Re: Robin RGD3300 Diesel GensetChrisOlson wrote: »I bought a 39 foot roll of 6" thick x 24" wide fiberglass insulation.
They now sell fire-proof insulation, which looks like fiberglass butts, but has a dark-greenish color. You can heat it with a torch and it doesn't catch fire. I tried. I think you can buy it in Home Depot. -
Re: Robin RGD3300 Diesel Genset
Tony - yes, I'm going to try to seal around the bottom where they can get in by laying down a green-treated 2 x 6 under the bottom of the glass batts and then seal the raised corrugations in the steel outside walls near the ground with bag-crete.
NorthGuy - the insulation I bought is fire-retardant type. I got it at Menards. I will kind of melt in a direct flame from a torch but if you take the flame away it doesn't continue burning or melting. They don't call it fire-proof, just fire resistant, made from non-combustible fibers. I think that is required now by most building codes to help prevent spread of a fire inside the walls in a building.
That is sort of one reason I prefer to use the onboard fuel tank for liquid fueled generators. They ARE a fire hazard and if one would catch fire it's generally better to have a limited amount of fuel there (6 gallons) to fuel the fire instead of a large tank nearby. It would require a fuel transfer pump to have a large fuel tank a safe distance away for fire purposes, and that's not really practical for a small genset either. And nowadays you can't even set a stationary fuel tank anymore for a generator unless it has spill containment (concrete dike). It won't pass the building inspector. For a large diesel genset it's worth it to go thru the hassle. But for a small generator that will run for a whole year on 100 gallons of fuel, it's easier to just fuel it from a can.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Chris,
My genshed has a door the full size of the end, about 4 x 5.5 feet high. Mice would get in around the edges until I made some mouseproof stripping (like weather stripping, but for critters.).
The builder's lath cut about 3 inches wide in a long strip, fold the two cut edges together so in profile it will look tear drop shaped. Screw or staple the "mouse" stripping along the door frame and shut the door (or attach it to the door itself). It might take some muscle to shut the door, but no critter will be able to get past it. Weather strip is not really needed since you need to vent the structure somewhat anyway. My door is held shut by a padlock hasp, not a knob set.
Of course mice will find some way in sometimes. The last invasion was from around the exhaust stack thimble. Remedy was more lath and some coarse steel wool. I hate mice.
ralph -
Re: Robin RGD3300 Diesel GensetThey now sell fire-proof insulation, which looks like fiberglass butts, but has a dark-greenish color. You can heat it with a torch and it doesn't catch fire. I tried. I think you can buy it in Home Depot.
It's called "rock wool" very effective for sound and thermal. That said, it doesn't hold together exposed as well as fiberglass batts. You could cover all the exposed insulation (no matter the type) with a aluminum insect screen, well stapled to keep the mice out of the insulation.
Tony
Tn -
Re: Robin RGD3300 Diesel Genset
I don't think we'll have a big problem with mice in it. There's never been any gotten in to the present Honda generator house and that's not near as well sealed up as the new shed will be. My wife has two cats and they keep small animals pretty well under control for the most part. Those cats spend all their time either sleeping or hunting. And we never feed 'em except for buying them some raw chicken necks in the winter time. The cats are pretty fat so I think they do pretty good on the hunting part.
--
Chris -
Re: Robin RGD3300 Diesel Genset
If they spend their sleeping time in the sun, maybe they are off grid solar cats.ChrisOlson wrote: »The cats are pretty fat so I think they do pretty good on the hunting part.SMA SB 3000, old BP panels. -
Re: Robin RGD3300 Diesel Genset
Attachment not found.Attachment not found.If they spend their sleeping time in the sun, maybe they are off grid solar cats.
Yeah, and they seem to do that alot. They're both pretty friendly and want to be petted all the time too. The one doesn't mind being picked up, but the other one will run if you try to pick him up. If you pet him while he's on the ground everything is fine. But he'll claw you up seriously if you pick him up.
I think they're independent off-grid solar cats
This is the type of liner I'm using in the power house - it's that foil-faced 3/4" foam. With 6 1/4" thick bat insulation underneath. Got the back wall and ceiling done today - plus got the door in it.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Well, decided two things different tonight - I'm going to put a gravel floor in the powerhouse instead of a floating treated plywood floor. I like gravel - it's really hard to get it to burn.
And I decided to re-arrange the furniture a bit from what I had originally planned. The Robin diesel will set where I show it in the photo with the exhaust routed thru the wall to the right. The Honda will set along the right wall with the control panel facing the room and the exhaust routed directly thru the wall like it is in the present gen house. Electrical panels will go in the corner to the left of the door. Fresh air will enter thru the wall on the left in the photo (forced in by ventilation fan) and ventilation exhaust air will exit thru the wall to the right.
--
Chris
Attachment not found. -
Re: Robin RGD3300 Diesel Genset
Probably not the sort of thing you need to worry about in an detached, unoccupied structure like that, but does that particular foam normally specify a fire rated covering on either side to prevent toxic outgassing when exposed to flame?ChrisOlson wrote: »This is the type of liner I'm using in the power house - it's that foil-faced 3/4" foam. With 6 1/4" thick bat insulation underneath. Got the back wall and ceiling done today - plus got the door in it.SMA SB 3000, old BP panels. -
Re: Robin RGD3300 Diesel Genset
I'm not sure about the toxicity of it. But it won't burn. If you hold the point of the flame from a propane torch to it, it takes about five minutes to burn a hole thru it. And it never does catch on fire, nor is there any smoke from it. So I wouldn't call it fire proof (like concrete or steel). But it's definitely fire-retardant material.
It's got a listing of code compliance and ASTM numbers on it longer than my arm.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Chris,
\If you're having a forced vent fan for the shed have you thought about having it turn on and purge the air in the building before the Honda fires up? Just to remove any gasoline fumes before any relays or engine running occurs?
Ralph -
Re: Robin RGD3300 Diesel Genset
Ralph - it does that now in the little enclosure using Relay #3 in the AGS as a preheat would be for a diesel. It runs the fan for one minute before cranking. After the initial startup, then the fan is thermostatically controlled so it normally stays running after the genset shuts down until the temp in the enclosure falls below the stat setting.
I've changed that whole setup since I first built it, and after we put in the XW inverter. The XW-AGS operates three pilot relays in the gen house and the pilot relays handle ignition/ECU, crank, and fan control. I also added a fourth relay that sends switched B+ back to the XW-AGS, with the relay coil activated by the genset's battery charging alternator, so it knows when the gen has started so it can halt the crank signal. That wasn't required with the SW+ GSM.
--
Chris -
Re: Robin RGD3300 Diesel GensetChrisOlson wrote: »I bought a 39 foot roll of 6" thick x 24" wide fiberglass insulation. And I figured I'd cover that with that fire-retardant foil-faced 1" foam stuff like I used in the small enclosure for the Honda. For ventilation I'll pressurize the building like I do with the present small enclosure, as that helps force exhaust gases (where the most heat is) and fumes out the exhaust vents. ........
Be careful with crankcase breather fumes and the insulation capturing the oil mist, in a couple years, you can accumulate enough oil to make a rockwool wick burn nicely.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Robin RGD3300 Diesel GensetBe careful with crankcase breather fumes and the insulation capturing the oil mist, in a couple years, you can accumulate enough oil to make a rockwool wick burn nicely.
The crankcase breathers on both the Honda and Robin are re-combustor type that circulates the breather gases back into the intake. So no problems with that.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Testing with the extra muffler on it to make sure it doesn't cause too much backpressure. Works fine. It's actually pretty quiet outside even without the insulation installed on the east and west walls yet - no noisier than the Honda, really. With the door to the powerhouse open, however, it's LOUD!
[video=youtube_share;-tc_kDK6TpE]
http://youtu.be/-tc_kDK6TpE[/video]
--
Chris -
Re: Robin RGD3300 Diesel Genset
Chris
Since you first started this thread have been interested in what you are doing. I also found a Subaru Robin dealer here in Panama City. Phoned today, but was put on hold for a very long time, hung up. The generators on the web site that I would be interested in are:
RGX 4800E: voltage regulation - capacitor
SGX 7500E: voltage regulation - AVR
RGD 3300H: voltage regulation - capacitor
There are two smaller units in the SGX lineup, but they are recoil only according to the web site, a 3500 and a 5000. Was hoping to get some additional information from the company, but will try again. All models are electric start.
Have not been able to source a Honda generator dealer in Panama City. Will keep trying as I like your Generator Support setup.
Have also seen a Porter Cable generator at the local ferrateria (hardware store). Was pressed for time so I did not get to read the labeling. Looked these up on line and apparently some have a Honda engine. Will be looking at it in the next few days.
Nice generator shack. Having everything in the same space is always a good thing. Look forward to reading and seeing your continued progress.
Cheers
Ernest -
Re: Robin RGD3300 Diesel GensetPanamretiree wrote: »RGX 4800E: voltage regulation - capacitor
SGX 7500E: voltage regulation - AVR
RGD 3300H: voltage regulation - capacitor
Earnest, the RGD3300H would be the same unit I got except with a Hatz diesel. I'm very impressed with the gen head on my Robin. It actually will put out more power than what it's rated at (3,300 watts) for a short time - I loaded it to 15 amps @ 238 volts for about 15 minutes and the breaker didn't pop, nor did the voltage falter. The Robin DY27 puts out just a trace of exhaust smoke at 3.5 kVA load. Just one more amp and then it goes into torque rise and puts out some serious smoke (the way I got the smoke screw tuned). At 3.5 kVA I'm pretty sure it's at the engine's full rated hp. I won't run it there all the time, just in testing to see what she's got. But it is a pretty healthy little generator.
The other two models must be gas engine models. I've heard that the Subaru-Robin gas engines are very good units.
I made a second test run tonight - this time testing the ventilation system in the powerhouse with the generator at full load. Not real happy with the air circulation in there and it gets up to about 115-120 degrees inside with 70 degree ambient temp. Plenty of air flow but it's not picking up the heat from the genset like it should. I might add a second fan near the floor that causes a "swirl" in the room to eliminate the hot spot where the gensets are and drive the heat up into the airflow so it exhausts out the vent better. Plus I will probably add a second hot air exhaust vent near the floor..
[video=youtube_share;rAGWLHqX97s]
http://youtu.be/rAGWLHqX97s[/video]
--
Chris -
Re: Robin RGD3300 Diesel GensetChrisOlson wrote: »Earnest, the RGD3300H would be the same unit I got except with a Hatz diesel. I'm very impressed with the gen head on my Robin. It actually will put out more power than what it's rated at (3,300 watts) for a short time - I loaded it to 15 amps @ 238 volts for about 15 minutes and the breaker didn't pop, nor did the voltage falter. The Robin DY27 puts out just a trace of exhaust smoke at 3.5 kVA load. Just one more amp and then it goes into torque rise and puts out some serious smoke (the way I got the smoke screw tuned). At 3.5 kVA I'm pretty sure it's at the engine's full rated hp. I won't run it there all the time, just in testing to see what she's got. But it is a pretty healthy little generator.
The other two models must be gas engine models. They are. I've heard that the Subaru-Robin gas engines are very good units.
I made a second test run tonight - this time testing the ventilation system in the powerhouse with the generator at full load. Not real happy with the air circulation in there and it gets up to about 115-120 degrees inside with 70 degree ambient temp. Plenty of air flow but it's not picking up the heat from the genset like it should. I might add a second fan near the floor that causes a "swirl" in the room to eliminate the hot spot where the gensets are and drive the heat up into the airflow so it exhausts out the vent better. Plus I will probably add a second hot air exhaust vent near the floor.
--
Chris
Thought about your ventilation setup. Understand wanting to pressurize and force the air out of the compartment, but I would have thought "drawing" air in by having exhaust fans would be better. You can put the exhaust fans in key locations to ensure air flow to and through a specific area. With supply fans the air flow will go where it wants, not where you would like it to go. Exhaust fans could be setup so that you have exhaust fans specific for the RGD3300 and for the Honda ensuring air flow where you want it. You can also place the air inlets so that you draw air in such a way as to remove hot air from the upper part of the compartment.
Just a thought.
Cheers
Ernest -
Re: Robin RGD3300 Diesel GensetPanamretiree wrote: »With supply fans the air flow will go where it wants, not where you would like it to go. Exhaust fans could be setup so that you have exhaust fans specific for the RGD3300 and for the Honda ensuring air flow where you want it. You can also place the air inlets so that you draw air in such a way as to remove hot air from the upper part of the compartment.
Yep, you're right. Getting proper ventilation with the much larger room is not as easy as it is with the existing small enclosure for the Honda. It's going to take a combination of supply and exhaust fans I think with the air moving over the hottest areas. Those 20" window fans work really good because they don't take much power for the amount of air they move. I think adding another 20" window fan in a key location down by the floor, exhausting warm air, and having the vent up by the ceiling opposite the supply fan to get rid of heat the collects up there, will greatly lower the summer time temps in there.
We have little need for generators in the summer, for the most part. Winter is when they'll run the most. The Robin diesel might run for several days at a time in the winter when we get poor days with no RE power - it's my new idea to prevent cycling the batteries during those times. Run the very efficient little diesel to carry house and shop loads and heat water instead of digging into the bank and then having to recharge the batteries with the Honda. And just use the Honda for heavy peak loads like the electric range or clothes dryer.
In winter time the temp in the powerhouse is probably going to be about right with the way I got it set up. So I'll have to block off an extra ventilation fan for winter, probably, to prevent too much cold air from coming in.
--
Chris -
Re: Robin RGD3300 Diesel Genset
Cold weather is a problem in N NY . We cover our generator with a wool blanket if less then 20°f. If not the oil never gets warm enough . I hope my generator doesn't see the nice house you build for yours ! We could have trouble :0)
ThomOff grid since 1984. 430w of panel, 300w suresine , 4 gc batteries 12v system, Rogue mpt3024 charge controller , air breeze windmill, Mikita 2400w generator . Added 2@ 100w panel with a midnight brat -
Re: Robin RGD3300 Diesel Genset
Thom, I used a 75 watt heat lamp on the Honda all last winter to keep it warm. It never failed to start once. I plan on doing the same thing in the new powerhouse. I don't necessarily need to keep the diesel pre-heated all the time because the use of that generator is more of a planned thing. But the Honda has to start and go to full load within one minute after startup to supply on-demand peak load power. So that means the Honda has to be kept warm most of the time in winter.I hope my generator doesn't see the nice house you build for yours ! We could have trouble :0)
You mean your generator will go on strike and say, "OK, that generator over there has a house to live in - I want one too"
I got about $500 bucks in the new powerhouse. It's not expensive to build. But I suspect I'll have another $500 bucks in wiring to get the power from the powerhouse to the utility room because the wire run is now about 150 feet. I have to run service wires for two generators (although I can use a shared neutral and ground because both generators cannot run at the same time). And control wires for the Honda. Plus 120V service to the powerhouse for lights and fans in it. Plus conduit. Plus electrical service panels. And trenching in the conduit and wiring. Yeah, I'm probably over $500 bucks just to hook 'em up.
I'm using a 200 foot AWG 10 generator cord at present to test the Robin in the shed.
--
Chris -
Re: Robin RGD3300 Diesel Genset
I like your setup and the way you approach things. What about the gravel floor and the issue of dust? I have a gravel floor electrical room and the dust is an on going issue especially with forced air cooling on all of this new-fangled stuff.
Skip12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014. -
Re: Robin RGD3300 Diesel Genset
Onanused to make (and use) a vacuflo fan system. Instead of a pusher fan on the engine, drawing air at random from the surrounding area, it uses a tractor fan, pulling ducted air directly from outside so that the engine is always getting cool outside air rather than potentially reheating inside air. I have used a few over the years and they work quite well. If high interior temps are an issue, consider ducting your intake air. (Chris is clearly smart enugh to know this, but for others with less experienc)
Tony -
Re: Robin RGD3300 Diesel Genset
Skip - the present smaller gen house for the Honda has a gravel floor and dust has never been a problem in there. So I don't think it will be a problem. But if it dries out from the heat and dust gets kicked up I'll just dump a couple five gallon pails full of water on the floor. The area where I build the powerhouse is a low area that gets all the rain runoff from the shop roof, so I think the ground is going to stay pretty wet under that gravel, though.
Tony - yep, I think I'm going to have to go a version of that system that Onan used. I sat in the powerhouse on my upside down five gallon pail studying the situation last night and that was the exact conclusion I came to - I need to duct the ventilation intake air directly towards the diesel generator. That will give it fresh cool air. And when it's not running the fresh air will flow around the diesel and over to the Honda where it can use it. Then put a forced air exhaust fan where I got that warm air exhaust vent, and make the exhaust vent larger. That will prevent the air from going directly across the room and out the warm air exhaust vent, without picking up the heat off the generators like it is now.
The only thing is, an axial fan does not work that good for ducted air. So I'm going to try to find a centrifugal furnace blower fan for the intake side. I'll try the axial fan first, but I suspect the back pressure from the ducting will reduce the airflow too much.
--
Chris -
Re: Robin RGD3300 Diesel Genset
And don't fight mother nature--Look at mounting the outlet vent high where the heat rises.
For another application I put a "heat trap" in (vent high, but then ducted down low for exhaust) to make a quick and dirty environmental test chamber. The exhaust fan would drive the hot air down the duct to the low exhaust when I needed to cool the chamber (assuming you need to keep the building "warm" in winter.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Robin RGD3300 Diesel Genset
Bill, that's why I put that warm air exhaust vent up by the ceiling. I figured that the heat would naturally rise and the air flowing across the room would carry it out. But there must me some turbulence issues there so the air doesn't mix properly and carry the warm out out like it should. Standing in the room with the Robin running there was a nice cool blast of air flowing directly across and out the vent. The vent air was warmer than the intake air, but not warm enough. But it was trapping hot air down by the generator. I think I need to introduce a "swirl" in there by ducting it so the ventilation air picks up the hot air and carries it out.
For noise, you have to have the ventilation openings away from the generator so the sound has to go around corners to make it outside. If you put the ventilation opening right by the gen, then it's really loud right thru the hole.
This is NOT my area of expertise, so I'm just experimenting
--
Chris -
Re: Robin RGD3300 Diesel Genset
Consider insulating the exhaust pipe from the room, so that it doesn't add heat to the room. A tin box with rock wool on one side might work, or some fire rated foam. If that can vent to the outside with free air that might help as well.
T.
PS. My original power house has a Coupola on the roof with a Pair of 48"x 36" vents, one on each side. In those days, my little Onan would run with the heat vented directly from the engine case out 8" stove pipe out the side walls. When the big Lister was running, I had an old paddle fan on the ceiling oer the Lister, pulling air up and out he coupola. Since there was a large opening under the engine through the floor, I could run in nearly all temps and never see temps more than about 10f above ambient. In the really hot summer I would open the side windows and or the man door. Closing it up made it quieter, but by no means quiet.
In the winter I would run with the Coupola shutters shut, and the room would warm up to about 50f at 0f outside.
T -
Re: Robin RGD3300 Diesel Genset
I put the muffler in the room because I wanted to use it for heat in the winter so I can get it up to about 60-70F in there for those air-cooled engines. The muffler, however, doesn't put out anywhere near the heat that the engine cooling system puts out. The silver insulation, which is only about 6" from the muffler, barely gets warm to the touch with the generator running at full load for an extended period. That's a pretty big muffler for a little 265cc engine, so it just doesn't get that hot.
I really think the ducting idea you came up with will work good, and use both forced intake and forced exhaust to improve the airflow thru the thing for summer. I found a little 1/3 hp axial fan that has special blades on it with an actual airfoil on the blades - it moves a LOT of air. I'm going to build a air box around the ventilation exhaust, mount that fan on the air box and try it again, using a temporary deflector of some sort to deflect the incoming cool air right over the genset.
--
Chris -
Re: Robin RGD3300 Diesel Genset
OK, this made a pretty dramatic difference with a makeshift air deflector and adding a 1/3 hp exhaust fan. With this setup, other than the noise, it's pretty comfortable inside the powerhouse with the generator running.
[video=youtube_share;RqcwuHdl5mA]
http://youtu.be/RqcwuHdl5mA[/video]
--
Chris -
Re: Robin RGD3300 Diesel Genset
I found out that this setup barely gets the room above ambient temp. For whatever reason, blowing the fan right on the genset gets the heat away from the generator, it goes around the back wall and right up to the exhaust fan. I ran the little Robin for 24 hours straight from 6:00 PM yesterday to 6:00 PM today. Halfway thru the test run today I pulled that makeshift air deflector down and made a flap that covers the air intake hole. Then placed the fan so it's blowing right on the gen. It dropped the temp in the powerhouse by 5 degrees. 77 degrees outside 84 degrees in the powerhouse.
The little diesel burned 5.3 gallons of fuel and our consumption was 36 kWh. But several times during the test run the load exceeded what the little thing can put out so the XW assisted it from RE power. So the 36 kWh all didn't all come from the little generator. But most of it did - better than 30 kWh.
This is what it looks like the way I have it set up now.
The room is so air-tight that the exhaust fan pulls that foam insulation flap I made open about a foot. So I'm thinking that in the winter I'll just set the window fan on the floor and have it run all the time when either generator is running to circulate air in the room and eliminate "hot spots". And let the Duct Stat control the exhaust fan. The flap will go shut by itself when the exhaust fan isn't operating and help keep the cold air out when it's 30 below and the generators aren't running.
This is my theory on this:
With the price of diesel fuel crashing recently, and it's now cheaper than gasoline (which hasn't happened for 5 years) - and off-road #2 being 60 cents a gallon cheaper than gasoline right now, I can run this thing around the clock for about $15 a day. That's pretty darn cheap off-grid prime power when I take into account that a week of bad RE conditions in the dead of winter can be easily handled without charging the batteries even once with the generator. In fact, the batteries can float for the whole week, we can use all the freaking power we want and live in style, and the fuel bill in that little diesel generator will only be about $105 running 24 hours a day for 7 days.
As it is now, on those bad days when we only get 3 kWh (if we're lucky) the Honda starts on low battery voltage and charges up the batteries. And we only got about 20 gallons of hot water in the heaters because the only element that heats is the top one in the primary heater unless we get sufficient RE power. With this little diesel going I can heat water 24 hours a day if I want during those times, just to keep it busy - and not have to conserve a single watt in the house or shop.
So the way I got it figured is that the net difference between having to charge batteries with the Honda and heat water with it (inefficient) vs running the little diesel for week, not cycling the batteries at all, and having all the power we want on tap ("borrowing" from the little bit of RE we get for Gen Support on the big loads) is about nil. It costs money to cycle batteries and charge them with an inverter charger. My theory is that the long term total cost of off-grid power will be cheaper by using the prime power genset and putting some fuel in it than it will by working the snot out of the batteries and the Honda for that week (or two).
We'll see how all this pans out. But after my 24 hour test run, she's lookin' good.
Now I have to get the Honda moved to the new powerhouse so it can live with its new companion. Also, preheat for that diesel for winter time starting is neatly solved. I can heat the Honda's head and carb with the heat lamp like I did last year and it'll start in any weather. The Honda runs several times a day in the winter, even during excellent RE generating times, for peak load support. As well insulated as this new powerhouse is, just the fact that the Honda runs an hour or two every every day will keep the diesel warm without having to preheat it at all.
--
Chris
Categories
- All Categories
- 234 Forum & Website
- 142 Solar Forum News and Announcements
- 1.4K Solar News, Reviews, & Product Announcements
- 200 Solar Information links & sources, event announcements
- 901 Solar Product Reviews & Opinions
- 256 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 430 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 656 Solar Water Pumping
- 817 Wind Power Generation
- 624 Energy Use & Conservation
- 624 Discussion Forums/Café
- 316 In the Weeds--Member's Choice
- 75 Construction
- 125 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed