I have an installation where the inverter is located at the array with a 200' trench to the main service panel point of connection. The installer provided a ground rod at the array which is bonded to the array/inverter GEC & EGC.
My question is: the 200' conduit run from the inverter to the main panel has only 3 conductors [L1, L2 and N]. In searching through 690.47(A) and 250.50 - 60/64 I find ambiguous reference to including a separate GEC from the inverter to main panel.
Any insights would be appreciated.
Brent
My question is: the 200' conduit run from the inverter to the main panel has only 3 conductors [L1, L2 and N]. In searching through 690.47(A) and 250.50 - 60/64 I find ambiguous reference to including a separate GEC from the inverter to main panel.
Any insights would be appreciated.
Brent
Comments
-
Re: GEC question
First question would be to the building inspector, as to what he is going to want. safest or not, what he wants, he gets, if you want your permit signed.
could run bare copper $$$ in the bottom of the trench, and PVC conduit above it.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: GEC question
The code is not that ambiguous. It requires a couple things you don't seem to have.
1) An equipment grounding conductor for your inverter output circuit. (I'm assuming the conduit in the trench is PVC). This is a fairly important safety measure which should not be left out. Suppose you have a fault from L1 or L2 to ground in the inverter? Your breaker in the service panel will not trip.
2) A bonding jumper between the AC and DC grounding electrodes, as required by 690.47(C)(1), in the 2011 NEC. (We are on the 2011 code now in California.) -
Re: GEC question
Thanks for the responses. Good answers.
Brent
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed