault, and be damaged, as I read it.
Good Luck, Vic
Just my opinions.Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Hi Masterjoe,
Looking at the MPPT 80-600 Manual, looks like the Max Isc total on the PV input to this CC is 28 Amps.
Assume that your system runs two strings of 9 PV, and that those PV modules have a Vmp of about 30 Volts, and an Isc of approximately 9.1 Amps, then your PV input will not exceed the CCs input Isc Max. At least as I read the manual.
Have not yet found the PV String Sizing Tool, yet.
FWIW, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Hi Masterjoe,
Looking at the MPPT 80-600 Manual, looks like the Max Isc total on the PV input to this CC is 28 Amps.
Assume that your system runs two strings of 9 PV, and that those PV modules have a Vmp of about 30 Volts, and an Isc of approximately 9.1 Amps, then your PV input will not exceed the CCs input Isc Max. At least as I read the manual.
Have not yet found the PV String Sizing Tool, yet.
FWIW, Vic
For the panels you have as mentioned would need 2nd CC to get full potential on 24 VDC system.GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
As I continue to learn here I am starting to get very soured on solar. According to Schneider we need a new CC as this one was damaged in the storm. The battery bank may have been too I don't know voltage from the inverter is reading 25.7v and has been all night. So we are back to grid voltage which we have been every night since the system came online, since AC pass thru means grid voltage. Our electric bill has nearly doubled. Schneider does not cover lightning strikes and homeowners insurance will but our deductible is $1000.00. Cutting my losses and having the system removed will cost me money, and continuing to have it will cost me money. A very bad and costly mistake on my part. Since we don't have the money to replace the CC, I honestly don't know where to go from here, as I am now just constantly getting an F11 fault Outputpvvoltage. More to follow.4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
Hi Masterjoe,
Sorry to hear of the lightning event. It sure can make an expensive mess of things.
Flooded batteries are very tough. It would be surprising if your batteries were damaged by any indirect lightning strikes, IMO.
Believe that you mentioned this in another Thread ... If one connects a GT system to the grid before having the correct meter configuration, your production will actually be billed as consumption, by most utility meters. But, once you get the correct metering, your production will be credited in some manner, depending on your Rate plan.
Here are some very good MidNite Surge Protection Devices (SPDs):
http://www.midnitesolar.com/products.php?menuItem=products&productCat_ID=23&productCatName=Surge Protection Devices
More Later, Good Luck, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Thanks Vic, It is just my luck. Just want to throw this out there since I just got off the phone with Schneider. George had me check the battery bank voltage. Ima write this like I am an idiot lol, there is 12 6v 390ah batteries supposed to be in 3 strings of 4 batteries. There is a positive red tape wire coming off the positive end and a wire with black tape coming off the negative end going into the house. I take the leads from the volt meter red lead to red tape wire, black lead to black tape wire. I get 55.7v, George replies so it is a 48v system. No I say it is supposed to be wired for a 24v system. So what is this voltage really? Still waiting to get a hold of my wonderful installer.4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
Another place to measure the voltage is at the input to the Inverter, or at least at the Main breaker that feeds the inverter, and the main system Negative busbar, where the inverter connects.
It is very difficult to miswire three strings of 6 V batteries as 48 V. And, most of your system voltage readings seem to indicate that it IS a 24 V system.
If there are fuses or circuit breakers on each battery string, and one of those popped/tripped, and the battery string wiring was poorly done, one might be able to get 48 V into the inverter ,,, guess, perhaps.
Back to work, others here will chime in. We all wish you the best of luck!! Thanks for the update, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
When in doubt read the manual."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
I'd say power the whole thing down for a couple minutes, and then apply battery power to the charge controllers, let them boot up, and energize the PV and see if things start charging, Then you can start up the inverter.
Sounds like the installer forgot the SPD's and you may have fried a lot of gear.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
In an update to my question of what thatI get 55.7v, George replies so it is a 48v system. No I say it is supposed to be wired for a 24v system. So what is this voltage really?
4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
I'm thinking that having a very good solar guru stop by would be worth it. You have gone through absolute hell.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
I suspect, installer error, if I read correctly that you have had higher bills since the install...
Also a lack of education by the installer, unless you did not want or refused to learn (I know some people who just want solar because "it's hot" or "it's the right thing to do" but don't want to learn.)
If they lead you to believe than a grid tied system with battery back up would be saving you money, I'd call it fraud, unless you have very high electric rates. The reason for a grid tied system with battery backup is to have very reliable service.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
And I would add exercising due diligence on the part of the owner. This is not a simple grid-tie inverter with 4 wires and a ground. They have the problems with the Outback hybrid also on their forum."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Thought I would give a shout out to the very knowledgeable personnel here. Battery backup for very reliable service went out the window with a lightning strike. My installer was 95% sure if we replaced the GFP fuse the CC would be just fine. He insists he "has never replaced a CC". Well turns out he is 95% wrong "we" are replacing a CC. Schneider won't warranty an act of God which is funny considering one would think lightning would be warrantied since it is electricity. Installer says it is not his problem either. So I will be saving up $1,000 to buy me a new one. In the mean time we have 12 fine batteries sitting outside doing nothing. I gave my installer a call and asked him how long the batteries could sit idle before I can look forward to replacing them too. I said the earliest I have an idea when we could get a new CC is April. He said as long as the batteries are not being discharged they are just fine. Well me being a semi intelligent person I don't buy that load of bull. So I thought I would post it here. PS in that lightning strike we had blew 3 fuses, the 600v GFP on the CC the 1000v on the PV and one on a panel.4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
April for a new controller? It is most likely that lightning would take out an AC inverter--But close behind is probably the charge controller.
I don't remember, but if these are flooded cell batteries... But flooded cell batteries need to be fully/correctly charged at least 24 hours every month. Whether you do this with an AC charger (that has a float voltage setting), or get a cheap solar charger to limp by for now--Your choice.
Nominally, a battery bank on float needs a minimum of 1% to 2% rate of charge (400 AH battery bank needs minimum of 4-8 amps). If you cycle the bank at all--You should have a 5% rate of charge minimum.
If you don't have a backup AC to DC battery charger yet--Now would be a good time to invest in one.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
So now I have Nikki from Wholesale Solar confirming we have a high voltage situation here. We have 187.5 amps going into an 80 amp CC so yes we need 2. But try getting that through my installers head. So now that I have holes in the siding in the walls of my house, how hard would it be to remove all the equipment and have everything wired back to one electrical panel? cause I know I am going to have a huge fight getting him to even come and remove the equipment. As far as I am concerned the wife and I are going to write this off as the biggest costliest mistake I have ever made in our 17 years of marriage.4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
Masterjoe said:So now I have Nikki from Wholesale Solar confirming we have a high voltage situation here. We have 187.5 amps going into an 80 amp CC so yes we need 2. But try getting that through my installers head ...
YES, we have been trying to say this in a different way;
With 4500 Watts STC of PV on a 24 V system, with normal de-rating to about 75 percent, this represents 3375-ish WATTS of INPUT to the CC. At 24 V nominal, this represents about 140 AMPS OUTPUT from the CC, which is a gross overload on it.
A second problem which was mentioned in passing, before, is that this system really begged to be 48 volts nominal, which would reduce the output current to about 70 Amps in good sun, with moderate weather conditions. And could possibly have allowed using the preferred single string of batteries, plus being a bit more efficient at the same time.
If your contractor is Licensed to do this work, you might have some redress with the Contractor Licensing Authority in your state, or perhaps some County or City authority. If unlicensed, you might not have a lot of leverage with the contractor.
Good Luck, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
I agree. You need another installer badly. Serious mistakes made all over the place. I really doubt youll get any useful further help from that guy, and you best cut yor losses and get a pro to fix it up. If you cant afford to do that, i guess you might try selling the system for parts, and starting again when you can afford it. But as others have said hybrid systems are only for people with deep pockets, who have a radical need for power security. For the rest of us mortals, grid tie can work pretty well if you have a good NEM or FIT.
1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar -
I was listening, just trying to get as many different inputs as I can as this guy is adamant we only need one. Of course he is in California right now at a solar conference and won't be back until tomorrow. Having to go to a 48v system is going to require everything being redone. Something he may as well not bother with as I have no faith he knows what he is doing. I have spent most of my spare time learning and diving into the material here, on the internet and asking questions. It seems to me he is more interested in getting that next sale than he is fixing an i4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
4500 watts on a 24 volt system? Your salesperson was an idiot. 187 amps into an 80 amp controller? Same thing. No lightning protection in Florida? Isn't that sort of a lightning capital?
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Unfortunately I am stuck with him for the next 10 years. As my dad says it is good to get the bugs worked out now, it is too expensive to bail out. Piece mealing this system out to get lowball offers would just piss me off further. An expensive lesson learned.
4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
That may be as it may, but if you are going to do RE, you have to do it properly, else it is just going to be a continual drain on your finances and sanity. And possiblly safety. Seriously, i shudder to think how that thing is wired.
Bugs you say? You cant fix the kind of mistakes he made without a serious mindshift change. Vic and Soft have it bang on.
This is a grid interactive system, so you want to be harvesting every single photon, hence you need either 2 controllers, or, 48V. One or the other. And, in Florida, you typically need at least 4 SPDs, one on each end of the array home run, one each on the inverter AC in and AC out.
And you need to check out the net metering urgently. Somethings wonky as a boomerang there.
1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar -
Now I see why my installer is so adamant about me only needing one charge controller. On the bottom of the back page of the contract he writes "Will take back 4024 inverter for free if upgraded to a 48v system within 2 years of installation". So installing it as a 24v system knowing it needs to be a 48v system with half an array that cannot be used so I pay him more money to upgrade to something I should have had in the beginning. WOW!!! What a salesman.4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
zoneblue said:That may be as it may, but if you are going to do RE, you have to do it properly, else it is just going to be a continual drain on your finances and sanity. And possiblly safety. Seriously, i shudder to think how that thing is wired.
Bugs you say? You cant fix the kind of mistakes he made without a serious mindshift change. Vic and Soft have it bang on.
This is a grid interactive system, so you want to be harvesting every single photon, hence you need either 2 controllers, or, 48V. One or the other. And, in Florida, you typically need at least 4 SPDs, one on each end of the array home run, one each on the inverter AC in and AC out.
And you need to check out the net metering urgently. Somethings wonky as a boomerang there.4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
oh! your inverter is a schneider sw? thats whats going on then. the sw is a cheaper version of the venerable xw. however it only initially was offered as 24v. they plan to release the 48v version any day, and he's, like, waiting for it?
1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar -
No it is the XW4024. What I think he wants me to do is upgrade what should have already been a 48v system, because as he stated before he doesn't make much money off a hybrid system. What better way than to charge someone for something they should have already had. That tells me he knows half my solar array is no good to me and is giving me 2 years to figure it out. But one question I have for him is if I did have a working 24v system why would I want to upgrade it to a 48v system?4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
>"Will take back 4024 inverter for free if upgraded to a 48v system within 2 years of installation".
So, if i get this right hes offering a free upgrade to XW4048? Or he'll take the 4024 at retail, and sell you a 6048/6548? Im not really up on what the differences between the xantrex branded XW, and the Schneider branded XW, and cant really comment on the differences.
However the XW is generally considered a good inverter, and very capable for hybrid setups. Out of curiousity, having reread the thread, you dont appear to have a NEM agreement. Whats the reason? Is your power company uncooperative, or you just cant be bothered with the red tape? Without that you lose a lot of potential return on your investment. Backup mode becomes your defacto configuration.
If the system is running in a backup mode, ie batterys in float until power cut, then the second controller may not add all that much value to you. And really, for backup, you have a lot of money invested in the system, when a thousand dollar genset would have done the same job.
The real value in grid/hybrid systems is capitalising on what can be quite lucrative feed in tarrifs, tax breaks etc. That requires a net meter agreement, and the associated red tape. The third possible mode (arbitrage) is as others have said not ususally cost effective.
1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar -
Yes, we do have a NEM agreement with our electric company and have a net meter installed. Haven't been able to get a hold of him yet, will have to try Monday. I am just wondering is it common practice to install a 24v system for someone and oversize it on purpose in the hopes of a 48v upgrade. Secondly if he is going to charge me to upgrade how much can I look forward to? I mean the system would have to be rewired all over again right?4.5kw 24v System
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed