Robin RGD3300 Diesel Genset
Comments
-
Re: Robin RGD3300 Diesel Genset
More than likely, on a diesel, it would be a mechanical governor. There are very few small gensets with electronic governor because electronic requires things like current transformers to sense main winding current and computer to run the governor. So small gensets with electronic governor are going to be expensive.
The thing that sets frequency is usually called the "high idle" setting on a diesel. The thing that sets governor droop is usually called the "smoke screw". The thing that sets governor reaction time is usually called the "buffer screw". The thing that sets peak torque rise is usually called the "power screw" because it sets maximum fuel rate.
You can severely damage a diesel engine by adjusting the pump and governor if you don't know what you're doing. It's not too hard to adjust the wrong screw and more than double the power output of the engine, usually. It's like this one guy locally that brought a Cummins B-series to me that had all the pistons burnt in it. I rebuilt it and stuck it on the dyno and it was like, Holy Toledo! It was putting out over 850 hp and 1,500 lbs of torque and it's only rated 285 and 600 lbs. He went and turned the power screw out a half turn on the pump to "liven it up" a little because that's what somebody told him to do. That was one healthy 5.9 Cummins while it lasted.
--
Chris -
Re: Robin RGD3300 Diesel Genset
thank you very much, Chris! ...
about the governor was just curiosity. I can not play any adjustment, any diesel injection pump gives me so much respect ... I thing i just want to play a little the throttle to up a little the frequency, so this is the "high idle"?...is a pump adjust?...
I guess this if it will be something simple and easy to do...I'm wrong?...;-) -
Re: Robin RGD3300 Diesel Genset
unicornio - it all depends on what engine you got. Some of the little diesels are as simple as moving the high idle stop to increase the tension on the governor spring. BUT - this also usually increases the pressure on the smoke screw so it's going to have excessive governor droop. So you might have to adjust that too.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Sort of an update for folks who wonder about the long term viability of a small diesel prime power genset for off-grid:
I'm satisfied that it works as advertised, and it's pretty cheap. 94 degrees here today, 72 degrees in the house. Our solar has been running our AC and other normal loads, plus bulk charging the batteries (they haven't been absorbed yet this week) most of the time during the peak of the day. About this time of day (6:00 PM) the power from the solar starts to drop off enough that it doesn't keep up with loads anymore. So this is the time of day that I start the little Robin diesel so it can help out.
The 2-ton AC unit easily consumes 60 kWh/day in hot weather. We can produce about 33-34 kWh with solar, and about 8-10 kWh with wind power on the average. We're using ~80-85 kWh/day right now with the AC running. The wind picked up some this afternoon and it's supposed to blow up to 30 mph tomorrow. If it does that we probably won't have to run the diesel at all tomorrow because we can get 75 kWh in a day pretty easy from the turbines if the wind is 20 mph. But that doesn't happen that often in the summer. So on the average the other 35-40 kWh/day has to come from the diesel prime generator in order to enjoy our new air-conditioned lifestyle
The Robin diesel has been producing that 35-40 kWh on 4.6 gallons of diesel fuel per day for most of the week. So as the weather got hotter, the cost to run it, per day, has gone up. I'm using the AC2 input on the inverter for it this week because I can easily adjust the load on the generator by adjusting the Gen Support Amps. I set it to the lowest possible value to maximize solar harvest, and only use from the generator what is required to get the batteries bulked (but not absorbed) by the end of the day. The batteries are actually liking it - they're nice and cool and haven't used a single drop of water. So the cost to run the diesel has to be subtracted off the cost in batteries long term. I don't know what that cost is, but I know this is drastically increasing the life of the batteries by doing it - they basically haven't been worked all week, pretty much floating back and forth from about 65-80% SOC.
So, again, this is not the setup for everybody. Most off-grid folks won't a run a generator until the last possible watt-hour has been pulled from the batteries and life as they know it is gonna end unless they start it up. I don't look at it that way. We REALLY like our new air-conditioned lifestyle. And this is what's it's going to take to do it. It's seasonal. And the hottest part of the summer is yet to come. But I think me, my wife and our batteries are liking our new diesel prime power addition to our off-grid system.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Chris I am surprised at the AC consumption, our house is 2400 sqft with 10 ft ceilings (24,000 cu ft) and with dual 3 ton Trane 17 seer only consumes about 100 kWh on a really hot 110F day (yesterday was only 89.3kWh but the worst day was 117 kWh) with the thermostat set to 78F. (72F and the wife would be in long pants and a sweater). Granted the humidity is only 19% right now. -
Re: Robin RGD3300 Diesel Genset
The compressor has never stopped running today. The RH was 88% and now as the temp has dropped after sundown the RH has gone up to 92%. The RH in the house is 39% and 72 degrees temp. It's REALLY comfortable in here tonight. The air outside is so heavy that you can almost chop it with an axe. Here, we call it "muggy". It's what happens when we get a warm air mass that evaporates millions of tons of water off Lake Superior. We'll have fog here so thick after midnight that we won't be able to see 100 yards.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Sorry guys, I just had to poke in here. Mitsubishi 12000btu minisplit running about 10 hours yesterday, mid 80's, high humidity...about 5 kwhrs keeping the house at 78 or so. The early hours the consumption is in the 200-300watt range. By 6 or 7pm it's 600-800 fighting the heat soaking of the west/afternoon sun. The heaviest use day might have been 8-9kwhrs so far. Most of the running is off solar, but a little has been off utility power. Just keeping the humidity down makes things very comfortable.
Chris, I find a machete is a better way to cut through the muggy air. You can use it like a carving knife for tunneling but still can chop if you need to.
Ralph -
Re: Robin RGD3300 Diesel Genset
Ours didn't use that much power either when the temp was in the 80's and the humidity around 65%. But yesterday water was running out of the condenser like from a faucet.
With the AC we don't even have to run a dehumidifier in the basement now - the basement floor is not "sweating" at all. And we're saving on how much the 'fridge is running too. Our unit pulls 2.5 kW for the compressor and fan on the condenser. And then the air handler in the house draws about 180-200 watts. The air handler blows the air thru all the heating ducts for our wood furnace, so it goes to every room. It works really good. We only got 2-ton capacity cooling 2,000 sq ft. The installers that put it in, when they came to evaluate the "heat load" of our house, said it's better to size a hair too small than too big because it will be more efficient in normal mid-80's conditions, even though it runs steady with the temp in the 90's and really high humidity. They did not recommend a mini-split unit for whole house cooling, including dehumidifying the basement.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Since I started the diesel a couple days ago it hasn't been shut off for over 48 hours now. I tried something new - set the Gen Support amps down to 8 for the hot weather. This limits how much the generator can contribute, and also makes it run a little cooler for the hot weather. It makes the inverter and batteries carry minimum 1 kW for the AC, plus additional loads, which discharges the battery a little more so it doesn't get absorbed during the day. The generator produced 89 kWh (got an old GE utility meter on it in the utility room) in 48.6 hours and burned 10.5 gallons of fuel at the time I took this movie.
So I get slightly less kWh/gallon with a lighter load on the genset, but it's not significant. A higher load (~2.4 - 2.5 kVA) is the "sweet spot" for the Robin, but if I run it at that power setting then it don't work the batteries hard enough and the solar starts to absorb them during the day. I don't want the batteries to get absorbed more than once a week - especially in 90+ deg weather during the peak of the afternoon heat.
[video=youtube_share;Dzb8xu7Ydz4]http://youtu.be/Dzb8xu7Ydz4[/video]
--
Chris -
Re: Robin RGD3300 Diesel Genset
You know, sometimes things are so obvious that you don't see 'em. I've been fighting with improving the ventilation in my new powerhouse because I was seeing temps up to 110-115 degrees F in there in hot weather. In the old enclosure I built last fall for the Honda, the genset ran cooler in that enclosure in hot weather than it did standing in free air.
You know why? I had to regroup. The theory that heat rises is a good one. But it don't work in this application. In the old enclosure I was forcing fresh air in the top and out the end of the enclosure. It worked because it enhanced the natural airflow over the genset produced by the engine's cooling fan. So far I've been fighting that natural airflow in the new powerhouse. After the lightbulb came on over my head I hung some shop rags in there on a string and ran each genset one at a time with no ventilation fans running to see how the air wants to flow. And then I enhanced it with the fans. And I got immediate and drastically better results.
[video=youtube_share;q1KJSwf1GKU]http://youtu.be/q1KJSwf1GKU[/video]
The heat basically exits on the control panel side of the Robin and heads right out the exhaust fan. On the Honda the heat exits the end facing the door, turns the corner and heads right out the exhaust fan. The air intake fan provides a higher pressure area of cooler up near the ceiling because it's considerably more powerful than the exhaust fan. That prevents any heat from the gensets from rising as it heads out the exhaust fan. The circulation fan grabs air from the air intake fan and forces it down towards the floor to the cooling fan intakes on both engines, and the cooling fans on the engines do the rest of the work.
It works. Not like I expected in my first "design", though.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Well, I had some solar panels to install today on the house roof and got that done. Then when I was putting my tools away in the shop I happened to stumble over a 16" long piece of 5" chrome exhaust stack that I trimmed off one of my semi tractors awhile back because the stacks were too tall to get in a couple place we go to. It immediately came to me what that piece of exhaust stack is good for!
This is the true "finishing touch". The cherry on the whipped cream. The frosting on the cake.
[video=youtube_share;ewRmW41tDM0]http://youtu.be/ewRmW41tDM0[/video]
--
Chris -
Re: Robin RGD3300 Diesel Genset
very good exhaust tube, appears that you are tuning your genset shack!...;-)
sometimes appears something that was there waiting, and when you see it, seems you already knew that you were going to use it, even before you saw! ... hehehehe -
Re: Robin RGD3300 Diesel Genset
Never be good to have exhaust chrome on one and not the other, nor have the diesel be outdone by a gas job. -
Re: Robin RGD3300 Diesel Genset
Well, yeah. It's got chrome fuel cap, chrome switches, chrome exhaust and a few chrome bolts. I should probably pick up a chrome valve cover and some chrome cylinder stud nuts for it. A valve cover from a Yanmar L70 fits it and you can get those in chrome Plus maybe a stick-on chrome mudflap babe for it.
With all that chrome stuff, it's bound to put out more power :cool:
--
Chris -
Re: Robin RGD3300 Diesel Genset
Nice video as well. How many oil changes since you got the little 3500? Must be a few with the operating hours it has been getting. -
Re: Robin RGD3300 Diesel Genset
I've been running it 100 hours between oil changes (it's got a pressure lube system with a filter) and it's on its third oil change since I bought it. The little thing holds just about two quarts of oil. Even running at 115 degrees inside the powerhouse in really hot weather, it has never required any add-oil between changes. I'm running Cenex Superlube 518 SAE30 diesel oil in it.
One of the unexpected side effects of adding the Big Chrome Exhaust was that it made the exhaust note deeper and louder. So I had to make a baffle for the end of the 2" exhaust tube inside the big one to quiet it back down.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Have you thought about adjusting the placement of the small exhaust pipe inside the large outer and having the large outer open on the shed side to created an argumented exhaust which will pull air out of the shed to aid in keeping it cool. Would need to hardware cloth screen to keep critters out also. Could also, possibly drop exhaust sound some small percentage. Works on turbine and fan jet airplane engines.GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
Re: Robin RGD3300 Diesel GensetHave you thought about adjusting the placement of the small exhaust pipe inside the large outer and having the large outer open on the shed side to created an argumented exhaust which will pull air out of the shed to aid in keeping it cool.
Yeah, that's the way I got the Honda. But it took a lot of fiddling with it to get the exhaust pulse to create a negative pressure in the vent pipe. The diesel smokes a lot, especially at full load the way I got the pump adjusted for minimum "droop" to hold a constant frequency. I'm afraid if it's not perfect it would pull smoke into the powerhouse.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Guess that could be a problem. Would have to play with depth of pipe penetration and opening size on shed side of the big pipe. Glad to hear that you have played with the idea before. Free cooling air flow for the generators.GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
Re: Robin RGD3300 Diesel Genset
It takes proper size and length of the secondary tube as well as proper placement of the primary (usually called the "stinger") to get it to work. I stumbled on the correct combination with the Honda in my other smaller generator enclosure I had built for it. The sound wave can't be allowed to expand until it hits open air, and the expansion of the sound wave at that point creates a vacuum on the secondary tube.
Diesels are unthrottled so they move a lot a more air (exhaust flow volume) than gasoline engines do (except when a gasoline engine is at wide open throttle). It would be a bit more tricky with a diesel.
--
Chris -
Re: Robin RGD3300 Diesel Genset....
A start below or close to freezing temperature and it will snort, bang and blow lots of smoke. Sounds like the piston will come flying out, but still goes. Trying to hand start is futile for anyone not in shape with shoulders like the Hulk...or a farmer. Ralph
My shoulders are both shot, so the electric start is important for me. The listeroid has a great flywheel, which helps it fire off.
Any cold starting advice - preheating the air with a propane torch at the inlet ? I see they have a glow plug option - anyone with experience with that ? Coldest I'm expecting is 15F (-10c) in this area on a rare occasion.
Is it easy to let it idle for a moment to warm up, or does it slam the governor right to 3600 rpm (60Hz) at start up ?Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Robin RGD3300 Diesel GensetMy shoulders are both shot, so the electric start is important for me. The listeroid has a great flywheel, which helps it fire off.
Any cold starting advice - preheating the air with a propane torch at the inlet ? I see they have a glow plug option - anyone with experience with that ? Coldest I'm expecting is 15F (-10c) in this area on a rare occasion.
Is it easy to let it idle for a moment to warm up, or does it slam the governor right to 3600 rpm (60Hz) at start up ?
As long as the engine will crank at normal speed, pre-heating the intake air is usually sufficient to get most direct injection diesels to start.
Most small generators go right to rated speed when started up. You'd have to hack the throttle linkage like I did on my Robin to get it to idle for a few minutes for warmup.
--
Chris -
Re: Robin RGD3300 Diesel GensetChrisOlson wrote: »Most small generators go right to rated speed when started up. You'd have to hack the throttle linkage like I did on my Robin to get it to idle for a few minutes for warmup.
--
Chris
Is there any risk of damaging the AVR if the generator is run at lower than rated RPM?
I hate to start a cold engine at full RPM (especially 3600RPM), but I would be afraid to fry something on the AVR if tries to boost voltage at lower RPM.
I picked up an older YDG3700 (serial # 00185 so it must be an early one). After cleaning out a thick layer of sludge in the tank, I'm awaiting a new intank fuel filter and a few small parts before trying to get it running. While I wait for the parts to arrive, I am soaking injector pump and injector in Kroil penetrating oil in case they were gummed up from the fuel contamination. Anyway, I hate cold starting an engine like the Yanmar L70 with such high RPMs, but I am concerned that the AVR could be damaged at lower RPMs. -
Re: Robin RGD3300 Diesel Gensetkeyturbocars wrote: »Is there any risk of damaging the AVR if the generator is run at lower than rated RPM?
Absolutely none as long as you don't try to load it during warmup. The AVR is powered by the exciter winding in the gen head and a diode. It will attempt to full-field the rotor but with limited voltage input from the exciter it can't do much.
--
Chris -
Re: Robin RGD3300 Diesel GensetChrisOlson wrote: »Absolutely none as long as you don't try to load it during warmup. The AVR is powered by the exciter winding in the gen head and a diode. It will attempt to full-field the rotor but with limited voltage input from the exciter it can't do much.
--
Chris
OK. That's good to know. I remember reading in the past about some older military gensets (MEP-002A and -003A) that people said they fried the AVR because they ran it at lower RPM. Apparently, they just started it up and ran it at low RPM with no load, and something failed on the AVR board. From what I read, this happened to more than one person. I don't understand what happened there. The MEP-002A & MEP-003A are basically militarized versions of the civilian Onan 6.0 DJ and 12.0 DJ series gensets. -
Re: Robin RGD3300 Diesel Gensetkeyturbocars wrote: »OK. That's good to know. I remember reading in the past about some older military gensets (MEP-002A and -003A) that people said they fried the AVR because they ran it at lower RPM. Apparently, they just started it up and ran it at low RPM with no load, and something failed on the AVR board.
The AVR tries to full-field the rotor if the voltage is low. But it takes a lot longer than just a couple minute warmup to burn it out at low voltage. I should take a photo of the throttle "hack" I did on the Robin. I put an aluminum arm on the throttle lever with two notches in it. One for dead idle, and an intermediate notch for warmup. It has the same latch mechanism as the Yanmar for rated speed operation.
Basically, when you first start it you'll let idle for about 30 seconds to get oil pressure and make sure everything has lube. Then you'll push it up to about 2,800 - 3,000 rpm under no load and let it warm up until warm air is blowing off the cylinder fins. At that point you can take it up to rated speed and put load on it. This is way easier on the engine than starting it cold and having it misfire and smoke from incomplete combustion and being over-fueled when it's cold.
It takes a lot longer than the couple minutes required for warmup to overheat the AVR from trying to full-field the rotor.
--
Chris -
Re: Robin RGD3300 Diesel GensetChrisOlson wrote: »It takes a lot longer than the couple minutes required for warmup to overheat the AVR from trying to full-field the rotor.
--
Chris
I'm glad to hear that. I've run generators at lower than rated RPM (with no load) with no problems. After reading about a transistor failing on the AVR board of those old military generators, I was becoming a bit paranoid. -
Re: Robin RGD3300 Diesel GensetChrisOlson wrote: »... I should take a photo of the throttle "hack" I did on the Robin. I put an aluminum arm on the throttle lever with two notches in it. One for dead idle, and an intermediate notch for warmup. It has the same latch mechanism as the Yanmar for rated speed operation....Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed